American Fire Sprinkler Association
12750 Merit Dr., Suite 350 Dallas TX 75251
Ph: (214) 349-5965       Fax: (214) 276-0908

----------------------------
TECHNICAL UPDATE
July 5, 2007
----------------------------

"If wood joist construction is coated with fire retardant paint with a flame spread rating of 25 or less, is it acceptable to eliminate sprinklers within that area? Would it be classified as a Class A or Class B coating?"

We have reviewed NFPA 13, 2002 edition that you indicated as the applicable standard. Our informal interpretation is that using fire retardant coatings in the combustible concealed space is not acceptable to omit sprinklers.

Sections 8.14.2.11, 2002 edition and 8.15.1.2.11, 2007 edition states, "Concealed spaces in which the exposed materials are constructed entirely of fire-retardant treated wood as defined by NFPA 703, Standard for the Fire Retardant Impregnated Wood and Fire Retardant Coatings for Building Materials, shall not require sprinkler protection." Since this section refers to fire-retardant treated wood, the definition is located within NFPA 703. The definition is "A wood product impregnated with chemical by a pressure process or other means during manufacture, which is tested in accordance with NFPA 255." In addition, there is no mention of coatings applied to the wood to reduce the flame spread in section 8.14.1.2.11.

The use of coatings in concealed combustible spaces was addressed during the 2006 ROP process in 13-192 Log #38 on page 52 with a final action of "Reject." A proposal was submitted to the committee to clean up the language since the paragraph does not explicitly specify which method of treatment is required. Since fire-retardant treated wood is not defined by NFPA 703, the existing wording has led to the misunderstanding that both fire-retardant impregnated wood and wood that has been treated with a fire-retardant coating are acceptable to meet this exception. An informal opinion from an NFPA staff member indicated that the writers' intent was to limit this exception to fire-retardant impregnated wood (compliance with Chapter 2 of NFPA 703). This conclusion is reinforced by the Canadian Wood Council (CWC) Wood Reference Handbook, which states that "Fire-retardant treated wood (FRTW) is material which has been pressure impregnated with special chemicals which improve the performance of wood products in a fire." Fire retardant coatings are tested and listed for the flame spread rating but not for the progressive burning test, and uses are limited to the description in their listings. Anecdotal reports of acceptance of fire-retardant coated lumber in attics has revealed that the coating tends to flake and deteriorate, perhaps because of humidity problems, and regular reapplications are required to maintain the coating. The committee states on the task group's decision is based on the NFPA 703 ROP draft with respect to the definition of (3.3.2) "Fire Retardant-Treated Wood." And the proposed changes to NFPA 13 will be based on the final edition of NFPA 703. Thus, only fire retardant treated wood defined according to section 3.3.2 in NFPA 703 can be used in the concealed spaces to omit sprinklers.

The Class A or B fire-retardant coatings has its application and unfortunately, concealed combustible spaces to omit sprinklers is not one of them. But for your information, when coatings are used, it has to be applied according to the manufacturer's instructions. The type of coating purchased and application would indicate whether it's a Class A or Class B coating. The difference is that a Class A coating reduces the flame spread to 25 or less, and Class B reduces the flame spread to greater than 25 but not more than 75, and both have a smoke developed rating not exceeding 200 when tested in accordance with NFPA 225.

------------------

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.

Copyright (c) 2007, American Fire Sprinkler Association. All Rights Reserved

-------------------

If you'd rather not receive future faxes from AFSA, fax your removal request to Linda Dawson at Efax (214) 242-3155 or call toll free (888) 839-4830 or send e-mail request @ [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful.