Sue,

Well said. Ordinary Hazard Group 2 with Quick Response Heads.
Works for Light Hazard and Ordinary Hazard occupancies. No need to go back
and modify the overall system.
I've yet to see a tenant finish out which didn't benefit from this approach.

Mike Slaughter
Risk Reduction Division
Travis County Emergency Services District 2
Office:    (512) 989-4531
[email protected]




On Fri, May 22, 2026 at 7:10 AM Sue Stafford <[email protected]> wrote:

> I have had to come behind firms that design basic shell buildings as light
> hazard without consideration to future occupancy code compliance
> downstream, and it is *not* pleasant.
>
>
>
> I have always had my designers standard shell type buildings at Ordinary
> Hazard Group 2 with 120 sf spacing at minimum.  Yes, there is a little more
> time and cost for design & material up front but is essential for future
> use consideration.
>
>
>
> As noted in previous comments, opens the door for you to educate your
> client understand a shell building concept and it allows developers /
> tenants more flexibility to quickly fill these spaces.
>
>
>
> Give those who pay our bills that and we see more work from them!
>
>
>
> My 2 cents…😊
>
>
>
> *Sue Stafford *|Design Manager
>
>
>
> 3141 Eagles Nest St., Suite 250, Round Rock, TX 78665
>
> *[email protected] <[email protected]>* |
>
> www.caruthps.com |  O: 512-276-2774 | M: 281-910-7853
>
>
>
>
>
>              A Fire and Life Safety Company
>
>
>
> *From:* [email protected] <[email protected]>
> *Sent:* Sunday, May 10, 2026 4:34 PM
> *To:* 'Discussion list on issues relating to automatic fire sprinklers' <
> [email protected]>
> *Subject:* [Sprinklerforum] Re: Shell space?
>
>
>
> My 2 cents:
>
>
>
> I always encourage developers and municipalities to require minimum design
> criteria for speculative lease warehouse construction, based either on the
> potential storage height or at a minimum, the design criteria for 20 ft
> high pallet rack storage of Class IV commodities (.33/3000) or even
> .45/3000.
>
>
>
> Now, you might ask yourself…. Self, why is that a good idea? Well, because
> when new businesses start up, cash is always limited, and if that business
> has the choice between moving into a facility that is ready for their
> occupancy needs, without having to invest $$$ into modifying the fire
> sprinkler system in a building they do not own, they’d rather pay a higher
> lease rate per sqft for a space that is ready to move into.
>
>
>
> Where local policies require move-in-ready spaces, they attract more
> businesses and a larger tax base to support their community's needs.
> Additionally, while this may increase the size of the underground and
> backflow preventer, not having such a policy could result in having a 4”
> underground private fire service main and backflow, which would make any
> needed upgrades to the system for a tenant or new owner very much more
> expensive down the road.
>
>
>
> Again, just my opinion for protecting speculative lease buildings based on
> a minimum expectation…. They don’t build them 30 ft + tall so people can
> store 8 ft high. My opinion does not represent any organization or committee
>
>
>
> Bob Caputo
>
>
>
>
>
> *From:* Rick Matsuda <[email protected]>
> *Sent:* Saturday, May 9, 2026 5:42 PM
> *To:* [email protected]
> *Cc:* [email protected]; [email protected]
> *Subject:* [Sprinklerforum] Re: Shell space?
>
>
>
> Steve, great point.
>
> I was only an AHJ…not a smart contractor.
>
> Rick
>
>
>
> On May 9, 2026, at 5:23 PM, Steve Leyton <[email protected]>
> wrote:
>
> 
>
> That's a big step forward for common sense, but what if the tenant is a
> sales office with full height partitions for privacy?  Until you see a plan
> for the fit-out, you don't know if sprinkler spacing will average 85 or 185
> sq. ft.  My firm specifies and/or designs that sprinklers shall be spaced
> at 100 sq. ft. and modeled for .20/1500.  Overkill? Perhaps, but we always
