Standard spray sprinkler option is always on the table. I thought the Globe Low 
Flow Attic Scheme (now Victaulic) had a listing for 3:12 as well.

The way I see the AP calc is all of the AP's up to 1,950 Sq. Ft.

Couple points of caution:
Be sure to check all the CPVC/Sprinkler listings for CPVC Dry systems in attics.
Also note that the AP sprinkler requires a maximum water delivery time of 60 
seconds when you use that sprinkler.

Taylor Schumacher, SET
Security Fire Sprinkler<http://www.j-berd.com/>
1 Industrial Blvd | Sauk Rapids, MN 56379
Office: 320.640.7050 | Cell: 605.212.2132

From: Jeff Brickell <[email protected]>
Sent: Tuesday, September 01, 2026 12:32 PM
To: [email protected]
Subject: [Sprinklerforum] Tyco AP Heads Under Shed Roof

I have a shed roof on an apartment building protected by CPVC pipe.  The shed 
roof has a 3:12 pitch.  The only special application head that meets the slope 
and configuration requirement is the TY3190.   The heads' data sheet does not
Warning: Unusual sender <[email protected]<mailto:[email protected]>>
You don't usually receive emails from this address. Make sure you trust this 
sender before taking any actions.
I have a shed roof on an apartment building protected by CPVC pipe.  The shed 
roof has a 3:12 pitch.  The only special application head that meets the slope 
and configuration requirement is the TY3190.

The heads' data sheet does not show a shed roof configuration, it only shows 
them being used in a hip, and in conjunction with BB's or SD's.

The attic space is wood-framed and it will be a dry system.  Has anyone used 
these heads by themselves, not in conjunction with the BB or SD heads?  If I 
follow the spacing guidelines from the other diagrams, how many heads would I 
calculate?  I'm thinking (7) would be fine.

I've reached out to Johnson Controls, however, I thought I would get some other 
people's opinion and advice.

Thank you.


Jeff Brickell, CET
NICET III CERTIFIED
CERT #147245

OREGON CERTIFIED COBID FIRM #13272
(EMERGING SMALL BUSINESS)

TRIAD FIRE PROTECTION
[cid:[email protected]]
OREGON . WASHINGTON . ARIZONA

OFFICE  503.856.6333
CELL       602.550.4292
FAX        866.766.8862

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to