Thanks Matt, but the challenge is that this assembly needs to be capable of 
being buried. I’m familiar with the ones used inside buildings and we’re not 
inside a building.



Craig Prahl | Jacobs | Fire Protection SME – EV, AM, DC, Special Hazards
[email protected]<mailto:[email protected]> | 
www.jacobs.com<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS

From: Mike Watts <[email protected]>
Sent: Monday, March 9, 2026 3:27 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [EXTERNAL] [Sprinklerforum] Re: Flexible assembly on pump discharge in 
seismic cat D area

https: //www. metraflex. 
com/products/fire-protection-division/?matchtype=e&network=g&device=c&keyword=metraflex%2520fireloop&campaign=1880371110&adgroup=72795587649&matchtype=&network=g&device=m&keyword=&campaign=1879994101&adgroup=67581073182&gad_source=1&gad_campaignid=1879994101&gclid=Cj0KCQjw37nNBhDkARIsAEBGI8NDEzU6QG8GfbpPNfSPMWigac-U8CJvEPSnVW2RWo1KlqAmv4AklogaAifAEALw_wcB

https://www.metraflex.com/products/fire-protection-division/?matchtype=e&network=g&device=c&keyword=metraflex%2520fireloop&campaign=1880371110&adgroup=72795587649&matchtype=&network=g&device=m&keyword=&campaign=1879994101&adgroup=67581073182&gad_source=1&gad_campaignid=1879994101&gclid=Cj0KCQjw37nNBhDkARIsAEBGI8NDEzU6QG8GfbpPNfSPMWigac-U8CJvEPSnVW2RWo1KlqAmv4AklogaAifAEALw_wcB<https://urldefense.com/v3/__https:/www.metraflex.com/products/fire-protection-division/?matchtype=e&network=g&device=c&keyword=metraflex*2520fireloop&campaign=1880371110&adgroup=72795587649&matchtype=&network=g&device=m&keyword=&campaign=1879994101&adgroup=67581073182&gad_source=1&gad_campaignid=1879994101&gclid=Cj0KCQjw37nNBhDkARIsAEBGI8NDEzU6QG8GfbpPNfSPMWigac-U8CJvEPSnVW2RWo1KlqAmv4AklogaAifAEALw_wcB__;JQ!!B5cixuoO7ltTeg!BWdLNiB0wT0Oq1otdTS9COyq4nddN1b-DHtK1HTZ2JYlAF5bwYWhkk20EEdum1dwOCtIRh6S-3QhEXxigBI$>


Mike Watts  RME-G-3218231

Sprinkler Service Manager

[image]

Firetrol Protection Systems, Inc.

4616 W. Howard Lane, Building 7, Suite 700

Austin, Texas 78728

[email protected]<mailto:[email protected]>

Office 512-687-0115<tel:+15126870115>

Cell 512-660-4411<tel:+15126604411>

________________________________
From: Prahl, Craig <[email protected]<mailto:[email protected]>>
Sent: Tuesday, February 10, 2026 9:28:47 AM
To: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Flexible assembly on pump discharge in seismic cat D 
area

I have a packaged fire pumphouse, discharge exists horizontally through the 
wall and then turns down to connect to the underground outside of the bldg. The 
seismic design category SDC) is “D”. I am being told by the project ME that we 
should

I have a packaged fire pumphouse, discharge exists horizontally through the 
wall and then turns down to connect to the underground outside of the bldg.



The seismic design category SDC) is “D”.



I am being told by the project ME that we should have a flexible connection on 
the discharge side outside the bldg. to accommodate the potential of 8-inches 
of movement between the pumphouse and underground piping system.



I’ve looked around to try and find such an assembly for 8” pipe suitable for an 
outdoor installation and so far haven’t found such a device.



So, my question for those out there in seismically active areas, is this 
standard practice and who makes such an assembly?



Craig Prahl | Jacobs | Fire Protection SME – EV, AM, DC, Special Hazards

[email protected]<mailto:[email protected]> | 
www.jacobs.com<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>

1041 East Butler Road   Greenville, South Carolina  29606

CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS



________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to