One time I did a six-story Medical Office Building as 100% shell space; 
specified by the engineer as Light Hazard with 220 ft2 spacing.  All tenants 
were to be medical offices… Light Hazard.



The very first tenant to go in was a shop for nurses’ uniforms… Ordinary Hazard 
Group 2.  On the opposite corner of the building from the riser.



The second tenant to go in was a restaurant… Ordinary Hazard Group 1.



Yes, the system had to be significantly revised.  Fortunately, there were no 
other tenants yet, so there was no interruption of existing tenants to rework 
the sprinkler system.



Now, as a consulting engineer, I do not allow Light Hazard designs for shell 
spaces, but that is specified, not a code requirement.





David L. Miller, P.E.

Engineered Fire Protection, LLC

11920 Richcroft Avenue

Baton Rouge, Louisiana 70814

225-273-5040



From: Fpdcdesign <[email protected]>
Sent: Saturday, May 9, 2026 5:04 PM
To: Ken <[email protected]>; Discussion list on issues relating to 
automatic fire sprinklers <[email protected]>
Subject: [Sprinklerforum] Re: Shell space?



A vacant space is considered light hazard so that is what the low bidder 
designed to.



Todd Williams

Fire Protection Design/Consulting

Stonington, CT

860-608-4559






On May 9, 2026 at 5:20 PM, <Parsley Consulting 
<mailto:[email protected]> > wrote:

Friends,

I'm in the process of a lengthy plan review of a -13 compliant sprinkler system.

The layout has shown large areas of "shell" space, and the calculations show 
light hazard, for future TI.

For a long time, perhaps to long to admit, I've had the impression such spaces 
should be either OH1 or OH2.

Any clarity?

sincerely,

Ken Wagoner, SET
Parsley Consulting
3002 Younger Drive
Harrisonville, Missouri 64701-3909
Phone: (760) 745-6181
Visit the website 
<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>



_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To 
unsubscribe send an email to [email protected] 
<mailto:[email protected]>



--
This email has been checked for viruses by Avast antivirus software.
www.avast.com
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to