AFSA Technical Update
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

A newsletter dealing with codes and other technical issues

March 6, 2013
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Maximum Distance from Peak for Residential Sidewall Sprinklers

"The client would not allow us to use pendent residential sprinklers for an 
application.
Residential sidewall sprinklers were installed as an alternative along beams and
 the deflector is aligned parallel with the slope. How far can the sidewall 
sprinkler
be below the peak of the ceiling?"

In response to your question we have reviewed NFPA 13, 2013 edition as the 
applicable
standard. Our informal interpretation is that the manufacturer's installation 
guide
for residential sprinklers provides this guidance for spraying across the slope.

Section 8.10.3.5 indicates that where sprinklers are installed along sloped 
ceilings,
the sprinkler shall maintain the minimum listed spacing, but no less than 8 ft, 
measure in the plan view from sprinkler to another as shown in Figures 
8.10.3.5(a)
and (b). Although the figures show pendent sprinklers, this section does not 
specifically
indicate whether it does or does not apply to sidewall sprinklers that would 
spray
across the slope. The maximum distance of the sprinkler from the peak is not 
shown
in the figure. Section 8.10.4.2 says that sidewall sprinklers shall be 
positioned
so that the deflectors are within 4 in. to 6 in. from the ceiling unless the 
listing
allows greater distances. This statement does not provide clarity to your 
question.
Since the NFPA 13 standard does not address this specific application, the 
manufacturer's
residential sprinkler installation guides were referenced for guidance. The 
installation
guide does specifically address your application and shows a minimum of 8 ft 
between
sprinklers. The distance from the peak for both pendent and sidewall sprinklers 
(that spray across the slope) shows a maximum distance of 3 ft. Note that the 
distance
of sprinkler from the peak along the slope is one half the maximum sprinkler 
spacing
for the coverage area. This information between manufacturers is consistent 
regarding
sidewall sprinklers that spray across the slope.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001OwxOcFTWiD-su0r1LayfHAgJoU-hGO5UUmkfR59x7tXuaXTdGOhJR7mqYJOvPa6fqziGgFFw2M2eQj7EQh6smdqcfjPSfICySNpnoVcT5RWePIXuzTAWcw==]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2012, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?e=001OwxOcFTWiD8hls_s3Yd4FBV_EC1ccIZLQ_Z6CR5zcjj2IjP5ouzasVeBDolFL0nydkc16OdI3Avg_EBD4SAXighnqpToS5pgBlqhWG9CY3-0BbgNw5U6RBM2CeGLZ-jv7HYa21vymElocnbk7QcDyQd22CoQl2yRYKiCuByVqJcZfV-c_WExWMMQ1UCr0HGD_tjaMhLIQSo=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
May 13 - May 24, 2013

