American Fire Sprinkler Association [http://www.firesprinkler.org/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
AFSA Technical Update
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
A newsletter dealing with codes and other technical issues
August 8, 2014
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
CMSA Obstruction
"We are renovating an existing warehouse for a new commodity. We are installing
a new system with the K-17 specific application control mode (16.8 K-factor
upright).
A 1 ft x 4 ft light is centered between sprinklers with 4 ft from the sprinkler
to the edge of the light. The top of the light is 18 inches below the
deflector
and the light is 3 inches deep. Does the light present an acceptable
obstruction?"
We have reviewed NFPA 13, 2013 edition that you indicated as the applicable
standard.
Our informal interpretation is that the light should be acceptable as located.
NFPA 13 does not provide guidance for the overall potential for obstructions
like
it does for all the other types of sprinklers. It simply addresses a few
specific
arrangements. As such, it is basically inadequate. The position of the light
fixture
appears to meet the obstruction requirements but the standard is not specific.
The light fixture is located on opposite sides of the obstruction per Section
8.11.5.1.3.
Although this allowance is generally used to address obstructions tight to the
ceiling,
it ensures an adequate sprinkler discharge reaching the floor. Another
reasonable
approach when the situation does not correlate with the few arrangements in NFPA
13 is to follow the very conservative obstruction criteria for ESFR sprinklers.
Since the ESFR criteria of Section 8.12.5.3.1 is for continuous obstructions,
the 1 ft dimension is the one of interest. In accordance with Section
8.12.5.3.1(3),
1 ft wide obstructions must be at least 1 ft horizontally from the sprinkler.
With
the light located 4 ft from the sprinkler, it does not present a problem.
Suppression
mode sprinklers are the most sensitive to being negatively affected by
obstructions.
Considering this fact and that CMSA criteria is inadequate, applying the ESFR
criteria
provides an appropriate answer, but the AHJ must concur with this approach.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
firesprinkler.org
[http://r20.rs6.net/tn.jsp?f=001C7-wd6haA8AT4sEdCaZDayYwoiwftdwSRVdfB7mNfJejHfQG_NtxkZ3IrIimvM27i9NpX62yyn9GIgKat-1D_20dxOjpJiRi-RHWnCmsCpCZMcCc7j3x6U4L-468hJGHYlzNhziuZbBZvC0cqx7rjvOxDx91TQkzn1tUAy6ZwTY_vWTYwhB2uw==&c=_lgxLvnM08SS1gcTF88vtKQ668DKswXsoe76AnafTYjQJ_OJYOawfg==&ch=DcGtWDCojG_4KMRZ-71zjMUz2M_oz4qMabRr8kDDdZYURdZkPw2oKQ==]
Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
in fire protection engineering. This is provided with the understanding that
the
AFSA assumes no liability for this opinion or actions taken on it and they are
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2014, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
PDF Version
PDF Link
[http://r20.rs6.net/tn.jsp?f=001C7-wd6haA8AT4sEdCaZDayYwoiwftdwSRVdfB7mNfJejHfQG_NtxkQFbBmu8Q419LMhBHCbDWVMbzlPmSdgyUVJXOhgO3a0f2789FSw9EBiEGW11Khe93ENn5e-hOcOYomesUHq-U2v8mKMQYAWauzSf2cFIJLsjP3SvhT9KRiYXMQxBh4Ug9_fibrQZRd5OWWmC2yH-4UmXzrppQGlD_33fUqr-ABg5KVLQDBHN-Bm6C5ZmDrWZtgoqW5CDC8xpv83PcBdxOMM=&c=_lgxLvnM08SS1gcTF88vtKQ668DKswXsoe76AnafTYjQJ_OJYOawfg==&ch=DcGtWDCojG_4KMRZ-71zjMUz2M_oz4qMabRr8kDDdZYURdZkPw2oKQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
New Class Added!
Nov. 10 - 21, 2014
Oct. 13 - 24, 2014
SOLD OUT!
Sept. 8 - 19, 2014
SOLD OUT!
July 14 - 25, 2014
SOLD OUT!
Check our calendar to view upcoming training.
For details and/or to register, visit the AFSA Calendar
[http://r20.rs6.net/tn.jsp?f=001C7-wd6haA8AT4sEdCaZDayYwoiwftdwSRVdfB7mNfJejHfQG_NtxkbcVIW7C7aa7kNCWsRVRA8P_VpKYcGBjeFLBaKEaOe2O8xUfNxf3IE0SYaFmeenlEum6MiKHu5ELN4P1iqNwN9Ks6lyPEfME6j8vB-E8TSGiWCUH2f7LeL3_lmPraJBexcQpD-JbbOPn5r67Ne-UB-_GTs8mTmi43mNonHEtENyK3iAwHpzvRczZosd2Mh80oMx3uhKJI7Nlb5q4-2QHgexchVdL9pC_r2ysGosFK8mElYBv3tDyKMlIRe1O29SSB38yTz3esziTHqc8um3LXoVqQvMk-2sg0Q==&c=_lgxLvnM08SS1gcTF88vtKQ668DKswXsoe76AnafTYjQJ_OJYOawfg==&ch=DcGtWDCojG_4KMRZ-71zjMUz2M_oz4qMabRr8kDDdZYURdZkPw2oKQ==].
