American Fire Sprinkler Association [http://www.firesprinkler.org/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

AFSA Technical Update
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

A newsletter dealing with codes and other technical issues

May 10, 2013
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Pipe Penetration in Rated Stairwell
"There is a 2 story building of noncombustible construction with a cast in place
 stair from the 1st to 2nd floor.  A fire sprinkler line was designed to 
penetrate
upper lever of noncombustible stair, provide protection in combined stairwell 
per
NFPA 13, and continue through to feed a weight room on the opposite side.  The 
architect
of record is stating per IBC/IFC 1022.4 all sprinklers in an "existing 
enclosure"
does not apply.  Fire sprinkler system is being requested to be routed around 
stair
enclosure.  Typical applications such as multi-floor buildings utilizing a 
combination
sprinkler stand pipe has the pipe entering the stairwell and sprinkler system 
exit
to adjacent floors along with the main drain/gang piping.  Would this example 
apply
to the stairwell in question?"
In response to your question we have reviewed NFPA 13, 2010 edition that you 
indicated
as the applicable standard and the IBC, 2009 edition that you indicated as the 
applicable
code. Our informal interpretation is that the IBC allows for sprinkler piping to
 penetrate the rated stair enclosure.

Section 1022.4 Penetrations of the IBC states, "Penetrations into and openings 
through
an exit enclosure are prohibited except for required exit doors, equipment and 
ductwork
necessary for independent ventilation or pressurization, sprinkler piping, 
standpipes,
electrical raceway serving the exit enclosure and terminated at a steel box not 
exceeding 16 square inches." This section explicitly gives an exception for 
sprinkler
piping. The 2012 edition also has similar wording. As such, the sprinkler piping
 can pass through as long as the penetrations are sealed per Section 713. 
Sprinkler
pipe penetrations on each floor are no different than a pipe penetrating across 
the rated enclosure. The IBC does not indicate any type of restrictions for 
penetrations
by sprinkler piping in this section.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

NFPA 13 Public Inputs Due May 31st
NFPA is soliciting input for the 2016 edition of the NFPA 13 standards. The 
proposals
can be submitted using a Word document form or online.
NFPA 13 [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=13] - 
Standard
for the Installation of Sprinkler Systems
NFPA 13D [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=13D] - 
Standard
for the Installation of Sprinkler Systems in One- and Two-Family Dwellings and 
Manufactured
Homes
NFPA 13R [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=13R] - 
Standard
for the Installation of Sprinkler Systems in Low-Rise Residential Occupancies
NFPA 24 [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=24] - 
Standard
for the Installation of Private Fire Service Mains
Other standards accepting public inputs with later due dates:
NFPA 14 [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=14] - 
Standard
for the Installation of Standpipe and Hose Systems
NFPA 15 [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=15] - 
Standard
for Water Spray Fixed Systems for Fire Protection
NFPA 20 [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=20] - 
Standard
for the Installation of Stationary Pumps for Fire Protection
NFPA 291 [http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=291]   
Recommended
Practice for Fire Flow Testing and Marking of Hydrants
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001fQ58ue-H1AyJVsyVsypZ9K1tRIqrtJFI_zL0DFGX-Pkrs_gSvKQL6Nm8oC_bRun1r4L45jr_Rhzryh90ppgASWtSgw1FDNo5KNdwhT_2_TO9-yxl8-jTHqpxLx7FjaYu]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2012, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?e=001fQ58ue-H1AwVuputfII8OD6mB0W8xj0GKLGl6uBZF9sGN6k47JyccXucZJjUk1YwceuN0K7abfh-Mk0QPVs4OIWpcRntLXhRZN2X8WEUGJBBdd8SLeHD5muFXgHcKnMJA0dOfJX9m7qg0PyQSSorhkCR22nHMugyoaVUg4hESITvr08ocCH5j0-TsiMUNFniIp8oOk4v-2k=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Webinar
Bob Caputo
to Present an
AFSA Webinar on
"Technical Changes from the 2010 ed. to the 2013 ed. of NFPA 13
Part 3 - "Residential Sprinkler Requirements"
Wed., May 29, 2013
Free to AFSA members!
Register Button 
[http://r20.rs6.net/tn.jsp?e=001fQ58ue-H1AxFR2GVEZOJ836Nv2ceflNH1r_oQpRtE52Iu9kQgqWAgGt4i175S_LSkkMZ1SYxQwFww8cYshauvz3RRPDUF-jgQQhgtG3p20n739Fxlq7xgrdOaEZcPgrSyEsos1KQxsPGPTA9F2pHpvqvXXBz8tguNfhv3QilsM0=]

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001fQ58ue-H1AznOWWrdxosKiUqKo-gazEvzDwbjptWsb3fJxQ18vkcHuwlBztwVnPTSYUWAaBhUDSOjzGImkI5fMUMX4ILIadFkWgq84HVijaz8E5MpD1_Jz-cSIwxAn0U88pAxNrX3U0V6Y55dGA4PGkPWoulXarJBAVS6LOCEntbQxnt1DW9bDdPzImB1CFla-1TJC6dA76VDbeBvsxq42HxBxaZOKhzDyCf7qcth1cR6mnqxRv-f8SHxPjie4cS1hjc0QhWNQM2tpug4BUSXAgvjQgoSZGE].
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
July 29 - August 9, 2013

