American Fire Sprinkler Association [http://www.firesprinkler.org/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
AFSA Technical Update
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
A newsletter dealing with codes and other technical issues
January 23, 2014
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Nursing Home Bathrooms
"We have 100 bathrooms of a nursing home that have a 1-piece fiberglass shower
fixture.
The actual bathroom size is approximately 5 ft x 6 ft noncombustible
construction.
There is a bulkhead from the ceiling down to the top of the shower stall that
varies
between 11 in. to 15 in. A state inspector states that the showers need
protection.
There are residential sprinklers installed in the bathrooms. Are sprinklers
also
required in the showers?"
Our informal interpretation is that one sprinkler in the bathroom is all that
should
be required. We have reviewed NFPA 13, 2007 edition that you indicated as the
applicable
standard.
The 2013 edition of NFPA 13 includes a new section to specifically address this
issue. Section 8.5.5.4 Closets states, "In all closets and compartments,
including
those closets housing mechanical equipment, that are not larger than 400 cu. ft.
in size, a single sprinkler at the highest ceiling space shall be sufficient
without
regard to obstructions or minimum distance to the wall." The bathroom is a
compartment
and this application qualifies to apply this section. This concept has been
included
in NFPA 13R for many cycles, but it is now included in the 2013 edition of NFPA
13.
The issue of obstructions in compartments that creates shadowing has always been
allowed by NFPA 13 and is considered acceptable. Although a specified allowed
amount
of shadowing has not been quantified, there has been additional attention to
this
issue in more current editions of NFPA 13. This additional information does not
change the requirements of the 2007 edition but simply helps clarify the intent
of that edition. For that reason, this interpretation includes this information.
It may also be helpful in incorporating information from later editions of the
standard to realize that the 2007 edition of NFPA 13 allows alternate
arrangements
to be applied, per Section 1.6, as long as the level of safety prescribed by the
standard is not lowered. What better means for assuring an equivalent
application
than acceptance of or statements by the NFPA 13 technical committee. Thus minor
obstructions are very common and the intent of NFPA 13 for providing protection
throughout the area is satisfied without covering every square inch of floor
area
and without installing an additional sprinkler. This is of particular value
since
one of the main objectives of the sprinkler system is to keep the upper layer
cool,
preventing flashover, thus controlling the fire. This is supported by Annex
A.8.4.5.1
that states, "The response and water distribution pattern of listed residential
sprinklers have been shown by extensive fire testing to provide better control
than
spray sprinklers in residential occupancies. These sprinklers are intended to
prevent
flashover in the room of fire origin, thus improving the chance for occupants to
escape or be evacuated." As such, no additional sprinklers are needed to cover
the shower areas within these rooms.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
firesprinkler.org
[http://r20.rs6.net/tn.jsp?f=001m7UR5vovRgjY0Ong0t41rWJBfGoFxEPBVowiKxlVGqUp2HyS1g32SEtbNzBS39DoMZObal7UN-OgD9R6q18DecxvVW1rdeio30a8z4FMQoVTxD0XImbPUwS1gE2-DQEipnsPLCKQX71vb2erUDv8NcqvGDnWiRMCkIiTd1Z0pJ9gAdVI7-nUhA==&c=YcoCzmsKeAZWuToOjtr1h_LCGaf0P4yQ2WGeItOtbF9VO4ghYQNEaQ==&ch=yYkckJGf2grMFjqcK9yI2iA5-m33akAJG6shW99X9EXY8yQJOVODXg==]
Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
in fire protection engineering. This is provided with the understanding that
the
AFSA assumes no liability for this opinion or actions taken on it and they are
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2012, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
PDF Version
PDF Link
[http://r20.rs6.net/tn.jsp?f=001m7UR5vovRgjY0Ong0t41rWJBfGoFxEPBVowiKxlVGqUp2HyS1g32SFGXVlDCmmWtErvN5UY3D6RwuzQUcKy_afjRLe23fEOTiy2c5DxE5Z26Ehxz4lnxlwoMDS188y-S3OoVpBzc1p_U5RJZtv0Imh1Qh1Q0rqlucQlmkW4ixy5z51i_xUtVHYqxoXY4RV6vLdS-1C1Lbu7BCw3X8B0akjau4fMWmNbrID_SSVLw2X0P83yYOBc7yliglKgxWDLtQZpFYRNLSwM=&c=YcoCzmsKeAZWuToOjtr1h_LCGaf0P4yQ2WGeItOtbF9VO4ghYQNEaQ==&ch=yYkckJGf2grMFjqcK9yI2iA5-m33akAJG6shW99X9EXY8yQJOVODXg==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
"Liabilities & Pitfalls of Contract Clauses with Regard to Inspection, Testing,
& Maintenance of Sprinkler Systems"
by
Terry Victor
&
Joe Canterbury
Monday, February 3, 2014
11:00a.m. - 12:30 p.m. Central.
