IMPROVING THE STANDARDS
The Standard Council issued TIA 05-2 (SC 07-10-9/Log 889) on the 2005 edition of NFPA 11, Standard for Low-, Medium-, and High-Expansion Foam" modified section 4.7.3.4 as follows: "rubber or elastomeric- gasketed fittings shall not be used in fire-exposed areas hazards unless the foam system is automatically actuated, or test data is submitted to show acceptable performance under fire conditions within a fire exposed hazard."

IBC FOR THE PROTECTION OF BALCONIES AND DECKS FOR NFPA 13R SYSTEMS.
AFSA Technical Services fielded a number of calls concerning the protection of balconies and decks according to the IBC. There was a question regarding whether a sprinkler head is required to be located in the eave of the building for the protection of the balcony or deck. A head is needed according the last paragraph in the commentary. The protection for balconies and decks according to the 2006 edition in Section 903.3.1.2.1 states, "Sprinkler protection shall be provided for exterior balconies, decks and ground floor patios of dwelling units where the building is of Type V construction. Sidewall sprinklers that are used to protect such areas shall be permitted to be located such that their deflectors are within 1 inch (25mm) to 6 inches (152 mm) below the structural members and a maximum distance of 14 inches (356 mm) below the deck of the exterior balconies and decks that are constructed of open wood joist construction."

The commentary further explains this requirement that states, "Balconies, decks and patios in buildings of Type V construction and used for Group R occupancies are required to have sprinkler protection. This is in addition to the requirements of NFPA 13R, which primarily addresses the life safety of occupants and not property protection. The intent is to address hazards such as grilling and similar activities. Since NFPA 13R does not require such coverage, there is potential that a fire on a balcony could grow much too large for the system within the building to handle. The concern is that a potential exterior balcony fire could spread to unprotected floor/ceiling assemblies and attic spaces and result in major property damage. Section 308.3.1 specifically addresses restrictions on open flame cooking devices used on combustible balconies.

Regardless of whether the exterior walking surface is attached to the building and called a balcony or is a freestanding structure such as a deck or patio the concern for fire ignition in the area adjacent to the exterior wall is the same. Sidewall sprinklers should be selected based on the area of coverage and climate. If the potential for freezing exists, dry sidewall sprinkler should be used. Where the overhanging deck or balcony is extensive, an extended coverage sprinkler should be selected.

The requirement is for protection of the balcony or deck. If there is not ceiling or overhead projecting above the area, a sidewall sprinkler must still be installed to comply with the requirements. A properly located horizontal dry sidewall sprinkler, even without typical heat collection considerations, still provides protection for these exterior areas even if the sprinkler is assumed to only be activated by radiant heat effects."

Note in the requirement that the protection of balconies and decks only applies to buildings of Type V construction regardless of the balcony or deck construction. The IBC commentary indicates that type V construction allows the use of all types of materials, both noncombustible and combustible, but is not most commonly constructed of dimensional lumber.
---------------------
MARK YOUR CALENDARS FOR THE NEXT VIRTUAL SEMINAR
It's a Lot More Than Project Management December 18, 2007

To Register:
Event ID: 13464
  4:00 PM EST
  3:00 PM CST
  2:00 PM MST
  1:00 PM PST
Earn:  0.15 CEU's  / 1.5 CPD's.
         Member:       $ 90 per connection
     Non Member:        $130 per connection
CEU Certificate:      $ 40 per listener to receive CEU Certificate.

If any listeners at your site need CEU/CPD credit, the processing fee is an additional $40 per person. Enter each person's full name and e- mail address you are purchasing CEU/CPD credits for including yourself to receive Certificate

To Register:
Online: www.krm.com/clse
By Phone: 800-775-7654, please have your credit card information ready.
By Fax: 800-676-0734.  Fax completed form with Credit Card information.
By Mail: KRM Information Services Inc. PO Box 1187 Eau Claire, WI 54702-1187 (Payment must accompany registration)

OSU/AFSA FIRE SPRINKLER INSPECTION TRAINING & CERTIFICATE PROGRAM
Stillwater, OK
November 15-17, 2007

AFSA CAROLINAS CHAPTER WEEKLONG SEMINAR SERIES
Greensboro, NC
November  12-16, 2007

AFSA ON-LINE SCHOLARSHIP 2007-2008
Begins August 28, 2007 through April 11, 2008. 10 Lucky high school seniors will win a $2000 scholarship. Go to www.afsascholarship.org for more information.

---------------------------
TechTalk is prepared by the Technical Services Department of the American Fire Sprinkler Association: Vice President of Engineering and Technical Services, Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a CFPS and a NICET IV certified automatic sprinkler technician, and Tom Wellen, a degreed fire protection-engineering technologist. Opinions are provided with the understanding that AFSA assumes no liability for the opinions or actions taken on them and they are not to be considered the official interpretation of the NFPA or that of its technical committees. Copyright (c) 2007, American Fire Sprinkler Association, 12750 Merit Drive, Ste 350, Dallas, TX 75250 Voice (214) 349-5965 ext 124 or Fax (214) 343-8898. All rights reserved. If you'd rather not receive future faxes from AFSA, fax your removal request to Linda Dawson at Efax (214) 242-3155 or call toll free (888) 839-4830 or send e-mail request @ [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful.
 _______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to