“When a pump is employed in conjunction with a water storage tank  
utilized as a secondary water source in seismic applications, how is  
the pump sized?”

We have reviewed IBC, 2006 Edition and NFPA 13, 2007 Edition that you  
indicated as the applicable standard. Our informal interpretation is  
the fire pump is sized based on both water sources.

For higher seismic design categories, IBC 903.3.5.2 requires a  
secondary on-site water supply equal to the hydraulic calculated  
sprinkler demand, including the hose stream requirement. As identified  
in NFPA 13:23.1.2 – “Water supplies shall be capable of providing the  
required flow and pressure….” Thus, the supply includes the pump and  
it must be capable of meeting the system demand whether the water is  
from the street or an on-site tank. The impact is that the pump must  
be sized for both available pressures. Typically, the street provides  
a higher-pressure contribution so it must be applied when evaluating  
the maximum churn pressure to ensure the system pressure rating is not  
exceeded. The contribution from the tank (assuming it is near ground  
level and does not exceed the pressure provided by the street supply)  
would be a lower pressure contribution and would be used to determine  
the minimum pump size in order to meet the sprinkler demand.

-----------------
Technical Update is prepared by the Technical Services Dept. of the  
AFSA: Vice President of Engineering and Technical Services Roland  
Huggins, a PE registered in fire protection engineering; Phill Brown,  
a NICET IV certified automatic sprinkler technician and NFPA Certified  
Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire  
protection engineering technologist. This is provided with the  
understanding that the AFSA assumes no liability for this opinion or  
actions taken on it and they are not to be considered the official  
position of the NFPA or its technical committees.

Copyright © 2009, American Fire Sprinkler Association.  All Rights  
Reserved
--------------------------
If you’d rather not receive future faxes from AFSA, fax your removal  
request to Amy Sweeney at Efax (214) 242-3155 or call toll free (888)  
839-4830 or send e-mail request @ [email protected]. Please  
include your company name and the specific fax numbers(s) at which you  
do not wish to receive faxes from us.  Our failure to comply with your  
request may be unlawful.



_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to