American Fire Sprinkler Association [http://www.firesprinkler.org/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

AFSA Technical Update
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

A newsletter dealing with codes and other technical issues

October 2, 2013
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Sprinkler at Bottom of Stair Shafts

"Is it the intent that the head be underneath the lowest landing, typically the 
mid-landing, or underneath the lowest main floor landing or both since coverage 
under one will typically not spray over the full floor area below the other?"

We have reviewed NFPA 13, 2013 edition as the applicable standard. Our informal 
interpretation is that it is the intermediate landing.

The technical committee has been wrestling with the issue for several cycles. In
 the 2007 edition it stated in noncombustible shafts to place the sprinkler at 
the
top and under the first landing at the bottom of the shaft in Section 
8.15.3.2.1.
In the 2010 edition it was modified to say under the first accessible landing at
 the bottom of the shaft.  The issue of concern is despite the code saying not 
to
store things in the stairways, it happens.  This occurs when there is an offset 
for example the stairs go up the left side of the shaft and the floor continues 
to the right of the stairs to the rear of the shaft. In this location you are 
standing
under the first intermediate landing. That is where the sprinkler goes. The 
landing
directly over the door is the second landing. If the open floor beside the 
stairs
is enclosed, then the use of the stairs typically keeps the remaining area 
clear.
As such, the technical committee has deleted the need for the sprinkler at the 
bottom
for such conditions. The 2013 edition added a new section 8.15.3.2.3.1: 
Sprinklers
shall be permitted to be omitted from the bottom of the stairwell when the space
 under the stairs at the bottom is blocked off so that storage cannot occur.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

NFPA Document Revisions
Below is a partial list of documents under revision.
NFPA Documents currently accepting public input:
NFPA 14 
[http://r20.rs6.net/tn.jsp?e=001qrwX4CPDHiMGGJ0eUipm0KZBuNNgIi4kDQ4oj5Vxk-eQMX1UZA-ytwB_km61L_LGWsIJXXDJeOGyOQZ3OCZAG0CZfdS0pa5ilu4nLyLAmd4EP1El8aW15g==]
Standard for the Installation of Standpipe and Hose Systems
NFPA 15 
[http://r20.rs6.net/tn.jsp?e=001qrwX4CPDHiOcN_96FPpLVcS0MINrTjyhbN7oilm14xUv5Nehg1RUVY44YCj4kIhPBR8OtUOJK9hx2w3uO_e7TLBKGG-aWX_Zx0tQ2b5ANfbn-8peuLemMA==]
Standard for Water Spray Fixed Systems for Fire Protection
NFPA 214 
[http://r20.rs6.net/tn.jsp?e=001qrwX4CPDHiP-zNAjjMoCQboXAi1g6f2P4g39HobKQrvOlaXMKxt8ruwnkfBU7M5DtMKGq64Q2WVvTTVtX9CBAo3B6Zw1zaParFJqTs5QpeAhw2K1Fm4eBQ==]
Standard on Water-Cooling Towers
NFPA 232 
[http://r20.rs6.net/tn.jsp?e=001qrwX4CPDHiO1NEwSyj2VmtmAAqXn5E4NYw-8ydRLdNlIMIzJ3KhmjtfI_r2RUx0oWlDOhPxrA43Pwz5aVr3m1BdR1jVOKYxZoxx_7PkVxWHIUhNPXowbmw==]
Standard for the Protection of Records
Documents currently accepting public comment:
NFPA 11 
[http://r20.rs6.net/tn.jsp?e=001qrwX4CPDHiMADoJOMQOSdPwDWgXeFQ8kW9t9PjkjpIpQvFjWkOKhVY-UK23vWTP8zG4SJVbxmCGSnlE6Fi0YzYiy2Sb4UjO1uZOaeCTRMRormO2D6n2CbQ==]
Standard for Low-, Medium-, and High-Expansion Foam
NFPA 13E 
[http://r20.rs6.net/tn.jsp?e=001qrwX4CPDHiNnFVpWcMB9H4JTScEdizjpOXhUxYYJ8d4YEgVwM7jdLTo1Ciiqcapa3dUOClrjb2o1cwEYEWvCxXqCrl0c7zvj9BI3tQ-lWBrbfxJBovRTaQ==]
Recommended Practice for Fire Department Operations in Properties Protected by 
Sprinkler
and Standpipe Systems
NFPA 16 
[http://r20.rs6.net/tn.jsp?e=001qrwX4CPDHiMoBeFyrn4HM_Dl0rIUCn9wRx7xO5y8ADaaXDbwU-Sny4GZ3BXDW_D7_dr_kOTHcwOErON16387fAw7X1t3MbNn5Rc3uCyb8lv_9cwQ7_dHcQ==]
Standard for the Installation of Foam-Water Sprinkler and Foam-Water Spray 
Systems
NFPA 33 
[http://r20.rs6.net/tn.jsp?e=001qrwX4CPDHiP8tnEWiFuO9OlONjnXd3VdB6JhhgkbYnUiYTPHm1-U2rL9l58SgXrNegkpxdxEjihmEJW7iWhALZ5K0Zx6ASCr_rpprdXy413CgWNmuN6QRw==]
Standard for Spray Application Using Flammable or Combustible Materials
NFPA 45 
[http://r20.rs6.net/tn.jsp?e=001qrwX4CPDHiNIF--OhvXfGhhP44xDD9iYj7QgtGAxVjGWan28p3e-V_S41Ug5XyOBVSId_trfYEoO5SvdD7tp38PHm75iAKFsSru4vqfCtD8Bjiqm6554hA==]
Standard on Fire Protection for Laboratories Using Chemicals
Not a member of NFPA?  See nfpa.org/freeaccess 
[http://r20.rs6.net/tn.jsp?e=001qrwX4CPDHiORSuz5sodX82hNMYNv_Y7O_qYjTqFriyxT1Nq8d1XCL7XiIjkWGYNbq8_mdDXsstUoApmyDgzTg-SWTvv3kajUn27D7rEEAedIy_TlmvyB7KCZ0Gnd6GPl]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001qrwX4CPDHiNrTdVIsUeq9UNEwe7vSxfhEGOvdyrJrzh5MJxG_TcxwDisM0KeMRoYbgz0BGik9An12ESqV84NKPndI63mzNxp8EPvrB5iQzPnKSHFcP7xBz8bl-nfC999]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2012, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?e=001qrwX4CPDHiM1beUnZz3ftmxPlEhU4La3W0-aMzxFA9RptPHMzbti8Iy8gP9s27EdEKfVKsV_4aeKHo7DkdUCz1tfbim6ckQGQwad4pptavaW_eHZypVUORs2s-sETQ28KzascGBi2eePeWUmImBCTQMHCPvUnwiq1I-uC7Kjqama1lDfxxpKMNO0LmErgGgsuETilDEVo5drDde6w1nEeg==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
Oct. 28 - Nov. 8, 2013

