August 13, 2009

------------------------



"I have an interior canopy mounted in three different configurations;  
(1) on a  wall,(2)on the face of a furred down ceiling with an EC  
sprinkler under the ceiling, and (3) on the fascia of a floating  
ceiling. Sprinkler deflectors at the ceiling are located more than 18  
inches above the canopies. Are sprinklers required under the interior  
canopies that are noncombustible fabric and 30 inches wide?"



In response to your question we have reviewed NFPA 13, 2007 Edition as  
the applicable standard. Our informal interpretation is that  
sprinklers are not required under the canopies.



Section 8.15.7 addresses canopies but that is for "exterior" canopies  
on a building. The standard does not address interior canopies but the  
application is more suited for obstruction rules. Section 8.5.5.3.1  
indicates that sprinklers shall be installed under fixed obstructions  
over 4 ft wide such as ducts, decks, open grate flooring, cutting  
tables, and overhead doors. Sprinklers are not required under the  
canopy since it is less than 4 ft wide. This would apply to all three  
situations you noted in the question above as long as the sprinklers  
are spaced according to NFPA 13. A similar situation was presented for  
shelf type obstructions located against the wall during the A2009  
Report on Comments in 13-87 Log #21. New annex material and a figure  
will clarify that obstructions located against a wall and located  
entirely below the 18-inch plane from the sprinkler deflector should  
be in accordance with 8.6.5.3.3. Note this annex falls under standard  
pendent and upright sprinklers but it seems appropriate to apply this  
rationale to any sprinkler type that has obstruction rule wording  
similar to 8.5.5.3.1.



-----------------

Technical Update is prepared by the Technical Services Dept. of the  
AFSA: Vice President of Engineering and Technical Services Roland  
Huggins, a PE registered in fire protection engineering; Phill Brown,  
a NICET IV certified automatic sprinkler technician and NFPA Certified  
Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire  
protection engineering technologist. This is provided with the  
understanding that the AFSA assumes no liability for this opinion or  
actions taken on it and they are not to be considered the official  
position of the NFPA or its technical committees.



  Copyright ⌐ 2009, American Fire Sprinkler Association.  All Rights  
Reserved

--------------------------

If you'd rather not receive future faxes from AFSA, fax your removal  
request to Linda Dawson at Efax (214) 242-3155 or call toll free (888)  
839-4830 or send e-mail request @ [email protected]. Please  
include your company name and the specific fax numbers(s) at which you  
do not wish to receive faxes from us.  Our failure to comply with your  
request may be unlawful.



  
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to