Dewayne,
A couple of questions:
1) Does this meet the 10% or 4,000sf requirement?
2) Does the storage meet the 1,000sf in one pile requirement?
3) Is there 25' or more between storage areas?

If you don't meet the above criteria, you are moved into the Low-Piled Storage requirements.
In my opinion, what you have would be considered solid shelves.
4.3.1.5.1 than re-directs you to 25.6.1, from there it gets complicated.


/Thank you,
Bob Knight, CET III//
/*/Fire by Knight, LLC/*/
//208-318-3057/
FIREBYKNIGHT

On 6/11/2026 12:37 PM, Dewayne Martinez wrote:

Sheets of laminate (class III) (5’x10’) stored in multiple row solid shelf racking.  Each shelf is 6” high, 5ft wide and 10ft long.  When looking at it from the front  the rack uprights are 6ft apart.   The rack is 12ft high and contains 5 rows total.  How would one go about protecting this?  There is no room between the shelves for in-racks .  Is section 4.3.1.5.1 (NFPA 13, 2019ed) allowing me to protect with a OH2 overhead density if the racks meet the definition of miscellaneous storage?

Thank you,

Dewayne Martinez

Fire Protection Design Manager

*TOTALMechanical*

*/Building/**//**/Integrity/*


W234 N2830 Paul Rd.
Pewaukee, WI  53072

[email protected] <mailto:[email protected]>

Ph: 262-522-7110

Cell: 414-406-5208

http://www.total-mechanical.com/ <http://www.total-mechanical.com/>



_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email [email protected]


--
This email has been checked for viruses by AVG antivirus software.
www.avg.com
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to