American Fire Sprinkler Association
12750 Merit Dr., Suite 350  *  Dallas TX 75251
Ph: (214) 349-5965          Fax: (214) 276-0908

-----------------
TECHNICAL UPDATE
JUNE 9, 2010
-----------------

“We are performing sprinkler inspections on older residential type systems.  We 
have noted on our inspection form that no hydraulic plate is on the system.  
When the inspection is reviewed by the fire marshal, they are requesting a 
sign.  Are hydraulic signs required per NFPA 13D or NFPA 25?”

We have reviewed the 2008 Edition of NFPA 25 and the 2010 Edition of NFPA 13D 
as the applicable standards. Our informal interpretation is that the standards 
do not require a hydraulic data plate for NFPA 13D applications. 

The requirement for a hydraulic data plate or placard (as often called but 
technically labeled the Hydraulic Design Information Sign) is part of NFPA 13 
(section 24.5). NFPA 13D has no such requirement. It's also interesting to note 
that IFC section 901.6.1 requires inspections per NFPA 25. NFPA 13D systems are 
explicitly excluded from the scope of NFPA 25 according to section 1.1.3. As 
such, inspections aren't even required by the codes. However, keep in mind in 
the future that there will be a change in the 2012 Edition of the IBC for NFPA 
13D systems classified as Institutional or “I” occupancies. Institutional or 
“I” occupancies using the NFPA 13D allowance in IBC will require a hydraulic 
placard and inspection as if it was a NFPA 13R system.
-----------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President of Engineering and Technical Services Roland Huggins, a PE registered 
in fire protection engineering; Phill Brown, a NICET IV certified automatic 
sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and 
Tom Wellen, a degreed fire protection engineering technologist. This is 
provided with the understanding that the AFSA assumes no liability for this 
opinion or actions taken on it and they are not to be considered the official 
position of the NFPA or its technical committees. 

 Copyright © 2010, American Fire Sprinkler Association.  All Rights Reserved
--------------------------
If you’d rather not receive future faxes from AFSA, fax your removal request to 
Amy Sweeney at Efax (214) 242-3155 or call toll free (888) 839-4830 or send 
e-mail request @ [email protected]. Please include your company name and 
the specific fax numbers(s) at which you do not wish to receive faxes from us.  
Our failure to comply with your request may be unlawful.