Freeze Protection In Coolers

"I have a client with a large warehouse cooler storing shelled peanuts at a 
strict
temperature between 34 and 36 degrease F because if the product freezes it will 
be ruined. With reference to 8.16.4.1.1, and although it will be below 40 
degrees
F, would this cooler need to be protected with a dry system since it is so 
strictly
controlled to stay above freezing?"

We have reviewed NFPA 13, 2010 edition that you indicated as the applicable 
standard.
Our informal interpretation is that since the area is not subject to freezing, a
 dry pipe system would not be required.

Section 8.16.4.1.1 indicates that where portions of systems are subject to 
freezing
and temperatures cannot reliably be maintained at or above 40 degrees F, 
sprinklers
shall be installed as a dry pipe or preaction system. Note the use of the word 
"and"
in the sentence. This means both conditions have to be true before the 
requirement
is applicable. So, if you are installing a sprinkler system an area that is not 
subject to freezing, a dry pipe system is not required, even though there may 
not
be means of reliably maintaining a minimum temperature of 40 degrees F. Also, if
 the area is subject to freezing, but there is a reliable means of maintaining 
the
temperature at 40 degrees F or higher, a dry system is not required. Since the 
area
in question is in a cooler (an enclosed environment where the temperature is 
mechanically
controlled) where strict temperature controls are maintained between 34 and 36 
degrease
F, it is considered not subject to freezing. Thus, freeze protection is not 
required.
Care must be taken in the placement of sprinklers near the discharge for the 
coolers
if the air temperature is less than 32 degrees F. A proposal was submitted for 
the
2013 edition of NFPA in 13-291 Log #62 with a final action of Accept in 
Principle.
New wording for 8.16 indicates that piping shall be permitted to be installed in
 areas where the temperature is less than 40 degrees Fahrenheit when heat loss 
calculations
performed by a Professional Engineer prove that piping will not freeze. The 
proposed
wording was challenged during the comment stage but the challenge was rejected 
by
the Committee with a statement: Deleting 8.16.4.1.5 would preclude the use of 
wet
systems in cold storage facilities where freezing is not a concern (i.e material
 stored at 38°F).
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Proposed TIAs for Antifreeze
The following Tentative Interim Amendments (TIAs) have been proposed to NFPA for
 NFPA 13, 13R, 13D and 25.  They are being published for public review and 
comment.
 Comments should be filed with the Secretary, Standards Council, by July 2, 
2012.
 The links to the TIAs are in blue text below:
NFPA 13
TIA 1066 
[http://www.nfpa.org/Assets/files/AboutTheCodes/13/ProposedTIA1066NFPA13.pdf]
NFPA 13R
TIA 1062 
[http://www.nfpa.org/Assets/files/AboutTheCodes/13R/ProposedTIA1062NFPA13R.pdf]
TIA 1065 
[http://www.nfpa.org/Assets/files/AboutTheCodes/13R/ProposedTIA1065NFPA13R.pdf]
NFPA 13D
TIA 1060 
[http://r20.rs6.net/tn.jsp?e=001--FazplE_0pi2Qg43OHEQxRnbGCy_RJU0CNTjvcbctIeMDnO50tiVoA7Q6Hl3nXp43_l3xCbNhY_Df5PljUqdEQPgPa3fJQ6pGip4SvNhCn8IC-2fYeBIFeDYR_MvVrDIWgXpRVUDXu460FKO0apgJeAnp8c_ocE2M1VZgJP9TT1lqbMxHEgz72gSU1hTB2g3iS_rrPVxWg=]
TIA 1061 
[http://r20.rs6.net/tn.jsp?e=001--FazplE_0p90Wy6kf-N3ozKGj7rfazFAqce3PD1MDc-5CobzRfGb1Amf4mgowounLi3O--DaSVM0p2v5MqXdugSfvWeokDcxY9ZA31aPSoyzj4QdsIY5EykRrBSCqm7c0dJ1lC2DlKLOUdVVN6v74jyuXxXtBwLd5VMZeV-sHeGJP3jXjjxv4lrXEaSAtFou8xI0xcM69Y=]
TIA 1067 
[http://r20.rs6.net/tn.jsp?e=001--FazplE_0qRT3j-4sHWJJxEinSpFnMQF1gn8FPqEl8SsoeBoKEu9cJaWquMvCs4brTwgakwt4BE1n2WtjjhUKKmplNAKKiKeg4LTgW-pNib74LKPaNZ-lrF0WkP7AmAsIhXkINGcoUzz8xAHtoM2IV05b3NdldpjIWUSW-3LU_eGvdOqvBvFv5YpdYkPs_IhZDeqILp5MA=]
NFPA 25
TIA 1068 
[http://www.nfpa.org/Assets/files/AboutTheCodes/25/ProposedTIA1068NFPA25.pdf]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001--FazplE_0qdN_vaRRSNseCgeY5PZxLzh36DntEmRpi9njPfRrF9u3BY6bKoDnV6nMSaDHbyRFWvAkcGAwDmHWjqlHJE8Niv0pVnHe6zQAdOYfcVFE_VDA==]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2012, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Printable Copy
PDF Version 
[http://r20.rs6.net/tn.jsp?e=001--FazplE_0qj7GGFuuEfDvSbh88-XwOEkf6-jiUugclQvkTcijWmQZUii-l3PPcjEnFOBpggbKfRaxLcpmjScLAWgMgKIaJ_oh_D-tw5SqyEJQL3lkpTbX2hRjt4xZaXg2uoIZz9eDQQYHPXjyJp644mTsjoE971GILIt7ktsg2r-ExRILQhLJ2S12OVCT01DTHw3WGUBK4=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Mark Your Calendar!
Beginning Fire Sprinkler System Planning School 
[http://r20.rs6.net/tn.jsp?e=001--FazplE_0o_g5yzb0XlLw7ctT46OqOazmTB1BZ3OAkcs5lPqCmcgAzbdPn5MN75UAo2eBORp6lEHLXp6wrI9NBEwnrogOnPV25vrmm2DY9_kdykDmI7fW9lysdLkzvt8ioC3ZWQSs8e_bbHsfNWPhfXaT52-SmiEg_54Ym-PBmJcEPl-1Y47A==]

July 23 - Aug. 3 
[http://r20.rs6.net/tn.jsp?e=001--FazplE_0o_g5yzb0XlLw7ctT46OqOazmTB1BZ3OAkcs5lPqCmcgAzbdPn5MN75UAo2eBORp6lEHLXp6wrI9NBEwnrogOnPV25vrmm2DY9_kdykDmI7fW9lysdLkzvt8ioC3ZWQSs8e_bbHsfNWPhfXaT52-SmiEg_54Ym-PBmJcEPl-1Y47A==]
(click here for details) 
[http://r20.rs6.net/tn.jsp?e=001--FazplE_0o_g5yzb0XlLw7ctT46OqOazmTB1BZ3OAkcs5lPqCmcgAzbdPn5MN75UAo2eBORp6lEHLXp6wrI9NBEwnrogOnPV25vrmm2DY9_kdykDmI7fW9lysdLkzvt8ioC3ZWQSs8e_bbHsfNWPhfXaT52-SmiEg_54Ym-PBmJcEPl-1Y47A==]

Nov. 5 - Nov. 16

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001--FazplE_0ojcwUAm8gH2P5Oj4G8hvjpzp3w0X2YQ0bCGG-4BcKBpQEr9eMp8NWuyhbtLvGVF1vEOUwKRlOtck9FG8NSwsyltTKYZSCyW9MjosnXKY2NY1KFxMTYpEjGofLTUdSnWhAgvVSeEE0TYjFAMq3k1hmFU-UPRGKyt6DqyR2uKSsf0zNt5c-k50JfZykdH-X1tTS9q68ZYH4cQdsmfs5O6tfQ4BDMMhA4a-b0yVzc2HPxMUZz7rfs7pcavI92vIYZfpQ9xygSswiHVWLz3soRnFWY].
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?e=001--FazplE_0pijBBgbnas71pWH6OeLLz9ygUwyCruedCVOEtv2gOq7v0qZwv2UpAHSGveVYOH7ag8Y172jS5HK7RCbH5nFz9fqlutYcZwYULNuEK2lDSdkFmJe1h1EKiZ18jQOu8Zb1Fb6rr89Q2Hzi64-6NybmK0kMqg_RFoHWg=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?e=001--FazplE_0pwL9MtVci6KNTDovQ7V47aOL9QzuE-T41JqZ0sAqsR6hdpykSOYfbLJdbUv_Ev5C-vUYSTF7SM-JUFN15Snl-Fei7xIwugBr8yYWz7WF0WcZDYRHmMrQ8uXl82yyshLSMSv4ZJGVl_lBe_dhXag5Hx-JOG2yraJd0=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001--FazplE_0qdN_vaRRSNseCgeY5PZxLzh36DntEmRpi9njPfRrF9u3BY6bKoDnV6nMSaDHbyRFWvAkcGAwDmHWjqlHJE8Niv0pVnHe6zQAdOYfcVFE_VDA==]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001--FazplE_0ojcwUAm8gH2P5Oj4G8hvjpzp3w0X2YQ0bCGG-4BcKBpQEr9eMp8NWuyhbtLvGVF1vEOUwKRlOtck9FG8NSwsyltTKYZSCyW9MjosnXKY2NY1KFxMTYpEjGofLTUdSnWhAgvVSeEE0TYjFAMq3k1hmFU-UPRGKyt6DqyR2uKSsf0zNt5c-k50JfZykdH-X1tTS9q68ZYH4cQdsmfs5O6tfQ4BDMMhA4a-b0yVzc2HPxMUZz7rfs7pcavI92vIYZfpQ9xygSswiHVWLz3soRnFWY]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?e=001--FazplE_0p-KBFdwsXnPDRw-Zvni6T_urFveLEEb-r8jeOwWBSs4z05V8Mi8yVv7cXDUf8Hb_XxYhzhMECdYCfM_s1nhnRyZBJZr2e04t3YeALLNbJe4pFX0dPIcoW0WSCV5wUZ46NTXsfeAB0UWQ==]
