American Fire Sprinkler Association
12750 Merit Dr., Suite 350 * Dallas TX 75251
Ph: (214) 349-5965        Fax: (214) 276-0908

---------------
April 23, 2010
---------------

“8.16.2.4.3 allows control valves in the riser down stream of the fire 
department connection (FDC) when installed on the underground. If the 
underground supplies more than one riser can the FDC be installed on the 
underground so that one FDC is serving both systems even if the risers have 
control valves on them?”

We have reviewed NFPA 13, 2002 Edition that you indicated as the applicable 
standard as well as the 2010 Edition. Our informal interpretation is that the 
FDC can be located on the underground with riser control valves in place.

There may be some confusion where the fire department connection is made to the 
underground main on the supply side or system side. The connection must be 
downstream of the backflow preventer or check valve to ensure the water from 
the fire department connection does not flow back into the municipal water 
supply.  The typical city water valve pit arrangements are located in figures 
A.8.16.2 (a) and A.8.16.2 (b) (A.8.17.2 (a) and (b) 2010 Edition) that shows 
the fire department connection piping connecting on the system side of the 
backflow preventer.  Additionally, there is the issue of the control valves 
between the fire department connection and the sprinkler systems. Some control 
valves are permitted in the fire department connection piping as identified in 
section 8.16.2.4.4 (8.17.2.4.4 2010 Edition). It indicates that he requirements 
of 8.16.2.4.2 and 8.16.2.4.3 (8.17.2.4.2 and 8.17.2.4.3 2010 Edition) shall not 
apply where the fire department connection is connected to the underground 
piping. Section 8.16.2.4.2 indicates that fire department piping connections 
are on the system side of system control, check, and alarm valves for wet pipe 
systems, and section 8.16.2.4.3 indicates the connection shall be between the 
supply control valves and the system control valves for multiple systems. As 
such, Section 8.16.2.4.4 allows control valves to be located on the riser 
downstream of the FDC. This was clarified in the 2010 Edition of NFPA 13 from 
new Figures A.8.17.2.4.4(a) and A.8.17.2.4.4 (b).

-----------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President of Engineering and Technical Services Roland Huggins, a PE registered 
in fire protection engineering; Phill Brown, a NICET IV certified automatic 
sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and 
Tom Wellen, a degreed fire protection engineering technologist. This is 
provided with the understanding that the AFSA assumes no liability for this 
opinion or actions taken on it and they are not to be considered the official 
position of the NFPA or its technical committees. 

 Copyright © 2010, American Fire Sprinkler Association.  All Rights Reserved
--------------------------
If you’d rather not receive future faxes from AFSA, fax your removal request to 
Amy Sweeney at Efax (214) 242-3155 or call toll free (888) 839-4830 or send 
e-mail request @ [email protected]. Please include your company name and 
the specific fax numbers(s) at which you do not wish to receive faxes from us.  
Our failure to comply with your request may be unlawful.

_______________________________________________
Sprinklernotes mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to