American Fire Sprinkler Association
12750 Merit Dr., Suite 350 * Dallas TX 75251
Ph: (214) 349-5965        Fax: (214) 276-0908

-----------------
TECHNICAL UPDATE
May 13, 2010
-----------------

Both NFPA 13 and 24 use the following text to address backflow preventers: 
“Shall be listed for fire protection services.” The AHJ is taking the position 
that this is a special UL listing and UL listed is not adequate. This wording 
does differ from other “listed” references in NFPA 24 and 13 where similar 
terminology exists. Is it the intent that cross connection control devices must 
have a listing specifically for fire protection service or is the sole intent 
that the equipment be “UL Listed”?”  

We have reviewed the 2010 Editions of NFPA 13 and NFPA 24 as the applicable 
standards. Our informal interpretation is that these devices are listed in the 
UL 2008 Fire Protection Equipment Directory. 

The backflow devices are listed in the directory but are “Classified as to 
friction loss and strength of body ONLY” as, indicated in the general guide 
information for the Backflow Special Check Valve Devices category. The 2002 and 
2010 Editions of the Automatic Sprinkler Systems Handbook clarified this issue. 
 The commentary to A.3.2.3 states, “At least one agency uses the designation 
classified to indicate that a specific product meets its testing and evaluation 
requirements. Materials with this designation meet the intent of the term 
listed”. Thus, the UL Fire Protection Equipment Directory does list backflow 
preventers and meets the intent of the NFPA 13 standard.

-----------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President of Engineering and Technical Services Roland Huggins, a PE registered 
in fire protection engineering; Phill Brown, a NICET IV certified automatic 
sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and 
Tom Wellen, a degreed fire protection engineering technologist. This is 
provided with the understanding that the AFSA assumes no liability for this 
opinion or actions taken on it and they are not to be considered the official 
position of the NFPA or its technical committees. 

 Copyright © 2010, American Fire Sprinkler Association.  All Rights Reserved
--------------------------
If you’d rather not receive future faxes from AFSA, fax your removal request to 
Amy Sweeney at Efax (214) 242-3155 or call toll free (888) 839-4830 or send 
e-mail request @ [email protected]. Please include your company name and 
the specific fax numbers(s) at which you do not wish to receive faxes from us.  
Our failure to comply with your request may be unlawful.

_______________________________________________
Sprinklernotes mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to