“We perform a functional flow test at the finals for all residential sprinkler 
systems. When we did the flow test we made the gallons per minute, but the 
pressures were 5 psi or less (gauges were not calibrated very low). I indicated 
to the contractor that we needed the operating pressures at the two heads to 
flow in accordance with the technical data sheet, e.g. Reliable Model RFC 43 
Concealed on a 16 X 16 spacing, 13 gpm at 9.1 psi. He indicated that the 
pressures are irrelevant because the gallons were met. We explained that proper 
head discharge patterns would not be achieved if the required pressures were 
not meet. He further challenged. The contractor stated that he further 
investigated and installed a pressure gauge up stream on the head before the 
two remote heads (closer to the riser) and it had 10 psi, but only 5 psi at the 
head, we stated that would not be acceptable because the pressure at the remote 
heads need to be obtained. Can the pressure at the sprinkler be measured?”

We have reviewed NFPA 13D, 2007 Edition that you indicated as the applicable 
standard. Our informal interpretation is that attempting to field measure the 
pressures at the sprinkler may indicate inaccurate pressures. 

Nowhere in the standard is acceptance testing mentioned other than checking the 
piping for leaks at the system working pressure or if an FDC is present, a 
standard hydrostatic test.  Hydraulic calculations are performed to determine 
the minimum necessary flow and pressure needed on the system all the way to the 
city main. These formulas and procedures are themselves based on tests, 
verified by NFPA, SFPE, FMRC, UL and every single sprinkler manufacturer. The 
whole purpose of NFPA 13D requiring hydraulic calculations is to provide a 
scientific, reproducible and cost-effective means of determining the necessary 
water flow and pressure. A sprinkler flow test may not accurately measure 
pressure, is not reproducible, and is labor intensive.  However, there have 
been cases where the fire marshal is suspicious of these calculations and wants 
a flow test performed. The focus should be instead to diligently verify the 
calculations and that the installed piping and components matches that used in 
the calculation, ensure the reading for the city water supply is accurate, and 
determine if the supply is greater than the demand as indicated by NFPA 13.

----------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President of Engineering and Technical Services Roland Huggins, a PE registered 
in fire protection engineering; Phill Brown, a NICET IV certified automatic 
sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and 
Tom Wellen, a degreed fire protection engineering technologist.  This is 
provided with the understanding that the AFSA assumes no liability for this 
opinion or actions taken on it and they are not to be considered the official 
position of the NFPA or its technical committees. 

 Copyright © 2009, American Fire Sprinkler Association.  All Rights Reserved
--------------------------
If you’d rather not receive future faxes from AFSA, fax your removal request to 
Linda Dawson at Efax (214) 242-3155 or call toll free (888) 839-4830 or send 
e-mail request @ [email protected]. Please include your company name and 
the specific fax numbers(s) at which you do not wish to receive faxes from us.  
Our failure to comply with your request may be unlawful.

_______________________________________________
Sprinklernotes mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to