Free to AFSA members!
This 1.5-hour webinar will be presented FREE to all AFSA members.
Register Button
[http://r20.rs6.net/tn.jsp?f=001m7UR5vovRgjY0Ong0t41rWJBfGoFxEPBVowiKxlVGqUp2HyS1g32SO5h3Rn04SiDKvvA9D8efpLDJf_bg321JnIc1_8DMM3HM5lNUdFplvQE0BYlC-dzauiECrmWCYd5jUse9xpFStF0CLn7jkJWA8THjHDrcyQcVdD76VD0Fqw48QU4nJjTNSRElaOoiC8pfQ0sjVX51RzNmxDpU7EJA5DM5uE5j_FX&c=YcoCzmsKeAZWuToOjtr1h_LCGaf0P4yQ2WGeItOtbF9VO4ghYQNEaQ==&ch=yYkckJGf2grMFjqcK9yI2iA5-m33akAJG6shW99X9EXY8yQJOVODXg==]
Check our calendar
[http://r20.rs6.net/tn.jsp?f=001m7UR5vovRgjY0Ong0t41rWJBfGoFxEPBVowiKxlVGqUp2HyS1g32SCb7-j_Gt5tvsDYMblrKFNoYLx9cAmNLYQot-BjYdMk-ZigPXISbWMSgITaJJeJIZ16xsIsKc156sjHybycKlc_iF3fnMwyEETnXNmmQzUYp8P8ZCJQdfdW6Vj95TA6aYtkcDb717WGlk7tSWT_ihRrcWOTb8mYJ9YCVYshjG0NyEN2g3f9CGiEhhNzO5c2SsLpdgb7bSZ0LJT0TI7yF0Q1PLVmHtqNlUDANoURfl6iTKm34P5NL4M6aUQe0QrQJYcHHj7Gr77yo-LuKPkUk-_rnLFD6oBsOxg==&c=YcoCzmsKeAZWuToOjtr1h_LCGaf0P4yQ2WGeItOtbF9VO4ghYQNEaQ==&ch=yYkckJGf2grMFjqcK9yI2iA5-m33akAJG6shW99X9EXY8yQJOVODXg==]
to view upcoming training.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
Mar 30 - Apr 11, 2014
Check our calendar to view upcoming training.
For details and/or to register, visit the AFSA Calendar
[http://r20.rs6.net/tn.jsp?f=001m7UR5vovRgjY0Ong0t41rWJBfGoFxEPBVowiKxlVGqUp2HyS1g32SCb7-j_Gt5tvsDYMblrKFNoYLx9cAmNLYQot-BjYdMk-ZigPXISbWMSgITaJJeJIZ16xsIsKc156sjHybycKlc_iF3fnMwyEETnXNmmQzUYp8P8ZCJQdfdW6Vj95TA6aYtkcDb717WGlk7tSWT_ihRrcWOTb8mYJ9YCVYshjG0NyEN2g3f9CGiEhhNzO5c2SsLpdgb7bSZ0LJT0TI7yF0Q1PLVmHtqNlUDANoURfl6iTKm34P5NL4M6aUQe0QrQJYcHHj7Gr77yo-LuKPkUk-_rnLFD6oBsOxg==&c=YcoCzmsKeAZWuToOjtr1h_LCGaf0P4yQ2WGeItOtbF9VO4ghYQNEaQ==&ch=yYkckJGf2grMFjqcK9yI2iA5-m33akAJG6shW99X9EXY8yQJOVODXg==].
