TEST CONNECTIONS FOR ANTIFREEZE SYSTEMS LARGER THAN 150 GALLONS

A new requirement was added in the 2010 Edition of NFPA 13 to provide  
connections for every 100 gal when the system capacity is larger than  
150 gal as indicated by Section 7.6.3.7. This was needed to correlate  
with the NFPA 25 requirement that was added in the 2008 Edition.  
Section 5.3.4.3 of NFPA 25 states, “The antifreeze solution shall be  
tested at its most remote portion and where it interfaces with the wet- 
pipe system. When antifreeze systems have a capacity larger than 150  
gal, tests at one additional point for every 100 gal shall be made. If  
the test results indicated an incorrect freeze point at any point in  
the system, the system shall be drained.” The change was needed in  
NFPA 13 to provide the test connections during the installation of the  
system.



TEMPERATURE RATINGS

The 2010 Edition of NFPA 13 now allows intermediate-temperature  
sprinklers to be used throughout buildings in section 8.3.2.1. The  
2010 Edition of the Sprinkler Systems Handbook commentary indicates  
that traditionally, ordinary-temperature sprinklers have been required  
throughout a building unless the requirements of 8.3.2 required  
intermediate- or high-temperature sprinklers to be used.  However,  
many buildings are built without suspended ceilings, resulting in a  
mix of ordinary with the intermediate-temperature-rated sprinklers  
needed around heating diffusers and other heat-producing areas. Since  
the response time of quick-response intermediate-temperature  
sprinklers is not that different from ordinary-temperature standard- 
response sprinklers, the standard now groups ordinary- and  
intermediate-temperature sprinklers together and allows intermediate- 
temperature sprinklers throughout the building, reducing the need for  
multiple types of sprinklers.



DIFFUSERS DISCHARGING LESS THAN 100 DEGREES F

A new section was added in the 2010 Edition of NFPA 13 where  
sprinklers no longer have to be separated from HVAC ducts for ordinary  
temperature rated sprinklers when the diffuser discharge is less than  
100 degrees F. The new section is located under 8.3.2.5(9) and it  
states, “Ordinary-temperature sprinklers located adjacent to a heating  
duct that discharges are that is less than 100 degrees F are not  
required to be separated in accordance with Table 8.3.2.5(a).” There  
are many HVAC systems that function with lower temperature airflows  
and the requirements of Table 8.3.2.5(a) would not apply.



-----------------------------------



2010 AFSA DESIGN SCHOOLS

Beginning System Planning School

February 22-March 5, 2010

April 19-30, 2010

July 12-23, 2010

October 11-22, 2010

Registration Prices:

Special Member $880

Non-Member $1600



NOTE: Enrollment open only to AFSA Contractor Members until 6 weeks  
prior to each class





2010 System Layout School for Residential I & 2 Family Dwellings School

March 22-26, 2010

June 21-25, 2010

August 23-27, 2010

Registration Prices:

Special Member $600

Non-Member   $1150





AFSA/OSU Fire Sprinkler Inspection Training & Certificate Program

Oklahoma State University

Stillwater, OK

January 14-16, 2010

March 22-24, 2010

Registration Price:

Member $945



--------------------------

TechTalk is prepared by the Technical Services Department of the  
American Fire Sprinkler Association: Vice President of Engineering and  
Technical Services, Roland Huggins, a PE registered in fire protection  
engineering; Phill Brown, a CFPS and a NICET IV certified automatic  
sprinkler technician, and Tom Wellen, a degreed fire protection- 
engineering technologist.  Opinions are provided with the  
understanding that AFSA assumes no liability for the opinions or  
actions taken on them and they are not to be considered the official  
interpretation of the NFPA or that of its technical committees.


Copyright (c) 2009, American Fire Sprinkler Association, 12750 Merit  
Drive, Ste 350, Dallas, TX 75251. Voice (214) 349-5965 ext 124 or Fax  
(214) 276-0908. All rights reserved.

----------------------------

If you’d rather not receive future faxes from AFSA, fax your removal  
request to (888) 839-4830 or e-mail to [email protected].  
Please include your company name and the specific fax numbers(s) at  
which you do not wish to receive faxes from us. Our failure to comply  
with your request may be unlawful.



  
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to