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001fQ58ue-H1AznOWWrdxosKiUqKo-gazEvzDwbjptWsb3fJxQ18vkcHuwlBztwVnPTSYUWAaBhUDSOjzGImkI5fMUMX4ILIadFkWgq84HVijaz8E5MpD1_Jz-cSIwxAn0U88pAxNrX3U0V6Y55dGA4PGkPWoulXarJBAVS6LOCEntbQxnt1DW9bDdPzImB1CFla-1TJC6dA76VDbeBvsxq42HxBxaZOKhzDyCf7qcth1cR6mnqxRv-f8SHxPjie4cS1hjc0QhWNQM2tpug4BUSXAgvjQgoSZGE].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?e=001fQ58ue-H1Azka6J6h4a0nYQVv4mZ8PPLsmVjRPtTcYWA7nS2K8_WtECHl6E93OSjHeYZTrFHhi045JcOMPl4vTvhOnkl68SxOznL2F80T29oGI4p-5DZ4i5sqAYy6Ko-]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?e=001fQ58ue-H1AxBjWunyU5gjaBue1RWYJJukF1R_CF8p7QBKxBoAGy9XuJk5O5vuIZHRi0M-3cZnQZNumxxq_rFdNJv7Bn522kda-nJ-5cbS1XdCx_RSBnrzyxygFzIxDbxyTHL-wKixdhgaRkOj29m5aEAlMn_OXbc7CcavLDci60=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?e=001fQ58ue-H1Ax0hFwSVOR3uSgdZxH3dSrBcA28hTARZ59YzqevhKhiErlCNnbC0h7ZBVO8-kaz_5R2xhRQQTHcmUtNUc27UvzMzBeXS0VN3wIrNI4G29z0nCCqWu0pzQRGFd38n7l0qH-DIq39jOy14BXy_FDC_hLVaROxT0ewLDk=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001fQ58ue-H1AyJVsyVsypZ9K1tRIqrtJFI_zL0DFGX-Pkrs_gSvKQL6Nm8oC_bRun1r4L45jr_Rhzryh90ppgASWtSgw1FDNo5KNdwhT_2_TO9-yxl8-jTHqpxLx7FjaYu]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001fQ58ue-H1AznOWWrdxosKiUqKo-gazEvzDwbjptWsb3fJxQ18vkcHuwlBztwVnPTSYUWAaBhUDSOjzGImkI5fMUMX4ILIadFkWgq84HVijaz8E5MpD1_Jz-cSIwxAn0U88pAxNrX3U0V6Y55dGA4PGkPWoulXarJBAVS6LOCEntbQxnt1DW9bDdPzImB1CFla-1TJC6dA76VDbeBvsxq42HxBxaZOKhzDyCf7qcth1cR6mnqxRv-f8SHxPjie4cS1hjc0QhWNQM2tpug4BUSXAgvjQgoSZGE]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?e=001fQ58ue-H1Ay8QfanzqjRhfCbotAy_P49z-Z6VaPW2khcEsLuhSIm9m1pJvmjbFg_vSbFqVMX8y6K3lv43Vh74o0zCZC6oOAF6NSNBKD1Stg5y3aaxOZlroghcEuuySg_zg-NmRsbhy7HzezQs6PzYU56IpzFNdhJ]
Join AFSA Video 
[http://r20.rs6.net/tn.jsp?e=001fQ58ue-H1Az6ybwYW4UYQDogTXLgH4CsRWaFkMBxxjMSsPOmtYNptG9O6Yj75bQ7vtW9xAYi_k2zh6OWPERr-6ydG8EKkzVmYc6GkWIgOeckIx-5gWZfgIM9GFe9M6O3wnU1gZ3QMUbT52DrHtY2fLKtkfl1gUebVrbXCVsBbMA=]
National  
[http://r20.rs6.net/tn.jsp?e=001fQ58ue-H1AzYAil8Ad4M_YDzY9FQ7qdLDF2rGLJL9nKAEvp-ptTIqzVq_b9IJ0Kz0a4L2DPteJNHyctIHJpPTdHrOIE82xeeU7rMOcAt7PVH2JQ75CNQNOr_niGDiB7D]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?e=001fQ58ue-H1AzYAil8Ad4M_YDzY9FQ7qdLDF2rGLJL9nKAEvp-ptTIqzVq_b9IJ0Kz0a4L2DPteJNHyctIHJpPTdHrOIE82xeeU7rMOcAt7PVH2JQ75CNQNOr_niGDiB7D]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?e=001fQ58ue-H1AwB8q5sTBAoW608oe2ztt2TXoqltD0a7Rg95H5s-6g80PhC5-usxP4pfBvKVXkW-wIpT4r3Cl0x6PBhyFdH5K6BFd8KmP6iWaQzA03LHNC0Ob9l-XOf30m6Xfwy3IAqe38RV4ForDDRxCs9gEBad6oR]
Technical Services 
[http://r20.rs6.net/tn.jsp?e=001fQ58ue-H1AyWXWcLCGYN5_woGwdrx7N4uzdXWsFTFuwh3kHz2TS3VcPXTbRo3RhBPUHl4SmBCbKWSmhOPnnQVjOdGFe25RbCJPIsz4iMRbv-p1emVxPRmR5eJ5xSphCDecFFe_i-JZ5o9nbvOL1HPw==]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?e=001fQ58ue-H1AybZjYuuuTW3RlK5A1QJdffzpsMrRedVTfDzyWaMdxBAitlsKkbZchXTFSEY9lmTBAK5lkbfiwgZTO8A7S0_aBWn0II9Un65d2eKvG-HBNHdGh6_9DxIUvXL68cunV7wO8_ibVIsvBXisvaaXA7f2R42CirR5tnDHcZqGqbXxdPmw==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1113371535335


This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001XCWTiV4UeiTNP0UdGySjrQ%3D%3D&llr=gdnaptcab


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001XCWTiV4UeiTNP0UdGySjrQ%3D%3D&llr=gdnaptcab


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp


Online Marketing by
Constant Contact(R)
www.constantcontact.com


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to