e-campus_logo
[http://r20.rs6.net/tn.jsp?f=001m7UR5vovRgjY0Ong0t41rWJBfGoFxEPBVowiKxlVGqUp2HyS1g32SGsVbny1JwaQj45ZJV_K8v1B6HHEgA-C7P2qbXo2C8IlPfHHh0ggYvLn4oxXt8Knk5WZ3diD1sMPssNh2ZOSaSY59ehlP_hzcF9HheCH6MTGif0eDfOQwX29zRu4ZiVurg==&c=YcoCzmsKeAZWuToOjtr1h_LCGaf0P4yQ2WGeItOtbF9VO4ghYQNEaQ==&ch=yYkckJGf2grMFjqcK9yI2iA5-m33akAJG6shW99X9EXY8yQJOVODXg==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Free Subscription to Sprinkler Age
[http://r20.rs6.net/tn.jsp?f=001m7UR5vovRgjY0Ong0t41rWJBfGoFxEPBVowiKxlVGqUp2HyS1g32SByUmXTw62m6T1EcdUwsA3gQJp1wNZVge3PtkCwOMuJekXI5zP9CfkNSn8FkZvL6dj-mEiT28zNuHLFOEGpTuCXeAkelV0-ukz8ibVAL2klIqbV1Cu7isVWjNmnSLQO2ozDE9jdSrTrtl6b_iyWTBKYqcRzQliosF91-XJeotObm&c=YcoCzmsKeAZWuToOjtr1h_LCGaf0P4yQ2WGeItOtbF9VO4ghYQNEaQ==&ch=yYkckJGf2grMFjqcK9yI2iA5-m33akAJG6shW99X9EXY8yQJOVODXg==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Quality Contractor
[http://r20.rs6.net/tn.jsp?f=001m7UR5vovRgjY0Ong0t41rWJBfGoFxEPBVowiKxlVGqUp2HyS1g32SHYykUTLpiBhdnWE5ZhxCqlweENH6gdqTjZ27doTb6v1K-otnoSyFzcQdx9k3_p3T5fE-VLLYyCa29rogdQG0m9i1XfMDoAMcxDbvwPvHF0isAl8GC-OgsUkNvfc3D2zzFvsPVRIcaGdQ4WKlXQaqVYntuxDk1HuL6sinswoGSQb&c=YcoCzmsKeAZWuToOjtr1h_LCGaf0P4yQ2WGeItOtbF9VO4ghYQNEaQ==&ch=yYkckJGf2grMFjqcK9yI2iA5-m33akAJG6shW99X9EXY8yQJOVODXg==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Quick Links
Firesprinkler.org
[http://r20.rs6.net/tn.jsp?f=001m7UR5vovRgjY0Ong0t41rWJBfGoFxEPBVowiKxlVGqUp2HyS1g32SEtbNzBS39DoMZObal7UN-OgD9R6q18DecxvVW1rdeio30a8z4FMQoVTxD0XImbPUwS1gE2-DQEipnsPLCKQX71vb2erUDv8NcqvGDnWiRMCkIiTd1Z0pJ9gAdVI7-nUhA==&c=YcoCzmsKeAZWuToOjtr1h_LCGaf0P4yQ2WGeItOtbF9VO4ghYQNEaQ==&ch=yYkckJGf2grMFjqcK9yI2iA5-m33akAJG6shW99X9EXY8yQJOVODXg==]
AFSA Calendar
[http://r20.rs6.net/tn.jsp?f=001m7UR5vovRgjY0Ong0t41rWJBfGoFxEPBVowiKxlVGqUp2HyS1g32SCb7-j_Gt5tvsDYMblrKFNoYLx9cAmNLYQot-BjYdMk-ZigPXISbWMSgITaJJeJIZ16xsIsKc156sjHybycKlc_iF3fnMwyEETnXNmmQzUYp8P8ZCJQdfdW6Vj95TA6aYtkcDb717WGlk7tSWT_ihRrcWOTb8mYJ9YCVYshjG0NyEN2g3f9CGiEhhNzO5c2SsLpdgb7bSZ0LJT0TI7yF0Q1PLVmHtqNlUDANoURfl6iTKm34P5NL4M6aUQe0QrQJYcHHj7Gr77yo-LuKPkUk-_rnLFD6oBsOxg==&c=YcoCzmsKeAZWuToOjtr1h_LCGaf0P4yQ2WGeItOtbF9VO4ghYQNEaQ==&ch=yYkckJGf2grMFjqcK9yI2iA5-m33akAJG6shW99X9EXY8yQJOVODXg==]
Buyer's Guide
[http://r20.rs6.net/tn.jsp?f=001m7UR5vovRgjY0Ong0t41rWJBfGoFxEPBVowiKxlVGqUp2HyS1g32SEtbNzBS39Do6YQhfTNAdoLpV9F8ShYejx_P1w-LSmdtgc9oA-x2-ifGD3CU0AWcvUFhZ3jMTjk2eNFy289g6c3FEt2Qu6FgkrA7l_G8ThMsj7rCQOYTFnE_3pPr0TPKpehzu6beZU0Y1_Gkr1Wii9_Ldv6y8DS8Gg==&c=YcoCzmsKeAZWuToOjtr1h_LCGaf0P4yQ2WGeItOtbF9VO4ghYQNEaQ==&ch=yYkckJGf2grMFjqcK9yI2iA5-m33akAJG6shW99X9EXY8yQJOVODXg==]
Join AFSA Video
[http://r20.rs6.net/tn.jsp?f=001m7UR5vovRgjY0Ong0t41rWJBfGoFxEPBVowiKxlVGqUp2HyS1g32SEtbNzBS39DokRyHbWWVcj7HCCFFnbJ4oViV94AD926X_18n4HF74QIqUz5CiJvgKV3b3Ipr023OIrLNFLLrvTzfW3WaAHv18xi7YI9M7iFQgFUnl3pwTzeceZTDsQBqivGuPlJNCCXPcDcbR__YJvAl1MymvLXx9A==&c=YcoCzmsKeAZWuToOjtr1h_LCGaf0P4yQ2WGeItOtbF9VO4ghYQNEaQ==&ch=yYkckJGf2grMFjqcK9yI2iA5-m33akAJG6shW99X9EXY8yQJOVODXg==]
National
[http://r20.rs6.net/tn.jsp?f=001m7UR5vovRgjY0Ong0t41rWJBfGoFxEPBVowiKxlVGqUp2HyS1g32SJdJLFCwE6zUk0Ielhwt4dGovANujBTftKXOwo0oRPc-xJK5Id56NczwTpsLuc5B1J_KMGAS03jrgurJhqucZ8A357VDU5C4ocYiWzmFuztjwX26ANT__mZ1NmoRQmL-NQ==&c=YcoCzmsKeAZWuToOjtr1h_LCGaf0P4yQ2WGeItOtbF9VO4ghYQNEaQ==&ch=yYkckJGf2grMFjqcK9yI2iA5-m33akAJG6shW99X9EXY8yQJOVODXg==]
Scholarship Contest
[http://r20.rs6.net/tn.jsp?f=001m7UR5vovRgjY0Ong0t41rWJBfGoFxEPBVowiKxlVGqUp2HyS1g32SJdJLFCwE6zUk0Ielhwt4dGovANujBTftKXOwo0oRPc-xJK5Id56NczwTpsLuc5B1J_KMGAS03jrgurJhqucZ8A357VDU5C4ocYiWzmFuztjwX26ANT__mZ1NmoRQmL-NQ==&c=YcoCzmsKeAZWuToOjtr1h_LCGaf0P4yQ2WGeItOtbF9VO4ghYQNEaQ==&ch=yYkckJGf2grMFjqcK9yI2iA5-m33akAJG6shW99X9EXY8yQJOVODXg==]
OSHA Alliance
[http://r20.rs6.net/tn.jsp?f=001m7UR5vovRgjY0Ong0t41rWJBfGoFxEPBVowiKxlVGqUp2HyS1g32SEtbNzBS39DounRf6sRFl1Q3QQfsxa4XNvs_vUmLGWafgjoa8FpzQFlAQfV9KOtaYbM8lfoKIFIy4sTj8K6BcWy2jR3j3m9vA-B6XmMHxdmsVj5Ncyj333Q0DdGMgBXY7t3k3BBUY1T9CpGYLAw29WnLwdgJJ08o9w==&c=YcoCzmsKeAZWuToOjtr1h_LCGaf0P4yQ2WGeItOtbF9VO4ghYQNEaQ==&ch=yYkckJGf2grMFjqcK9yI2iA5-m33akAJG6shW99X9EXY8yQJOVODXg==]
Technical Services
[http://r20.rs6.net/tn.jsp?f=001m7UR5vovRgjY0Ong0t41rWJBfGoFxEPBVowiKxlVGqUp2HyS1g32SPQh9Q64RrLUXBtGD3AAtsy-fmniNaRyQREM7u4QesdXbC_YifVWQwuD5XdhNqI9NzKqwjMBVU783DqMR9IOf-YzjqnB03WPlRCjxprmO_SrpJXfZLbl34hTQu5Q42wQ4J8-lTOU3ZSN&c=YcoCzmsKeAZWuToOjtr1h_LCGaf0P4yQ2WGeItOtbF9VO4ghYQNEaQ==&ch=yYkckJGf2grMFjqcK9yI2iA5-m33akAJG6shW99X9EXY8yQJOVODXg==]
Informal Interpretation Request Form
[http://r20.rs6.net/tn.jsp?f=001m7UR5vovRgjY0Ong0t41rWJBfGoFxEPBVowiKxlVGqUp2HyS1g32SODrWq1TiHc4wRbYcNglvwdaaD3X9-bEx_LyBAWRxPamvsNriFnp4d5xAsQx4gwKn_7zgi-5NbT4x4eG5Pe4FpnjGDQmG3CobJAhRYfCPoAfVURdY0lxiCcQK1IH3DBbamp_kAOX12AKvhXLdJIWN2GRATTCWvFu57w-ZK8xl9oM&c=YcoCzmsKeAZWuToOjtr1h_LCGaf0P4yQ2WGeItOtbF9VO4ghYQNEaQ==&ch=yYkckJGf2grMFjqcK9yI2iA5-m33akAJG6shW99X9EXY8yQJOVODXg==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Join Our Mailing List
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1116336827830
This email was sent to [email protected] by
[email protected].
Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=0229c230-354a-11e3-852c-d4ae527b8c41&ca=a0faa868-b6ce-425a-8575-b5ccfca12996
Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=0229c230-354a-11e3-852c-d4ae527b8c41&ca=a0faa868-b6ce-425a-8575-b5ccfca12996
Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp
Online Marketing by
Constant Contact(R)
www.constantcontact.com
American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas |
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org