American Fire Sprinkler Association
12750 Merit Dr., Suite 350 * Dallas TX 75251
Ph:(214) 349-5965         Fax:(214) 276-0908

--------------------------
December 2, 2009
--------------------------


Testing Antifreeze Systems with CPVC to Verify the Solution is Glycerin

In the November 5, 2009 Tech Update, we identified that one could use a field 
test for glycol (such as that provided by the Noble Company) to indirectly 
determine whether the correct compound was in use by showing that the wrong 
compound (ie glycol) is not present. Such a step seemed a reasonable approach 
since we are not aware of any field test for glycerin.  In further 
conversations with Noble, it has been decided that such an approach NOT be 
applied.  Although the test strips will reliably identify glycerin manufactured 
by Noble, it may or may not identify that produced by other manufacturers.  It 
is also possible for compounds other than glycerin to trigger a positive 
result.  Thus, with the potential for false positives and false negatives, 
Noble tests strips for glycol is not an answer to our needs.

Keeping in mind that the owner is responsible for their fire protection 
systems, including complying with NFPA 25 where required, and that they are 
hiring inspectors to perform portions of NFPA 25 (granted it is often the vast 
majority of it), discussing this issue with your client and addressing it 
contractually is warranted.

-----------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President of Engineering and Technical Services Roland Huggins, a PE registered 
in fire protection engineering; Phill Brown, a NICET IV certified automatic 
sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and 
Tom Wellen, a degreed fire protection engineering technologist.  This is 
provided with the understanding that the AFSA assumes no liability for this 
opinion or actions taken on it and they are not to be considered the official 
position of the NFPA or its technical committees.

Copyright © 2009, American Fire Sprinkler Association.  All Rights Reserved
--------------------------
If you’d rather not receive future faxes from AFSA, fax your removal request to 
Amy Sweeney at Efax (214) 242-3155 or call toll free (888) 839-4830 or send 
e-mail request @ [email protected].   Please include your company name 
and the specific fax numbers(s) at which you do not wish to receive faxes from 
us.  Our failure to comply with your request may be unlawful.