American Fire Sprinkler Association

12750 Merit Dr., Suite 350,  Dallas TX 75251

Ph: (214) 349-5965   Fax: (214) 276-0908


-----------------------
TECHNICAL UPDATE

OCTOBER 14, 2009

-----------------------


We have a dry pipe system installed in an attic with a sloped  
ceiling.  Near some of the attic spray sprinklers are return bends to  
sprinklers below the ceiling and are covered with 2 ft wide batt  
insulation. It looks like a small curtain next to the sprinkler. An  
inspector has flagged these as obstructions and indicated 8.6.5.2.2  
for floor mounted obstructions apply. Considering that the ceiling is  
sloped, what is the appropriate evaluation as an obstruction for these  
items?


We have reviewed the 2007 edition of NFPA 13 you indicated as the  
applicable standards. Our informal interpretation is the covered  
return bends fall under section 8.6.5.2: Obstructions to Sprinkler  
Discharge Pattern Development.


This is actually a very interesting question because when you look  
down the plane along the floor of the attic, the insulation appears  
above the sprinkler.  In actuality, though, you should be looking down  
the plane of the ceiling since we are evaluating the impact on the  
water discharge and the deflectors are required to be installed  
parallel to the ceiling as per 8.5.4.2. So with that plane of  
reference in mind, lets consider how to address the obstruction. First  
off, let╒s address whether it should be considered a floor mounted  
obstruction since the batt insulation does touch the floor. As stated  
in 8.6.5.2.2, it is guidance for privacy curtains, freestanding  
partitions, room dividers, and similar obstructions. All of these  
listed items are expected to obstruction a wider portion of the  
sprinkler discharge whereas the batt insulation is only 2 ft wide so  
the regular obstructions rules should be applied. As in all  
obstructions, one should step through the three sections to determine  
which one applies. Starting with 8.6.5.1, we can skip this one since  
it is for obstructions tight (or very close) to the ceiling. Moving to  
8.6.5.2 looks right since it is for obstructions less than 18 inches  
below the deflector (since we are looking down the plane of the  
ceiling). You do still have to consider two issues. First is this a  
continuous obstruction (defined as affecting two or more adjacent  
sprinklers. It is not. The second issue is a bit more obscure but as  
discussed in A.8.6.5.2.1.4, you have to ensure that the obstruction is  
not butted up beside the sprinkler so as to obstruct close to half the  
water discharge. These should then been consider continuous  
obstructions even though it does not affect two or more sprinklers.  
Since this is not the case, this section applies.

-----------------

Technical Update is prepared by the Technical Services Dept. of the  
AFSA: Vice President of Engineering and Technical Services Roland  
Huggins, a PE registered in fire protection engineering; Phill Brown,  
a NICET IV certified automatic sprinkler technician and NFPA Certified  
Fire Protection Specialist (CFPS); and Tom Wellen, a degreed fire  
protection engineering technologist. This is provided with the  
understanding that the AFSA assumes no liability for this opinion or  
actions taken on it and they are not to be considered the official  
position of the NFPA or its technical committees.

Copyright 2009 American Fire Sprinkler Association.  All rights  
reserved.
--------------------------

If you╒d rather not receive future faxes from AFSA, fax your removal  
request to Amy Sweeney at Efax (214) 242-3155 or call toll free (888)  
839-4830 or send e-mail request at [email protected].   Please  
include your company name and the specific fax numbers(s) at which you  
do not wish to receive faxes from us.  Our failure to comply with your  
request may be unlawful.



_______________________________________________
Sprinklernotes mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to