HYDRAULIC CALCULATION PROCEDURE
A new section was added regarding hydraulic calculation procedures to
clarify where the hydraulic calculations should terminate. This new
section is located at 22.4.1.5 and states, "Hydraulic calculations
shall extend to the effective point of the water supply where the
characteristics of the water supply are known." The intent of this
section is to clarify where the calculation terminates for a looped
water supply and a connection to a dead end main. The two are handled
differently. The water supply data from a flow test can be carried to
any point between the flow (pitot pressure) and test hydrants (static
and residual pressures) for a looped system. The calculations for a
dead end main have to be continued to the test hydrant (static and
residual pressures). The purpose of this is that the residual
pressure is not really known past the flow hydrant. Thus the
calculations have to be taken to the test hydrant for a dead end main
connection.
NFPA STANDARDS CYCLE
The following standards are accepting proposals for the new cycle. If
something is not clear or causing issues using these standards, now
is the time to take some action.
Annual 2009
Proposal Closing Date 10/5/2007
NFPA 13 Standard for the Installation of Sprinkler Systems
NFPA 13D Standard for the Installation of Sprinkler Systems in
One- and Two- Family Dwellings and Manufactured Homes
NFPA 13R Standard for the Installation of Sprinkler Systems in
Residential Occupancies up to and Including Four Stories in Height
NFPA 24 Standard for the Installation of Private Fire Service
Mains and Their Appurtenances
NFPA 291 Recommended Practice for Fire Flow Testing and Marking
of Hydrants
Proposal Closing Date 5/25/2007, Comment Closing Date 2/29/2008
NFPA 14 Standard for the Installation of Standpipe and Hose Systems
Notice of Intent to Make a Motion Closing Date 10/19/2007
NFPA 22 Standard for Water Tanks for Private Fire Protection
Proposal Closing Date 11/2/2007
NFPA 72 National Fire Alarm Code(r)
Proposal Closing Date 11/26/2007
NFPA 99 Standard for Health Care Facilities
Proposal Closing Date 8/31/2007, Comment Closing Date 8/31/2007
NFPA 101 Life Safety Code
----------------------
MARK YOUR CALENDARS FOR THE NEXT CLSE VIRTUAL SEMINAR
Residential Sprinkler Application
August 22, 2007
To Register:
Event ID: 12913
12:00 PM EDT
11:00 AM CDT
10:00 AM MDT
9:00 AM PDT
Earn: 0.15 CEU's / 1.5 CPD's.
Member: $ 90 per connection
Non Member: $130 per connection
CEU Certificate: $40 per listener to receive CEU Certificate. If any
listeners at your site need CEU/CPD credit, the processing fee is an
additional $40 per person. Enter each person's full name and e-mail
address you are purchasing CEU/CPD credits for including yourself to
receive Certificate
To Register:
By Phone: 800-775-7654, please have your credit card information ready.
By Fax: 800-676-0734. Fax completed form with Credit Card information.
By Mail: KRM Information Services Inc. PO Box 1187 Eau Claire, WI
54702-1187 (Payment must accompany registration)
Online: www.krm.com/afsa
2007 AFSA DESIGN SCHOOLS
Beginning System Planning School
July 9-20, 2007 Sold Out!
August 6-17, 2007 Sold Out!
October 8-19, 2007 Sold Out!
November 5-16, 2007 Sold Out!
December 3-14, 2007
Registration Prices:
Member $1200
Non-Member $1700
AFSA ANNUAL CONVENTION & EXHIBITION
Phoenix, AZ
September 26-30, 2007
Regular registration price till 8/31/07:
Member $600
Non-Member $865
----------------------------
TechTalk is prepared by the Technical Services Department of the
American Fire Sprinkler Association: Vice President of Engineering
and Technical Services, Roland Huggins, a PE registered in fire
protection engineering; Phill Brown, a CFPS and a NICET IV certified
automatic sprinkler technician, and Tom Wellen, a degreed fire
protection-engineering technologist. Opinions are provided with the
understanding that AFSA assumes no liability for the opinions or
actions taken on them and they are not to be considered the official
interpretation of the NFPA or that of its technical committees.
Copyright (c) 2007, American Fire Sprinkler Association, 12750 Merit
Dr., Suite 350, Dallas, TX 75251. Voice (214) 349-5965 ext 124 or
Fax (214) 276-0908. All rights reserved.
----------------------------
If you'd rather not receive future faxes from AFSA, fax your removal
request to Linda Dawson at Efax (214) 242-3155 or call toll free
(888) 839-4830 or send e-mail request @ [EMAIL PROTECTED]
Please include your company name and the specific fax numbers(s) at
which you do not wish to receive faxes from us. Our failure to
comply with your request may be unlawful.
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes