American Fire Sprinkler Association
12750 Merit Dr., Suite 350 * Dallas TX 75251
Ph: (214) 349-5965        Fax: (214) 276-0908

-----------------
TECHNICAL UPDATE
JULY 9, 2009
-----------------

“What is the classification of occupancy hazard for a hydraulic  
elevator machine room? What is the classification of occupancy hazard  
for the bottom of a hydraulic elevator hoist way with combustible  
hydraulic fluid?”

We have reviewed NFPA 13, 1999 Edition that you identified as the  
applicable standard. Our informal interpretation is the hydraulic  
elevator equipment use areas are an ordinary hazard occupancy  
classification.

The amount of fluid, operating pressure of the hydraulic unit, and  
that the elevator equipment is confined within a room or elevator  
shaft.  The hazard of hydraulic elevators is not similar to high- 
pressure hydraulic equipment used in manufacturing, industrial  
processes, and aircraft simulators in larger open areas where these  
occupancy hazards are indicated as Extra Hazard (Group I) for  
combustible hydraulic use areas. The intent of the standard is that  
the Extra Hazard (Group I) Occupancy class does not apply to elevators  
since the systems are smaller and have less pressure where the  
atomized fluid flaming fire is not a likely hazard. This was confirmed  
with NFPA staff. However, it seems like one could argue that the  
bottom of the shaft could be Light Hazard since the fuel loading is  
less than an office area. The predominate hazard is accumulated trash  
that falls down into the pit combined with a minor amount of hydraulic  
fluid (rather than a burning pool). Ordinary hazard versus Light  
Hazard is irrelevant since it is a small area with a sprinkler at 7  
psi with an area of 8 ft X 8 ft provides a density of Ordinary Hazard  
(Group 2). As with all ambiguous issues, discussion with the AHJ  
beforehand is a good idea.
----------------
Technical Update is prepared by the Technical Services Dept. of the  
AFSA: Vice President of Engineering and Technical Services Roland  
Huggins, a PE registered in fire protection engineering; Phill Brown,  
a NICET IV certified automatic sprinkler technician and NFPA Certified  
Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire  
protection engineering technologist. This is provided with the  
understanding that the AFSA assumes no liability for this opinion or  
actions taken on it and they are not to be considered the official  
position of the NFPA or its technical committees.

Copyright © 2009, American Fire Sprinkler Association. All Rights  
Reserved
--------------------------
If you’d rather not receive future faxes from AFSA, fax your removal  
request to Amy Sweeney at Efax (214) 242-3155 or call toll free (888)  
839-4830 or send e-mail request @ [email protected]. Please  
include your company name and the specific fax numbers(s) at which you  
do not wish to receive faxes from us.  Our failure to comply with your  
request may be unlawful.

_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to