I have a situation where there is a stair with approximately 70 ft  
elevation difference between the lowest and highest landing. The stair  
is open where there are no walls around it and is exposed to the  
atrium and other areas of the building. The sprinklers serving the  
stair are served from a control valve off the atrium sprinklers at the  
high roof level. How do you properly size the pipe for the sprinklers  
serving the stair? Would the pipe serving the sprinklers for the stair  
fall under 11.2.3.4.2 and calculate only seven of the 10 sprinklers  
operating since the stair is not enclosed?



We have reviewed NFPA 13, 2002 Edition that you indicated as the  
applicable standard. Our informal interpretation is that the stair  
should be treated as a special design area.



Section 8.14.17 indicates that stairs, towers, or other construction  
with incomplete floors, if piped on independent risers, shall be  
treated as one area with reference to pipe sizes. The commentary for  
8.14.17 indicates that stair towers can open a large percentage of  
sprinklers in the area. An independent riser supplying a stair or  
tower must be sized to supply all the sprinklers.  Since your  
application has the stairs open to the atrium, sizing the pipe to all  
sprinklers operating does not apply. The most logical method for an  
open stair is to treat it as one area since the stair is piped with a  
single line from the top and is independent of each floor. It is not  
likely to activate many heads in this open stair application. Thus  
using Section 11.2.3.4.2 for special design areas to calculate all  
sprinklers on the line up to a maximum of seven would apply.





-----------------

Technical Update is prepared by the Technical Services Dept. of the  
AFSA: Vice President of Engineering and Technical Services Roland  
Huggins, a PE registered in fire protection engineering; Phill Brown,  
a NICET IV certified automatic sprinkler technician and NFPA Certified  
Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire  
protection engineering technologist.  This is provided with the  
understanding that the AFSA assumes no liability for this opinion or  
actions taken on it and they are not to be considered the official  
position of the NFPA or its technical committees.



  Copyright © 2009, American Fire Sprinkler Association.  All Rights  
Reserved



--------------------------

If you╒d rather not receive future faxes from AFSA, fax your removal  
request to Amy Sweeney at efax (214) 242-3155 or call toll free (888)  
839-4830 or send e-mail request @ [email protected].   Please  
include your company name and the specific fax numbers(s) at which you  
do not wish to receive faxes from us.  Our failure to comply with your  
request may be unlawful.
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to