I’d love to hear from the manufacturers about this.  My first thought is that 
175 psi sprinklers must withstand test pressure of 700 psi or more, so an 
intermittent high pressure exposure (that’s what this would be, “intermittent” 
as opposed to “continuous” my not be a deal-breaker.   But… if the system 
working pressure is defined by the manual standpipe demand, the literal read in 
the standard is that 175 psi sprinklers are not rated for the working pressure 
and thus, would have to be protected or upgraded to HP.   The use of a pressure 
reducing control valve or installation of an in-line one can be considered, but 
if the normal pressure (from city water or a pump) is lower, then the setting 
of any PR device has to consider whether the valve would reduce inlet pressure 
under all circumstances or only if higher pressure than the discharge setting 
would be regulated.

Not much help, but I feel good about myself for participating.

Steve L

From: Matt Grise <[email protected]>
Sent: Thursday, September 24, 2026 10:00 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Quick question on NFPA 13/14 "System Working 
Pressure" and FDC-boosted pressure in a combined system

You might take a look at the sprinkler head listing documents and then contact 
the manufacturer. If the cut sheets for the sprinklers say that 175 is the max 
(however they word it) – and the sprinklers are exposed to pressures in excess 
of 175 (except for hydro testing) – then if a sprinkler fails, even at a time 
when the pressure is less than 175, I would anticipate you being thrown all of 
the way under the bus. And probably the bus will be put in reverse, backed up 
and then pulled forward to run you over again.

Not a risk that I would take.

Matt

From: Fpdcdesign <[email protected]<mailto:[email protected]>>
Sent: Thursday, September 24, 2026 11:52 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Quick question on NFPA 13/14 "System Working 
Pressure" and FDC-boosted pressure in a combined system

Have you looked in the 2022 or 2025 edition to see if the wording changed?

Todd Williams
Fire Protection Design/Consulting
Stonington, CT
860-608-4559


On Sep 24, 2026 at 10:45 AM, <Joe Burtell 
[MT-BILL]<mailto:[email protected]>> wrote:
I've got a combined sprinkler/standpipe system I'm working through and want to 
bounce a question off you, since you're on the NFPA 14 committee.

THE SCENARIO

I'm using NFPA 13 (2019) and NFPA 14 (2019). Facts:

The FDC will be supplied with a pumper truck at 200 psi, as this is a manual 
standpipe system.
All pipe, fittings, and valves on the combined riser are rated 300 psi or 
greater.
The sprinklers are residential sprinklers, which only come rated to 175 psi max 
— there's no higher-pressure listed option to spec around this.

Since the riser is shared between the standpipe and sprinkler systems, I'm 
trying to nail down whether that 200 psi FDC-boosted pressure is something the 
sprinkler branch has to be designed/protected against, or whether it's 
legitimately excluded from that side.

THE DEFINITION CONFLICT

NFPA 13 (2019), 3.3.235 - System Working Pressure:
"The maximum anticipated static (nonflowing) or flowing pressure applied to 
sprinkler system components exclusive of surge pressures and exclusive of 
pressure from the fire department connection."

NFPA 14 (2019), 3.3.24 - System Working Pressure:
"The maximum anticipated static (nonflowing) or flowing pressure applied to 
standpipe system components exclusive of surge pressures."

NFPA 14's 2019 definition dropped the FDC exclusion that NFPA 13 still carries. 
My understanding is the 2016 edition of NFPA 14 did exclude FDC pressure, and 
the exclusion came back (worded differently, as an explicit inclusion this 
time) in the 2024 rewrite. So in the 2019 pairing I'm stuck with, NFPA 13 
excludes FDC pressure from working pressure, and NFPA 14 doesn't carve it back 
out.

WHY IT MATTERS HERE

NFPA 13 also requires sprinkler components to be rated for at least 175 psi or 
the max pressure they're actually exposed to, whichever is greater — separate 
from how "system working pressure" is defined as a term. On a shared riser, if 
the standpipe side gets boosted to 200 psi via the FDC, that pressure is 
physically present at the riser regardless of which standard's definition 
"counts" it.

My residential sprinklers are only rated to 175 psi with no higher-rated 
alternative. If any part of the sprinkler branch could see more than 175 psi — 
even from FDC boost — that looks like a rating gap unless a PRV goes in on the 
sprinkler side of the floor control assembly.

WHAT I'D LOVE YOUR READ ON

In the 2019 edition pairing, is FDC-boosted pressure meant to count as part of 
the standpipe's "system working pressure," given NFPA 14 (2019) dropped the 
exclusion language that NFPA 13 (still) has?
For a combined system on a shared riser, does NFPA 13's exclusion of FDC 
pressure actually relieve the sprinkler branch from needing protection against 
it — or does the "rated for what it's exposed to" requirement override that 
once the riser is shared?
Practically: with 200 psi possible at the riser and 175 psi-max residential 
sprinklers with no higher-rated option, is a PRV at the sprinkler takeoff 
mandatory wherever calculated pressure (inclusive of anticipated FDC 
contribution) could exceed 175 psi? Or is there some other intended mechanism — 
FDC placard limits, a different assumption about how the two pressures interact 
on a shared riser — that I'm missing?

Any insight into the intent behind the 2019 language change, and how it's 
supposed to interact with NFPA 13's exclusion in a combined system, would 
really help.

[cid:[email protected]]
​​​​
Joe Burtell
Design Manager
D
C


406-204-4653<tel:406-204-4653>
406-861-4507<tel:406-861-4507>
3004 1st Ave South
Billings
,
MT
 59101
Office:
406‑247‑0470
www.summitfiresecurity.com<https://url.avanan.click/v2/r01/___http:/www.summitfiresecurity.com___.YXAzOnByb3RlY3Rpb25kZXNpZ25hbmRjb25zdWx0aW5nOmE6bzowYjhkNzIzMGNmYTZkMzdhYWFmMjRlY2RiNGYwZWZmNjo3OmU1YTY6ODFlMGE1MTk0N2Y4ODM4MTEyYjEyNmViNWVjNWYwY2M0N2U2OGZmYWU3MTQ3YjEzMWM3NGZiMTkwZDgxNzk1OTpoOlQ6Rg>
This is a commercial email sent by Summit Companies or one of its affiliates, 
with an office located at 1250 Northland Drive, Suite 200, Mendota Heights, MN 
55120. If you no longer wish to receive commercial emails from Summit 
Companies, please let us know by contacting us by mail or by email at 
privacy@summitcompanies to opt out.

IMPORTANT: Information contained in this e-mail may be privileged, 
confidential, and subject to other protections, including, but not limited to, 
the Electronic Communications Privacy Act, 18 U.S.C. Sections 2510-2521. If you 
are not the intended recipient, do not read, distribute, or reproduce this 
transmission. If you have received this e-mail in error, please notify the 
sender immediately and delete the message from your system. Thank you for your 
cooperation.
_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://url.avanan.click/v2/r01/___https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org___.YXAzOnByb3RlY3Rpb25kZXNpZ25hbmRjb25zdWx0aW5nOmE6bzowYjhkNzIzMGNmYTZkMzdhYWFmMjRlY2RiNGYwZWZmNjo3OjU0YjA6ZWM3ZjA2MDE4YjEwNjUzZTAyNmYzNWM3YWE3YzUyY2NmOGRhOWFmMTU1MjhiMjkwODE4MmY3ODE5NDY3YmFhNjpoOlQ6Rg>
 To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to