"I have a retail shell building approximately 12,000 sq ft, with the possibility of having six future tenants. Am I required to zone tenants with their own system?"



We have reviewed the 2007 Edition of NFPA 13 and the 2006 Edition of the IBC as the applicable standards. Our informal interpretation is that the system does not have to be divided into separate tenant zones.



There is no requirement in NFPA 13 and the IBC states in 402.8 that "Sprinkler protection for the mall shall be independent from that provided for tenant spaces or anchors." The real key to this issue is the definition of MALL in 402.2. This section indicates that the provisions of this section shall apply to buildings or structures defined herein as covered mall buildings not exceeding three floor levels at any point nor more than three stories above grade plane. In addition, a mall is a roofed or covered common pedestrian area within a covered mall building that serves as access for two or more tenants and not to exceed three levels that are open to each other. Due to the openness between floors and the tenant spaces, there is a greater dependence on the sprinkler system within the mall. For this reason, section 402.8 requires the mall to have either an independent sprinkler system or individual control valves to each tenant space. This way the sprinkler system within a tenant space can be modified without taking the mall system out of service. The NFPA 101 Life Safety Code is consistent with a requirement just for malls and it states in 36.4.4.10.2 that "The system shall be installed in such a manner that any portion of the system serving tenant spaces can be taken out of service without affecting the operation of the portion of the system serving the mall." Thus the need to be able to individually control tenant spaces does not apply to the typical building you described with separation between the tenant spaces.


-----------------

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.



Copyright (c) 2008, American Fire Sprinkler Association. All Rights Reserved

--------------------------

If you'd rather not receive future faxes from AFSA, fax your removal request to Amy Sweeney at Efax (214) 242-3155 or call toll free (888) 839-4830 or send e-mail request @ [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful. _______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to