> have enough outlets for a clean T.I. and the contractor of that work
> doesn't fall into hydraulic black hole.
>
>
>
>
>
> Steve Leyton
>
>
>
> Sent from my "Smart" Phone, so apologies for any typos or voice-to-text
> corruptions.
>
>
>
>
>
>
>
> -------- Original message --------
>
> From: Rick Matsuda <[email protected]>
>
> Date: 5/9/26 3:05 PM (GMT-08:00)
>
> To: [email protected]
>
> Cc: [email protected], Sprinklerforum <
> [email protected]>
>
> Subject: [Sprinklerforum] Re: Shell space?
>
>
>
> As a former AHJ, I would accept the following.
> Get a signed letter from the owner and the architect stating that the
> tenant improvement spaces will only be occupied by light hazard office
> spaces and not ordinary hazard spaces like retail, manufacturing, or
> storage.
>
>
>
> Inform all parties involved that any deviation from the letter will result
> in costly upgrades. It will be cheaper for them to plan for ordinary hazard
> now than to make changes in the future.
>
>
>
> They are also limiting the types of tenants who might want to lease the
> spaces.
>
> Good luck, Rick Matsuda
>
>
>
> On May 9, 2026, at 4:50 PM, daren welborn <[email protected]> wrote:
>
>  When I’m designing shell space in office buildings; it’s always been to
> light hazard.
>
>
>
> Shell space in a future strip mall or industrial type areas, has always
> been to ordinary group I or II.
>
>
>
> Sincerely,
>
>
>
> Daren Welborn
>
>
>
> On May 9, 2026, at 5:20 PM, Parsley Consulting <[email protected]>
> wrote:
>
> 
>
> Friends,
>
> I'm in the process of a lengthy plan review of a -13 compliant sprinkler
> system.
>
> The layout has shown large areas of "shell" space, and the calculations
> show light hazard, for future TI.
>
> For a long time, perhaps to long to admit, I've had the impression such
> spaces should be either OH1 or OH2.
>
> Any clarity?
>
> sincerely,
>
> *Ken Wagoner, SET*
> *Parsley Consulting*
>
> * 3002 Younger Drive Harrisonville, Missouri 64701-3909*
> *Phone: (760) 745-6181 *
> *Visit the website
> <https://url.avanan.click/v2/r01/___https:/linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1___.YXAzOnByb3RlY3Rpb25kZXNpZ25hbmRjb25zdWx0aW5nOmE6bzpiZjAzOTk0YWEzZWZlMzM2OTY5OTIxYmZjYmU3NmI3YTo3OjFmOWE6ZWMxN2ZlNzY3Mzk5NGVhNmJkNTFjYTMxZjEyMmI1M2I2YjMwMTQxYjlkYmJkMDJkZDIzNjJmNTQwNjM0MzQ2MjpoOlQ6Rg>*
>
>
>
>
> _________________________________________________________
> SprinklerForum mailing list:
>
> https://url.avanan.click/v2/r01/___https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org___.YXAzOnByb3RlY3Rpb25kZXNpZ25hbmRjb25zdWx0aW5nOmE6bzpiZjAzOTk0YWEzZWZlMzM2OTY5OTIxYmZjYmU3NmI3YTo3OmJmNWQ6YjZhMTU5ZGJkNWRiMjkwZTY2NDAxNTdiOGUzZGFhYjUyMmQ3YzMzNTkxODY3ZDY3N2JlZWU5MTc2NTc1NDJjZjp0OlQ6Rg
> <https://url.avanan.click/v2/r01/___https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org___.YXAzOnByb3RlY3Rpb25kZXNpZ25hbmRjb25zdWx0aW5nOmE6bzpiZjAzOTk0YWEzZWZlMzM2OTY5OTIxYmZjYmU3NmI3YTo3OmJmNWQ6YjZhMTU5ZGJkNWRiMjkwZTY2NDAxNTdiOGUzZGFhYjUyMmQ3YzMzNTkxODY3ZDY3N2JlZWU5MTc2NTc1NDJjZjp0OlQ6Rg>
> To unsubscribe send an email to
> [email protected]
>
>
> _________________________________________________________
> SprinklerForum mailing list:
>
> https://url.avanan.click/v2/r01/___https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org___.YXAzOnByb3RlY3Rpb25kZXNpZ25hbmRjb25zdWx0aW5nOmE6bzpiZjAzOTk0YWEzZWZlMzM2OTY5OTIxYmZjYmU3NmI3YTo3OmJhNjY6OGI4Y2UzY2JmNzU5OTdlZWViN2U5OWM2ZGZhNThhZDQ0NDBkNzY3ZWYwZDgxM2JhYjA5ZTFkMmIyOWZkYzI2Yzp0OlQ6Rg
> <https://url.avanan.click/v2/r01/___https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org___.YXAzOnByb3RlY3Rpb25kZXNpZ25hbmRjb25zdWx0aW5nOmE6bzpiZjAzOTk0YWEzZWZlMzM2OTY5OTIxYmZjYmU3NmI3YTo3OmJhNjY6OGI4Y2UzY2JmNzU5OTdlZWViN2U5OWM2ZGZhNThhZDQ0NDBkNzY3ZWYwZDgxM2JhYjA5ZTFkMmIyOWZkYzI2Yzp0OlQ6Rg>
> To unsubscribe send an email to
> [email protected]
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to