“We have a 4-story concrete parking structure with a non-combustible open 
stairway attached to the exterior of the building. Would heads be required at 
each level?”

We have reviewed NFPA 13, 2002 Edition that you indicated as the applicable 
standard as well as the 2007 edition of NFPA 13. Our informal interpretation is 
that sprinklers are not required within the stairway.

The 2002 edition does not explicitly address this issue but the 2007 edition 
clarified it. Section 8.15.3.2.4 (which is the same subject as 8.14.3.2 in the 
02 edition) states: Sprinklers shall be permitted to be omitted from exterior 
stair towers when the exterior walls of the stair tower are at least 50% open 
and when the stair tower is entirely of noncombustible construction. This is 
pretty common construction for parking garages and shows the intent of the 
technical committee even for older editions of NFPA 13 (even if you have to 
apply the 13:1.5 Equivalency Clause). It should also be noted that a sprinkler 
is not required at the top or under the first landing as dictated by 
8.14.3.2.1.  That criterion is for shafts, which by its very name is an 
enclosed construction element.

-----------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President of Engineering and Technical Services Roland Huggins, a PE registered 
in fire protection engineering; Phill Brown, a NICET IV certified automatic 
sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and 
Tom Wellen, a degreed fire protection engineering technologist.  This is 
provided with the understanding that the AFSA assumes no liability for this 
opinion or actions taken on it and they are not to be considered the official 
position of the NFPA or its technical committees. 

 Copyright © 2009, American Fire Sprinkler Association.  All Rights Reserved
--------------------------
If you’d rather not receive future faxes from AFSA, fax your removal request to 
Linda Dawson at Efax (214) 242-3155 or call toll free (888) 839-4830 or send 
e-mail request @ [email protected]. Please include your company name and 
the specific fax numbers(s) at which you do not wish to receive faxes from us.  
Our failure to comply with your request may be unlawful.


_______________________________________________
Sprinklernotes mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to