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001qrwX4CPDHiO5kYpbDrEnIeTnZZsyMxofZOvnyqu7oA92667t0hEqFAUdqs1Mr8Jh6w4A_0j8SF31QtdDR6wj2Op1suCTnY997x6Eq4WRQBhU5P4oA_SMn_XU87YHjjGX8Y7AHJtLtxeArNrvLEYbaHiL_E-XWG70j2qkUfjfqZqqFk3zQgs--mTkemcbaxwJf4kJ0KAzyZVJyVTYnXDwRKur1q2tqQUywj9gBN5vVXCm8rnE3IxmOzVO27VdUdvYdiVingtrDejizi6x27UXvttBHzPLoenV].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?e=001qrwX4CPDHiOGh6xajmLCf8gcYRbsqYBh--zOa2U9kksSNYzNFtgEAxgSQarGOLcVvhgQR7RwRto1lbAS2qYuLYgQwkYoOCmg1SjvPi5c22UQhlIc8r8B3hj5IAs-CvO7]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Webinar
NFPA 20
2013 Update
Nov. 20, 2013
11 am - 12:30 pm
Central Time

$15 fee for

1.5 CPDs

or 0.15 CEUs

Non-members $140

Register at

Webinars 
[http://r20.rs6.net/tn.jsp?e=001qrwX4CPDHiNOJpAf4CDertnlKeTAn_iQ6-Rdlr8O6PZZHPff6pvE6Tz6qbNG1MLp-88urhYVnZW6YdBO0BlXb3KFkyTgtWos_HULR3QuJShIn69Qbm2yO9i5QI3c6E5zW2V2zFMUrxN-JtNTw10bGN7xt9PYjBrQ-9ODQrObzSw=]
Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001qrwX4CPDHiO5kYpbDrEnIeTnZZsyMxofZOvnyqu7oA92667t0hEqFAUdqs1Mr8Jh6w4A_0j8SF31QtdDR6wj2Op1suCTnY997x6Eq4WRQBhU5P4oA_SMn_XU87YHjjGX8Y7AHJtLtxeArNrvLEYbaHiL_E-XWG70j2qkUfjfqZqqFk3zQgs--mTkemcbaxwJf4kJ0KAzyZVJyVTYnXDwRKur1q2tqQUywj9gBN5vVXCm8rnE3IxmOzVO27VdUdvYdiVingtrDejizi6x27UXvttBHzPLoenV].
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?e=001qrwX4CPDHiMttAS8fw6faaTyQ4-it0c4UUzPsX8OFKZVBVWFDDG0NFO9QYH7OL-A8Uj2gJFG7MeqUaeeYOfy98MqZ9uU_lmfLTz8Htj3KrfA8riuWHaAnTbpjOKJfMxXwDuN74rae86i0iP3X2PaXljC7iLnRTyXnoUthe9nVJ8=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?e=001qrwX4CPDHiPzeHQ65e-99E4G3x17mR6XHIgCXSYym5MBNS0zyidNvWiXTR63aQWJFOQm_5NM9mplqeyRySo6CAlXPMqjR3A9iaUe7tBZMhBK7RMe97xlcVhHo8dAFBIbYKXNvMcTG4nHL8gsaFag66cJQs_TMAT0GtiHCLRfLQM=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001qrwX4CPDHiNrTdVIsUeq9UNEwe7vSxfhEGOvdyrJrzh5MJxG_TcxwDisM0KeMRoYbgz0BGik9An12ESqV84NKPndI63mzNxp8EPvrB5iQzPnKSHFcP7xBz8bl-nfC999]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001qrwX4CPDHiO5kYpbDrEnIeTnZZsyMxofZOvnyqu7oA92667t0hEqFAUdqs1Mr8Jh6w4A_0j8SF31QtdDR6wj2Op1suCTnY997x6Eq4WRQBhU5P4oA_SMn_XU87YHjjGX8Y7AHJtLtxeArNrvLEYbaHiL_E-XWG70j2qkUfjfqZqqFk3zQgs--mTkemcbaxwJf4kJ0KAzyZVJyVTYnXDwRKur1q2tqQUywj9gBN5vVXCm8rnE3IxmOzVO27VdUdvYdiVingtrDejizi6x27UXvttBHzPLoenV]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?e=001qrwX4CPDHiP01EpG3y1MeqixnhM-s1Qci6ECintAPxxSuQmNnEucPCsbJncT5iUAV0w_GLtIlnga5xIm9D_C0HGm56bNd-NPAgmcOs3zc9q72-O7z_LHNn7zp7LY8WgD9yDiWowqs35PO9Yp9GneJi73s_5d6L_G]
Join AFSA Video 
[http://r20.rs6.net/tn.jsp?e=001qrwX4CPDHiNejnIWkPsNd2_r6mVGOyKh-i_pWdO-JYFjDD4f3byWZ_YHx7t3CigiKCVjy-k-3S-6KejLO-qUm5uATSCKGAPFr6jS156-apylUaRjT-svpNPsyWX_0efo9TQlIdAyrgV4rtZgcp4fGfpEo3FOXEtoDBLx9Vp7doQ=]
National  
[http://r20.rs6.net/tn.jsp?e=001qrwX4CPDHiPsw49KBHNmAXMMrpsDWAwp2tMxNl7GLzCIsuX5dypYhuFkx-RTO7l1zeyrq50Fe2n90_sgyNwU2_rruicW0Mr8KFf5h4gB48bBiP5TUYAm8X7lRmpWK56S]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?e=001qrwX4CPDHiPsw49KBHNmAXMMrpsDWAwp2tMxNl7GLzCIsuX5dypYhuFkx-RTO7l1zeyrq50Fe2n90_sgyNwU2_rruicW0Mr8KFf5h4gB48bBiP5TUYAm8X7lRmpWK56S]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?e=001qrwX4CPDHiNriEbYkBYpwME2ge9h1P80VJ1GrIdi7eovZVoB9hSOCrQKon5yPVMUEx72efH5aMsyMNSo7nkhQCWogf5uHm53g1NhiNbtKFoR0s28qUojTBwr62tJ5euk7Er_EEvMroc8wTogbz4gydoefudS07my]
Technical Services 
[http://r20.rs6.net/tn.jsp?e=001qrwX4CPDHiOEA-xY7GfjRIVIoU6wmMsx9fzuEVv0knpglJtPsj5UlO_ZBrAtMTfa4SHCjUAhpVXrjNW8JAMET2Rt7WBJWFvgRAjFXVUYhbJYpVXn2RH2bW35vAqc0Tg4tI2KckGAoqQFiJaKzr9MeQ==]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?e=001qrwX4CPDHiMbYZs_379Tvx_97XflsOQtyS2kLfjAV3ccPgXPlfF97E0gKA5yDW84NRRXLqZSfP8Ppa5QzYh4sgX_EGCiuz4ZBtbuuXP_XXp_rBk-4ZNJC2YvzqOjOOndyOBG98dB--8yaP0BqXcN7gO6k_7mJv5gRcLrcG-Fxgd3pNwQDrj5iA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1115137635275


This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001oZNRPPdDVAOSTad9TUdYeA%3D%3D&llr=gdnaptcab


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001oZNRPPdDVAOSTad9TUdYeA%3D%3D&llr=gdnaptcab


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp


Online Marketing by
Constant Contact(R)
www.constantcontact.com


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to