HORIZONTAL CONCEALED COMBUSTIBLE SPACES
The 2007 Edition of NFPA 13 requires a listed sprinkler in some  
horizontal combustible concealed spaces. This is located in Section is  
8.15.1.6 where it states, “Sprinklers used in horizontal combustible  
concealed spaces (with a slope not exceeding 2 in 12) with combustible  
wood truss or wood joist construction having a combustible upper  
surface and where the depth of the space is less than 36 in. from deck  
to deck or with double wood joist construction with a maximum of 36  
in. between the top of the bottom joist and the bottom of the upper  
joist shall be listed for such use.” Note that from the above section  
that a combustible wood deck as well as ALL the other conditions must  
be present to require the listed sprinkler. However, if there are wood  
joists with a metal deck, it is obviously still a combustible  
concealed space and must be protected but standard spray sprinklers  
can be used. It is also worth noting that Section 8.15.1.7 states that  
for composite wood joist construction, these listed sprinklers shall  
be PERMITTED to be used to provide protection of combustible concealed  
spaces described in 8.15.1. This is interesting because PERMITTED  
means it’s an OPTION verses a requirement.

The current specially listed sprinklers available for horizontal  
combustible concealed applications are Tyco CC1, CC2, and Viking's  
COIN sprinklers.  Pay very close attention to the manufacturer’s data  
sheets. These instructions are very specific for different  
applications regarding the type of pipe and the type of construction  
for the horizontal combustible space. These instructions were  
generated after fire tests conducted in the listing laboratories.   
There are requirements for draft curtains, deflector placements,  
obstruction rules, blocking within the channel spaces, and the  
installation of noncombustible insulation installation between the  
joists. The amount of insulation is driven by the type of construction  
since solid wood joist has a maximum allowed channel depth whereas  
composite wood joist require the channels to be filled.

When these spaces have CPVC piping, the installation manuals from the  
manufacturers also indicate the requirement for specially listed  
sprinklers for the horizontal concealed combustible spaces. The  
BlazeMaster Installation and Specification manual indicates that pipe  
and fittings must never be installed in combustible concealed spaces  
requiring sprinklers, as referenced in NFPA 13.  Then the manual  
indicates exceptions such as the use of specially listed sprinkler  
heads that have been tested and are listed for use with BlazeMaster  
products in combustible concealed spaces requiring sprinklers. When  
using BlazeMaster products in these applications, always follow the  
sprinkler manufacturers' installation guidelines. The other  
manufacturers' literature from Victaulic and Spear's Flameguard CPVC  
installation manuals also indicate similar requirements

-------------


NEW!  System Layout School for   Residential One & Two-Family Dwelling
October 5-9, 2009
Registration Prices:

     Member   $750
Non-Member   $1150
Special 20% Discount for members: $600

2009 AFSA DESIGN SCHOOLS
Beginning System Planning School
November 9-20, 2009

Registration Prices:
     Member   $1100
Non-Member   $1600

NOTE: Enrollment open only to AFSA Contractor Members until 6 weeks  
prior to each class

AFSA/OSU Fire Sprinkler Inspection Training & Certificate Program
Stillwater, OK
November 2-4, 2009      

AFSA 28th Annual Convention & Exhibition

Registration Prices After 9/4/09
     Member   $700
Non-Member   $925

NEW! Applied Sprinkler Technology Multi-Part Series – On-Line
     Member $125
Non-Member $155

Part 1,2,3 are available on AFSA’s Fire Sprinkler e-Campus now!

----------------------
TechTalk is prepared by the Technical Services Department of the  
American Fire Sprinkler Association: Vice President of Engineering and  
Technical Services, Roland Huggins, a PE
registered in fire protection engineering; Phill Brown, a CFPS and a  
NICET IV certified automatic sprinkler technician, and Tom Wellen, a  
degreed fire protection-engineering technologist.  Opinions are  
provided with the understanding that AFSA assumes no liability for the  
opinions or actions taken on them and they are not to be considered  
the official interpretation of the NFPA or that of its technical  
committees.
Copyright (c) 2009, American Fire Sprinkler Association, 12750 Merit  
Drive, Ste 350, Dallas, TX 75251.   Voice (214) 349-5965 ext 124 or  
Fax (214) 276-0908.  All rights reserved.
If you’d rather not receive future faxes from AFSA, fax your removal  
request to (888) 839-4830 or e-mail to
[email protected]. Please include your company name and the  
specific fax numbers(s) at which you
do not wish to receive faxes from us.  Our failure to comply with your  
request may be unlawful.


_______________________________________________
Sprinklernotes mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to