American Fire Sprinkler Association [http://www.firesprinkler.org/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

AFSA Technical Update
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

A newsletter dealing with codes and other technical issues

September 19, 2013
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Horizontal Concealed Combustible Space

"Construction consists of a combustible concealed space above acoustic ceiling 
tiles.
The roof slope is less than 2 in 12 and open web trusses support the roof. The 
open
web truss depth varies from 20 in. to 36 in. and the peak is in the middle of 
the
truss. Truss length is 37 ft.-8 in. and the roof deck is plywood sheathing. The 
ceiling is located approximately 48 in. below the peak. The AHJ's opinion is 
specifically
listed sprinklers are required to protect this horizontal combustible concealed 
space. We submitted drawings with standard spray upright sprinkler. Which 
sprinkler
is correct?"

We have reviewed NFPA 13, 2013 edition as the applicable standard. Our informal 
interpretation is that this is an ambiguous issue but the specifically listed 
sprinkler
should not be required.

Per the information in your question, if the distance between the peak and the 
suspended
ceiling is 48 in., the narrow portion of the truss (eave) would put the ceiling 
approximately 32 in. below the plywood sheathing. The technical committee's 
discussion
addressed only horizontal areas with no pitch for Section 8.15.1.6. As such 
there
is no guidance on what to do when there is a slope not exceeding 2 in 12 (which 
is considered horizontal per NFPA 13:3.3.5.2) and part of the area is greater 
than
36 in. This is further complicated by the fact that the listing of the special 
application
sprinkler has a maximum height of the concealed space of 36 in. in most cases 
and
54 in. for specific configurations (such as steel pipe in wood joist 
construction).
In looking at the Sprinkler Handbook it identifies that the concern is that for 
areas less than 36 in. the standard spray sprinkler does not develop a very good
 pattern. An additional statement in the Handbook that could cause some 
confusion
is where it states that once the height of the space exceeds 36 in., standard 
sprinklers
can be utilized. This is simply emphasizing that for those flat areas that are 
greater
than 36 in., standard sprinklers are fine. Considering that we are likely 
talking
about only a single branch line within the less than 36 in. portion and branch 
lines
with standard spray sprinklers covering the remainder of the attic, the upper 
branch
lines (which tend to be the first ones to activate) are the primary concern. 
These
have been identified as being able to adequately develop a discharge pattern. As
 such, requiring the lowest branch line to be sprinklers listed for horizontal 
combustible
concealed spaces isn't warranted. This arrangement is not that different than 
the
typical, more steeply pitched attic where the first branch line is within an 
area
that is less than 36 in. in height. Now, if there had been less pitch and the 
majority
of the branch lines were within an area less than 36 in. in height, it would be 
wise to use the specially listed sprinklers throughout or at least the portion 
that
is within their listing. As with all issues that are not well addressed by the 
standard,
discussion with the AHJ is recommended. A Public Input was submitted for this 
issue
where the proposed text reads, "8.15.1.6.2 Sprinklers specifically listed to 
provide
protection of combustible concealed spaces described in 8.15.1.6 shall be 
permitted
to be used in accordance with 8.3.1.2 throughout the area when a portion of the 
area exceeds a depth of 36 in." This has yet to be processed through the 
standards
making process and should not be relied upon as an official statement from NFPA 
13. Thus the committee is addressing the issue but it is not resolved.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001QG21Tth9-f7DLEx35_oMSx9h4wJBwoegpjM22YwuHGaWdPISNYGPOArghdJ1g7N3jkGdE7ThSNVT17a1M13I2jUVUl1w2QUfAYU3quYcjg9glL4JC85luiLre36okhGl]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2012, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
P 
[http://r20.rs6.net/tn.jsp?e=001QG21Tth9-f4WnNxp55kAeheshv8RRqUaV79mmkOIccsodrqot-vmAuA9o5eT1tFQIbUT_z4HkL25RAQ6uoFnxDrSvcDm11KYqsdK_BZK3UiBu-NJ1Wx7dr9WbGPHpiBr2S-maCAMv23kTNtNJNEI87HcreZ9KnBuXsZ3D6-GJ5gYFe2qUGXKA8L3mX6QfByAO6QOeTYqfKbzsVP8cICHNA==]DF
Link 
[http://r20.rs6.net/tn.jsp?e=001QG21Tth9-f7j-04DHNWkh3LV3kCdBsjAnuo47O-BMV9Tk4FjV9ah0B2ilcSLtU5z7U_A_-T1ccX8_2tC4o0pPlKmogzri7mYqwsUaErN6sewTyG92VgKkziQ0N_zuZ115f_vUMBRqZ74icnNq8ByH_x5OVjNl7tScwlJY-HXdV--QVVkcpVJhWzyyaVnJv-n-YXTdNqpK30cTUAK5S0UNg==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
Oct. 28 - Nov. 8, 2013

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001QG21Tth9-f5nMn3z2oR8qSAXG7c3KxyilmZY-6mtgHSJkj5KUFe97UCe1LEjoGLjZne-BeXMJh1F794Q9_jxT3lmm0N03YLx0flfSEMvaaiRM2KyG82xHq2_5vG2Vi_feRVt7FAJr_d2bhKH1CcmIKyvjM674hVcaWSYmG4CROevalV6lZvvIC7xQxo2NEqHE_jKFQX0EPIX_eRQV65IWUfsZqkVQ4QkbmxXNn6pAyxnbvo_VPOwGNsbBTX1BuleFKY3L4j-v6LQujC9taPOlu0NXc_kStu5].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?e=001QG21Tth9-f5xNWjEBU37tK5AjrALifbdXA5SjPKVNqutUunWBBR5HNCqJZzIA64EiZKPX1vHzt3zHwCPhFr-PboyNylGtMpkrcIzk8-dMaKOYKPZ50UWneIh0bRbcySR]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Webinar
NFPA 20
2013 Update
Nov. 20, 2013
11 am - 12:30 pm
Central Time

$15 fee for

1.5 CPDs

or 0.15 CEUs

Non-members $140

Register at

Webinars 
[http://r20.rs6.net/tn.jsp?e=001QG21Tth9-f65E8CXuSZtu62MCpM7hwr1M-P8UoaGY2KTzu3BDwt81ynrPrmh62lyPzvqA8mIeIfjgWjN5cdoF-HFenaL7bQGcCjhmSJukgBKrYmvyBIbgfZGKvhyPd2Uw51PRMADXBq-y8q7QBaNSnpZWwNmUvZ45lHhzsNBRFk=]
Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001QG21Tth9-f5nMn3z2oR8qSAXG7c3KxyilmZY-6mtgHSJkj5KUFe97UCe1LEjoGLjZne-BeXMJh1F794Q9_jxT3lmm0N03YLx0flfSEMvaaiRM2KyG82xHq2_5vG2Vi_feRVt7FAJr_d2bhKH1CcmIKyvjM674hVcaWSYmG4CROevalV6lZvvIC7xQxo2NEqHE_jKFQX0EPIX_eRQV65IWUfsZqkVQ4QkbmxXNn6pAyxnbvo_VPOwGNsbBTX1BuleFKY3L4j-v6LQujC9taPOlu0NXc_kStu5].
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?e=001QG21Tth9-f6GlbWYixTxyzESgPKzywvV7eNSH0lbcJ4EXTHWVOaBU1l2FG7hf7zrcdX6-m9wevcS7YphP4Muq9yzG4m6dFLOoLkvbtiii1YU3_qWl_I82pj5wgaeeVu4pbtpJ75H7FFLPJtgDyhE52sGpXf43J5r6kpfQzQSf9Q=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?e=001QG21Tth9-f6WxDGtgUYKk0WigIaZiSFphzA2Vp5Q9ewqlQY1yr1r0Uhn02ty--a-UC6HK9Zf48XcAh_NOFKkTc2vUZgwVmtqdHnqtS9K-SBFzj3YmlKTarU8GeeO2GZB6XkSz6zwBNfZYpUR4cluHCBb-nQst2K_elxjT5I_VOQ=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001QG21Tth9-f7DLEx35_oMSx9h4wJBwoegpjM22YwuHGaWdPISNYGPOArghdJ1g7N3jkGdE7ThSNVT17a1M13I2jUVUl1w2QUfAYU3quYcjg9glL4JC85luiLre36okhGl]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001QG21Tth9-f5nMn3z2oR8qSAXG7c3KxyilmZY-6mtgHSJkj5KUFe97UCe1LEjoGLjZne-BeXMJh1F794Q9_jxT3lmm0N03YLx0flfSEMvaaiRM2KyG82xHq2_5vG2Vi_feRVt7FAJr_d2bhKH1CcmIKyvjM674hVcaWSYmG4CROevalV6lZvvIC7xQxo2NEqHE_jKFQX0EPIX_eRQV65IWUfsZqkVQ4QkbmxXNn6pAyxnbvo_VPOwGNsbBTX1BuleFKY3L4j-v6LQujC9taPOlu0NXc_kStu5]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?e=001QG21Tth9-f6klQQYHll-8RqgNwbFixgEZdo31rUn9BGOsgL643371Q4W3qiHf-dc5BFmO4JpU3gX5LfVCLGlvXagEDVOoAsdzlMIucKjdIYMcmcbXKXtlquvw2NjrnpaFxghKMLooiK7KSJ6xS9vj-fc_0iUaH-C]
Join AFSA Video 
[http://r20.rs6.net/tn.jsp?e=001QG21Tth9-f60uS6xUKjUFBFvdBuQP5uMeqCPBvKVG0iZPLApVkFFi-fsGwzPAtmFWsn7V-CzV5Xlmv7SEu5DggCMnjt9io5tiaS5mRYI2zq62oFFG_jxDYxWhs9rKswMDtPsBrAaqb6ljFmqT0XDgSq8LQocuT9CMq5gjpH05uQ=]
National  
[http://r20.rs6.net/tn.jsp?e=001QG21Tth9-f5XRXuewW_hN8N22m67jLO_Fq0M0lcFBkJyuM2t2CA5Hc4xTcrBQtPBqa7DH8ucJVqZBcFUgcbqFZdIFyMqNRl5X9lzRczu5SoC-lQp3bZYUjG_YqU6xDKK]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?e=001QG21Tth9-f5XRXuewW_hN8N22m67jLO_Fq0M0lcFBkJyuM2t2CA5Hc4xTcrBQtPBqa7DH8ucJVqZBcFUgcbqFZdIFyMqNRl5X9lzRczu5SoC-lQp3bZYUjG_YqU6xDKK]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?e=001QG21Tth9-f7EniD8IJfQb9_7_zAUdeYjTUopVfotPTId48MRm7G1xo90ZFhiHuzh3jSK9RJD-Z8jQK_dUE-o0NiP0nPnQ5YX4RHEGqMSihA_wq5pGCnUGuVw2lbmd3xG3RConc4iKL1hfy1r4JRTnyhnguFwil8a]
Technical Services 
[http://r20.rs6.net/tn.jsp?e=001QG21Tth9-f44ed1qOamQ_ETZVNLOMTY5s7X3YxBkjlmJQBSBFn5evY9yW6hu5J604hDg1zQDgTqL4Glp7HsNNFUG-yopqBVKz-kus6pzkTYaj664p-fIA48oozvW3vemAyyxklWaW8PBddUdmKvRFA==]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?e=001QG21Tth9-f7YQRG13K6brzuGvm7eopVNhE-LSiGZp6XR3CcMYIG7R0VE3UO6XflBpQw_zGEvyYssGhd6ia1N3kX0Giy8etjMdRGiFyOCyv1E50_b_a7ZHu3i6XQWkBlmamFS17UK5L1jKRku_d0RoyKwHQkXLkxpCe0GQ6CC4CtxcDrsgu0FeA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1114984511613


This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001mUkGF8ix_2RPQfgoo8DXkQ%3D%3D&llr=gdnaptcab


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001mUkGF8ix_2RPQfgoo8DXkQ%3D%3D&llr=gdnaptcab


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp


Online Marketing by
Constant Contact(R)
www.constantcontact.com


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to