American Fire Sprinkler Association
12750 Merit Dr., Suite 350 * Dallas TX 75251
Ph: (214) 349-5965       Fax: (214) 276-0908

---------------------------
TECHNICAL UPDATE
OCTOBER 17, 2007
---------------------------

"I have a building of light hazard occupancy with skylights that are 24 sq. ft. with a depth of 48 in. and all skylights are separated by 10 ft. Is it the intent of NFPA 13 to separate skylights under 32 sq. ft. from ceiling pockets?"

We have reviewed the 2002 Edition of NFPA 13 that you indicated as the applicable Standard. Our informal interpretation is that skylights and ceiling pockets must be separated by 10 ft.

These two sections have different applications regarding sprinkler installations. Section 8.5.7 for skylights and similar ceiling pockets has no depth limitation. There is also no requirement for quick response sprinklers throughout the skylight compartment (unless it is light hazard) as long as the area does not exceed 32 sq. ft., and there is no regard of hazard classification of the space. There is also no requirement of the skylight to be noncombustible. When the skylight or similar ceiling pocket exceeds 32 sq. ft., then the ceiling pocket rules of 8.6.7 must be applied. For example, if you have a 4 ft by 4 ft skylight that has a depth of 4 ft, then apply section 8.5.7 where it permits the omission of sprinklers. If you have a skylight or similar ceiling pocket is 52 sq. ft. in area and 3 ft in depth, apply section 8.6.7. If the skylight or similar ceiling pocket is 52 sq. ft. in area and 4 ft in depth, the omission criteria for sprinklers cannot be accomplished for either section. The area exceeds the limit of 32 sq. ft. for section 8.5.7, and the depth exceeds the limit of 3 ft for section 8.6.7. Thus a sprinkler would be required in each skylight or ceiling pocket. As you noted, each unprotected pocket or skylight must be separated by 10 ft. There is some overlap between sections 8.5.7 and 8.6.7, but 8.6.7 does allow for larger pockets if all seven criteria are accomplished.

-----------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.

Copyright (c) 2007, American Fire Sprinkler Association. All Rights Reserved
--------------------------
If you'd rather not receive future faxes from AFSA, fax your removal request to Linda Dawson at Efax (214) 242-3155 or call toll free (888) 839-4830 or send e-mail request @ [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful. _______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes