Beam Near Wall Creates Pocket

"We have a metal building where the end wall has a column 1ft - 10½-inches 
inside
the face of the wall to the centerline of columns which also creates a 16-inch 
gap
from inside face of the wall girts (horizontal structural member) to the inside 
face of the beam flange.  We have a branch line 7 ft - 5 ½-inches from the 
inside
face of the wall and 5 ft - 7 ½-inches to the centerline of the column.  The 
standard
response heads will not spray to the wall due to the beam depth in some areas as
 it varies in depth from 50-inches to 22-inches.  Does the 16-inch gap require 
protection?
 Where should sprinklers be located down low below the beam or in the 16-inch 
space
within 12-inches from the deck?"

We have reviewed NFPA 13, 2013 edition as the applicable standard.  Our informal
 interpretation is that additional sprinklers are required between the beam and 
the wall.

The beam creates a ceiling pocket against the wall.  The problem with applying 
the
ceiling pocket rules of Section 8.6.7.2 is that there is a problem with meeting 
item number 3 that indicates that the entire floor under the unprotected ceiling
 pocket is protected by the sprinklers at the lower ceiling elevation.  The 
other
problem is number 6 where quick response sprinklers were not used.  The beam is 
more of a valance rather than a ceiling pocket.  The beam obstructs the 
sprinkler
at the ceiling level where the entire floor area is not protected.  Thus 
additional
sprinklers are needed on the other side of the beam.  If the sprinklers could be
 located to meet the obstruction rules of Section 8.6.5.1.2 (Beam Rule), then 
additional
sprinklers would not be needed since the entire floor area would be protected.  
Confusion can exist between applying the requirements of obstruction against 
walls
(Soffit Rule) and the obstructions to sprinkler discharge (Beam Rule).  The 
advantage
of the Soffit Rule over the Beam Rule is that it allows you to locate a 
sprinkler
closer to the wall than what would be allowed by the use of the Beam Rule.  Note
 that to qualify as a soffit, it must have a solid bottom plate.  You cannot 
apply
the soffit application to a valance, which will not be enclosed at the bottom 
plane.
 If the sprinklers cannot meet either application, an additional sprinkler will 
have to be installed on the other side of the valance.  The beam is too deep in 
this application to meet the Beam Rule.  Next, let's address your concern of 
shadowing
in the corner created by the column.  This is a mute point since it appears that
 sprinklers will be required between the beam and the wall.  If you can meet the
 obstruction rules, you can ignore dry shadow areas created by architectural 
features.
 Some material was added to the 2013 edition of NFPA 13 in A.8.1.1(3) that 
states,
"Notwithstanding the obstruction rules provided in Chapter 8, it is not intended
 or expected that water will fall on the entire floor space of the occupancy.  
When
obstructions or architectural features interfere with the sprinkler's spray 
pattern,
such as columns, angled walls, wing walls, slightly indented walls, and various 
soffit configurations, shadowed areas can occur.  Where small shadowed areas are
 formed on the floor adjacent to their referenced architectural features, these 
shadowed areas are purely on paper and do not take into account the dynamic 
variables
of sprinkler discharge.  Examples of shadow areas are shown in Figure 
A.8.1.1(3)(a)
and Figure A.8.1.1(3)(b)."  Lastly, the sprinklers located between the beam and 
the wall should be placed according to obstructed construction rules.  Steel 
Purlin
Construction is described as obstructed construction in A.3.7.1(8).  Although it
 may be believed the heads will not activate within this narrow space, there is 
no place in the standard that permits the omission of sprinklers.  Your options 
appear to be 1) install sprinklers between the beam and the wall, 2) install a 
bottom
to seal up the space, or 3) get permission from the AHJ to omit sprinklers 
between
the beam and the wall.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001c7txgrTX5XgH2_xgH1hNuFqOA02EVSvfS2A9PRPnTprtYsTX37s6elQXzITuFZ5Lb4yWEsDeLReP_DtqmqTEXocm63E-PuDAh6WdguIXfKY=]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2014, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?e=001c7txgrTX5XgH2_xgH1hNuFqOA02EVSvfS2A9PRPnTprtYsTX37s6elQXzITuFZ5L-AzDRQLr7UIRaUfEfFV7Zvm0eboKmyy-fpDv4IY3qDW2q1DF2Oaqx5Zv1O_KDAlwMlU3ibiyRWlfzPmW_ZviGU1f7RrO-4Kyr9kCbDASpUWaMGsExccngT0PPswakK-ErYX6SKi_YGo=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
Register for
Oct. 13 - 24, 2014
Sept. 8 - 19, 2014
SOLD OUT!
July 14 - 25, 2014
SOLD OUT!

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001c7txgrTX5XgH2_xgH1hNuFqOA02EVSvfS2A9PRPnTprtYsTX37s6elQXzITuFZ5Lb4yWEsDeLRdHdQnuWPrHj0_fOb408axkZdS5kMH-9SUeGZW53qDO1EUx87Rdp9hPJjhLtdjE3zkK1qO6EIen7VTIWpR5PVjC0T5XJTsTAwx5kVKGOQHK6RXUOBEGW70sYyOfaw83Awrclo9OyDgkvIenbCZy6Aa2ks9qJTozB2dz53juPJmA7L6a7bS50U6VHyjFnn6RtwNiDhqZi2d6uw==].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?e=001c7txgrTX5XgH2_xgH1hNuFqOA02EVSvfS2A9PRPnTprtYsTX37s6elQXzITuFZ5Lb4yWEsDeLRfSH2pFRZbZudfrfP4OWClNdc_i3Uk91danWwKQyg8QyQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

AFSA Webinar
NFPA 25, 2014 Edition
by
Russ Leavitt
June 19, 2014
This webinar examines not only the significant revisions that occurred and the 
reasoning
behind the changes, but also proposals that were rejected by the Technical 
Committee.
Cost is FREE for AFSA members.
Register Button 
[http://r20.rs6.net/tn.jsp?e=001c7txgrTX5XgH2_xgH1hNuFqOA02EVSvfS2A9PRPnTprtYsTX37s6elQXzITuFZ5Lb4yWEsDeLReP_DtqmqTEXocm63E-PuDAxTpHRM_4Y5ij5LU005HwuvNPgKFpnCRbHFuftKSp7-vG4Z1xud35UysnYthVcRUZ]
This seminar offers 1.5 CPD and 0.15 CEU.*
(*Note: There is a fee of $15 to acquire the CEU credits. The webinar/content is
 being given free, but the CEUs will have a fee.)
Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001c7txgrTX5XgH2_xgH1hNuFqOA02EVSvfS2A9PRPnTprtYsTX37s6elQXzITuFZ5Lb4yWEsDeLRdHdQnuWPrHj0_fOb408axkZdS5kMH-9SUeGZW53qDO1EUx87Rdp9hPJjhLtdjE3zkK1qO6EIen7VTIWpR5PVjC0T5XJTsTAwx5kVKGOQHK6RXUOBEGW70sYyOfaw83Awrclo9OyDgkvIenbCZy6Aa2ks9qJTozB2dz53juPJmA7L6a7bS50U6VHyjFnn6RtwNiDhqZi2d6uw==].
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?e=001c7txgrTX5XgH2_xgH1hNuFqOA02EVSvfS2A9PRPnTprtYsTX37s6elQXzITuFZ5Lb4yWEsDeLReP_DtqmqTEXocm63E-PuDAxTpHRM_4Y5hGK0Z9WbbyI9FVTOs8zJG1V883v1Yfk4Tc1jYOIr-oggNcUcKnkmTy]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?e=001c7txgrTX5XgH2_xgH1hNuFqOA02EVSvfS2A9PRPnTprtYsTX37s6elQXzITuFZ5Lb4yWEsDeLReP_DtqmqTEXocm63E-PuDAxTpHRM_4Y5gG8Fb3eCNDnzreIKqGluivSzzM1_j69soiJXFN_8bHp9FxCvaD2Tca]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001c7txgrTX5XgH2_xgH1hNuFqOA02EVSvfS2A9PRPnTprtYsTX37s6elQXzITuFZ5Lb4yWEsDeLReP_DtqmqTEXocm63E-PuDAh6WdguIXfKY=]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001c7txgrTX5XgH2_xgH1hNuFqOA02EVSvfS2A9PRPnTprtYsTX37s6elQXzITuFZ5Lb4yWEsDeLRdHdQnuWPrHj0_fOb408axkZdS5kMH-9SUeGZW53qDO1EUx87Rdp9hPJjhLtdjE3zkK1qO6EIen7VTIWpR5PVjC0T5XJTsTAwx5kVKGOQHK6RXUOBEGW70sYyOfaw83Awrclo9OyDgkvIenbCZy6Aa2ks9qJTozB2dz53juPJmA7L6a7bS50U6VHyjFnn6RtwNiDhqZi2d6uw==]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?e=001c7txgrTX5XgH2_xgH1hNuFqOA02EVSvfS2A9PRPnTprtYsTX37s6elQXzITuFZ5Lb4yWEsDeLRfYLN8Le9kgtK_InsE3NuXpV-1Isor_hbghy-plFSANHGtxCI2bxUhxrySu9xjNS7mFIiqOKVPDUg==]
Join AFSA Video 
[http://r20.rs6.net/tn.jsp?e=001c7txgrTX5XgH2_xgH1hNuFqOA02EVSvfS2A9PRPnTprtYsTX37s6elQXzITuFZ5Lb4yWEsDeLRc8x3CDcwi42yKVTMIoDG0hyXy-U7VBGz3AJuffsscKJku2UV2nfGj-koCwfDI506uli8Yr23UFhw==]
National  
[http://r20.rs6.net/tn.jsp?e=001c7txgrTX5XgH2_xgH1hNuFqOA02EVSvfS2A9PRPnTprtYsTX37s6elQXzITuFZ5Lb4yWEsDeLReTvM0qfwRR5JD93-Ej7xI04NIvxaB1EP4HcHQ-a_jLsQ==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?e=001c7txgrTX5XgH2_xgH1hNuFqOA02EVSvfS2A9PRPnTprtYsTX37s6elQXzITuFZ5Lb4yWEsDeLReTvM0qfwRR5JD93-Ej7xI04NIvxaB1EP4HcHQ-a_jLsQ==]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?e=001c7txgrTX5XgH2_xgH1hNuFqOA02EVSvfS2A9PRPnTprtYsTX37s6elQXzITuFZ5Lb4yWEsDeLRdULmApLqIb0Vmb7NPQbPnOe6JqE3OiSqz617B4GSVwEObTsbf701ljClhIkypNbBen0Ppi3kY7hw==]
Technical Services 
[http://r20.rs6.net/tn.jsp?e=001c7txgrTX5XgH2_xgH1hNuFqOA02EVSvfS2A9PRPnTprtYsTX37s6elQXzITuFZ5Lb4yWEsDeLReP_DtqmqTEXocm63E-PuDAxTpHRM_4Y5jyEHyPCs1WEIftgS70Pnuh]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?e=001c7txgrTX5XgH2_xgH1hNuFqOA02EVSvfS2A9PRPnTprtYsTX37s6elQXzITuFZ5Lb4yWEsDeLReP_DtqmqTEXocm63E-PuDAxTpHRM_4Y5jvTbw7rlHhq18GPNKXC7nfT737F1Taj92z4sr9fDUpUeWxOFsQs24K]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686&id=preview]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1117643506360&id=preview


This email was sent to [email protected] by [email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfY-V4yYxBBQbHvk74jf90rEKbatrTBH0Hw%3D%3D&t=001-6OF0jSjy9E0t_Y8o0LeRA%3D%3D&l=001FCSs65SMrsI%3D&id=001b-xBWU3VMkcCDNcOTBJBHAeNvyNZ1QyA&llr=gdnaptcab


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfY-V4yYxBBQbHvk74jf90rEKbatrTBH0Hw%3D%3D&t=001-6OF0jSjy9E0t_Y8o0LeRA%3D%3D&l=001FCSs65SMrsI%3D&id=001b-xBWU3VMkcCDNcOTBJBHAeNvyNZ1QyA&llr=gdnaptcab


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp


Online Marketing by
Constant Contact(R)
www.constantcontact.com


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251

THIS IS A TEST EMAIL ONLY.
This email was sent by the author for the sole purpose of testing a draft 
message. If you believe you have received the message in error, please contact 
the author by replying to this message. Constant Contact takes reports of abuse 
very seriously. If you wish to report abuse, please forward this message to <a 
href="mailto:[email protected]";>[email protected]</a>.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to