Fire Sprinkler eCampus 
[http://r20.rs6.net/tn.jsp?e=001--FazplE_0rVwHgr6hO6LrnDquaxGAYN4Gg7KYmOunFCa7nuaoRdMbKgs1gDPUrsyrpX_Op-JJ7cf5bsKa-D2H1gZtyDxSNsGVdb7XG-27Kpl5tke8NAqzgYNw98hInx]
   Join AFSA Video 
[http://r20.rs6.net/tn.jsp?e=001--FazplE_0qAEQWWHc80dZmLhmiUApguDkodltkdmZ9pU5LopGRwZO6lsQve2YbWitKczOF_W-9pZWDfLPpAsbm8ka1gX1Moo0Afznydw1bNstao_--oDxkLOC_vlPBH4JSpm9VQqJR5EZdlwPL1MLmm6Zeil1bh]
National  
[http://r20.rs6.net/tn.jsp?e=001--FazplE_0rR97C0LQtemltTzh1N6IhmcGwKNbAOr5ALT_DZg675Qd7ryQOQlXLOu8qmDP57JgtLZMEletVowdz5vfvxm-uDJGQLyPi2dMFI7yxYtr4tFA==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?e=001--FazplE_0rR97C0LQtemltTzh1N6IhmcGwKNbAOr5ALT_DZg675Qd7ryQOQlXLOu8qmDP57JgtLZMEletVowdz5vfvxm-uDJGQLyPi2dMFI7yxYtr4tFA==]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?e=001--FazplE_0ogkwrtH8upMo6qy61KRrHYLrddRw85eIZxURaExCWQL-ySzVEB3QbEDmz823vLeyIZlgG70VbnoBMVfVe_jYO40c6UNEIbfQdwJtiDOokQRjHFZQkyHTLoZzh_YxvPet-vm_WVu1SeAzuLXbeP-4Fa]
Technical Services 
[http://r20.rs6.net/tn.jsp?e=001--FazplE_0rCBIJEwpP5MCAVtUDCo3vrO6OLH8O15nLKld_cRKfCpuzVRsV8VpWRu6oqCygg7O_p7x2MyDYDHfGjQxVbm_Zw7Wv28t4PRKlrE0dIp1VECFD5Fpq9_7-OJL6_QQl0fcg=]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?e=001--FazplE_0rcFWdgKOfQgkpsg91KxSeKoPfTwycsxTPsBZP1f-AWqYdWKxLTtaIktURfg8PFjIQAHQNFiKNFwhspEmniWdn6PdXE7bT6fNe3fz4zjQbWMVgCK-HHVqtSDuzy33_NYH0dR1_sN2mfSGR60LtsXiy1ZSCvR21P3ks=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1110162985906


This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=0014vatrg6vFDqgqNbtDYqnNA%3D%3D&llr=gdnaptcab


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=0014vatrg6vFDqgqNbtDYqnNA%3D%3D&llr=gdnaptcab


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp


Online Marketing by
Constant Contact(R)
www.constantcontact.com


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to