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001OwxOcFTWiD_I8G_CWuD-Ond5oytEPvOwKZN0McA9zaGWcVPEJFpGKYygfhNApUonjn09aqBnPYVBFhN1oefmNBr_Ng08878lkavTV8Sx_U0y-uzLaYWCOIBraKqi73FWvd5cfH5qQ4eiCu4ATL6NmWmA-ap8r5_jGKRE40yAyVToDNFS5Mx7iqgfnR4HIMNJBhCA6wchZSvqVgGSic-ao6j38ok1789MuSt2EUUTjd0imyYd_OKzkmmvr6u0lGR5ig9D9xMDdI_tKwhI7mQQcwmRI8YrQbpI].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?e=001OwxOcFTWiD-KOX-vp6u1kHBMZCDFYpOZG72EgUfFq1DD7BfTEiVuh1jlKMWMbe_SJnqWJHvU01Qe195PEWi1P_KKapCxidCx8h8s-mwe-BG4z-yqaHeg9Mxh53ZSH_NV]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Webinar
Bob Caputo
to Present an
AFSA Webinar on
"Technical Changes from the 2010 ed. to the 2013 ed. of NFPA 13
Part I - Installation Requirements"
Wed., March 13, 2013
Free to AFSA members!
Register Button 
[http://r20.rs6.net/tn.jsp?e=001OwxOcFTWiD_RppAKHY_E-v2pvp1j47fzvy8Ai96-hX2KtegnGtLrZzf2LTlhMO-dWM8FVqcvC1Vlc-2OYXJ_3--mhMWTVQhTYrryUeGYT3bA_lY1dAZxD-P75WDiV1UBEhXSa7I9YfYzPEI3yVXARkXmBbfOvMiw]
For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001OwxOcFTWiD_I8G_CWuD-Ond5oytEPvOwKZN0McA9zaGWcVPEJFpGKYygfhNApUonjn09aqBnPYVBFhN1oefmNBr_Ng08878lkavTV8Sx_U0y-uzLaYWCOIBraKqi73FWvd5cfH5qQ4eiCu4ATL6NmWmA-ap8r5_jGKRE40yAyVToDNFS5Mx7iqgfnR4HIMNJBhCA6wchZSvqVgGSic-ao6j38ok1789MuSt2EUUTjd0imyYd_OKzkmmvr6u0lGR5ig9D9xMDdI_tKwhI7mQQcwmRI8YrQbpI].
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?e=001OwxOcFTWiD-sfFSziUG-LDnmJn7LnJaxBUz61JN-SPOK8y3ylGeZBbGp5pzizFxLcucr3Lhlg79FC5PhRPkz5T3bew37vxcqxI7U2YPFX9xDIArWUJwSwft7E7FJY_3GQaFKD1vyAXPm-G9ye3gJHjQQGCOILIPPVwC6v40YgWo=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?e=001OwxOcFTWiD8tEUVgaxMD1_Hgycr9iyms9a0VOzhURv5O8GgGBeedEdTPENk8eoIJdXTDFLxHkdTNql8IJYQDmVRMQ4FdCOJGlhs0o7AhKn6EjJmS2NtLagWndYFM8k1DAGVKCTq83xgamnKwadyuNHHVQ-DjDPDVUEcQjY2fP1s=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001OwxOcFTWiD-su0r1LayfHAgJoU-hGO5UUmkfR59x7tXuaXTdGOhJR7mqYJOvPa6fqziGgFFw2M2eQj7EQh6smdqcfjPSfICySNpnoVcT5RWePIXuzTAWcw==]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001OwxOcFTWiD_I8G_CWuD-Ond5oytEPvOwKZN0McA9zaGWcVPEJFpGKYygfhNApUonjn09aqBnPYVBFhN1oefmNBr_Ng08878lkavTV8Sx_U0y-uzLaYWCOIBraKqi73FWvd5cfH5qQ4eiCu4ATL6NmWmA-ap8r5_jGKRE40yAyVToDNFS5Mx7iqgfnR4HIMNJBhCA6wchZSvqVgGSic-ao6j38ok1789MuSt2EUUTjd0imyYd_OKzkmmvr6u0lGR5ig9D9xMDdI_tKwhI7mQQcwmRI8YrQbpI]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?e=001OwxOcFTWiD-UHXCpwYy7XbIjwk3hO3Ra5h93tdFuCeWi4XZLqcbX2stPJDTj8q7nILSrjx5gPnPHbMkCzjISdD4ipxSS0cGuvWu4ecvcZkVdeJ5Ofx67LZe3IvCSIoW8bYnsFKmpT2-Gp32YbWB_sQ==]
Join AFSA Video 
[http://r20.rs6.net/tn.jsp?e=001OwxOcFTWiD8fE0GM_QvIzBxguhc-LrcueFavn96yRXu3YShVxU3bz1jOa9IwjM6isNslj3t86of52ILGPyrc7u8YfqIV-5MSow0ladOa_XpSVInMeffTzvqmLfFuocg9Ko3Yob6NDB0dBfCINc791uuwoZX6Uq1-]
National  
[http://r20.rs6.net/tn.jsp?e=001OwxOcFTWiD8EWq1eVes6auhFKl3r6UCQwFYnUuXN7Un47l_4nSqsRX6y27uXLsa9Mgh3V0ZPdNL2ePAcsk5G_4V1TNCDPr-nmey8Hgt7pk5fQgktcfMqdw==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?e=001OwxOcFTWiD8EWq1eVes6auhFKl3r6UCQwFYnUuXN7Un47l_4nSqsRX6y27uXLsa9Mgh3V0ZPdNL2ePAcsk5G_4V1TNCDPr-nmey8Hgt7pk5fQgktcfMqdw==]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?e=001OwxOcFTWiD9V7TBZGgpo-Fpiw6e7uBd5Zazx6Zl8upO4eVaOxafkYe__m4ru3hiGjeM_p64ZLRihsG0EeqAVB6aFd3GOzxaW461z-HPak4dAVBVTBjxuZFMBUR6-uVE2Gi5KBZO8BJT4eFd6KlLEbAKnnkhCBu7f]
Technical Services 
[http://r20.rs6.net/tn.jsp?e=001OwxOcFTWiD-i6SplJVG7JHCBwyH8Sqf7cgj3aw-sO6T47QCkfN61c0aSUUMQTxqGSqdoWClDnXehJkvFzCrqVb4LWltGwZX9GyWat8yklxilFqpyLK0Sb902lmnpZq--d_xuY22rB74=]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?e=001OwxOcFTWiD9JSb3H39Z1D-u5TWr8SLfiem93wpNN1PHQ7P0S69qiutalrsRjqAql8pJFC7vwHFAf2jBD8bp36BPhi7K-O--YoED-Wet9UU8Fy0fOZ034oUI4az8lj0IxP8EfEunliQOIML4zG2IhAOz4ZWZNsDYsnaaPaKqAd8A=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1112647772706


This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001MoW6w0emNbCgMDReC4O0dw%3D%3D&llr=gdnaptcab


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001MoW6w0emNbCgMDReC4O0dw%3D%3D&llr=gdnaptcab


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp


Online Marketing by
Constant Contact(R)
www.constantcontact.com


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to