e-campus_logo
[http://r20.rs6.net/tn.jsp?f=001C7-wd6haA8AT4sEdCaZDayYwoiwftdwSRVdfB7mNfJejHfQG_Ntxka_0U-o9yqL908kylSJQDmlFLaMvSxKU1alXxbsRWSDbA5GMC8woMXko6w-qw0tJnF60WVFkqCozC4_XffRcSfNcsUrVTYYOwI7cJz08GkuVV7_rjqIzL_TFICP8kUl-Vg==&c=_lgxLvnM08SS1gcTF88vtKQ668DKswXsoe76AnafTYjQJ_OJYOawfg==&ch=DcGtWDCojG_4KMRZ-71zjMUz2M_oz4qMabRr8kDDdZYURdZkPw2oKQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Free Subscription to Sprinkler Age
[http://r20.rs6.net/tn.jsp?f=001C7-wd6haA8AT4sEdCaZDayYwoiwftdwSRVdfB7mNfJejHfQG_NtxkcB7YmoqxKqDZAa0OjDY69EzC6meg8hgAVBaFTAbaURY0C1Mo3O720YgvlohkcL8uQjfAczYbCsIs13qhnOpys6GW3HBfjS1AsGk6-Pr5NoLJp3Ag0mpoinNPH7IHKdWt9N4-54LxU_kbdb03MvJwqc3xWNOVZ1lDrqP-FnxUFKj&c=_lgxLvnM08SS1gcTF88vtKQ668DKswXsoe76AnafTYjQJ_OJYOawfg==&ch=DcGtWDCojG_4KMRZ-71zjMUz2M_oz4qMabRr8kDDdZYURdZkPw2oKQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Quality Contractor
[http://r20.rs6.net/tn.jsp?f=001C7-wd6haA8AT4sEdCaZDayYwoiwftdwSRVdfB7mNfJejHfQG_Ntxkbt1c2lRZUs2Trkra3SW8s5tiQ5Ls7FqYMNb-bl9e_c7WAfeG6r9lUK6YD9-oddThBaH9A8NLo9KP4OCElpi3bqZyUl5daALZkIkYN24P2QVUck31vSHX0Aav8BAIWzgOcWS1fzmWO4FEcyX4MQ7b22m8Z1TyiWi2-jEL_dT1S77&c=_lgxLvnM08SS1gcTF88vtKQ668DKswXsoe76AnafTYjQJ_OJYOawfg==&ch=DcGtWDCojG_4KMRZ-71zjMUz2M_oz4qMabRr8kDDdZYURdZkPw2oKQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Quick Links
Firesprinkler.org
[http://r20.rs6.net/tn.jsp?f=001C7-wd6haA8AT4sEdCaZDayYwoiwftdwSRVdfB7mNfJejHfQG_NtxkZ3IrIimvM27i9NpX62yyn9GIgKat-1D_20dxOjpJiRi-RHWnCmsCpCZMcCc7j3x6U4L-468hJGHYlzNhziuZbBZvC0cqx7rjvOxDx91TQkzn1tUAy6ZwTY_vWTYwhB2uw==&c=_lgxLvnM08SS1gcTF88vtKQ668DKswXsoe76AnafTYjQJ_OJYOawfg==&ch=DcGtWDCojG_4KMRZ-71zjMUz2M_oz4qMabRr8kDDdZYURdZkPw2oKQ==]
AFSA Calendar
[http://r20.rs6.net/tn.jsp?f=001C7-wd6haA8AT4sEdCaZDayYwoiwftdwSRVdfB7mNfJejHfQG_NtxkbcVIW7C7aa7kNCWsRVRA8P_VpKYcGBjeFLBaKEaOe2O8xUfNxf3IE0SYaFmeenlEum6MiKHu5ELN4P1iqNwN9Ks6lyPEfME6j8vB-E8TSGiWCUH2f7LeL3_lmPraJBexcQpD-JbbOPn5r67Ne-UB-_GTs8mTmi43mNonHEtENyK3iAwHpzvRczZosd2Mh80oMx3uhKJI7Nlb5q4-2QHgexchVdL9pC_r2ysGosFK8mElYBv3tDyKMlIRe1O29SSB38yTz3esziTHqc8um3LXoVqQvMk-2sg0Q==&c=_lgxLvnM08SS1gcTF88vtKQ668DKswXsoe76AnafTYjQJ_OJYOawfg==&ch=DcGtWDCojG_4KMRZ-71zjMUz2M_oz4qMabRr8kDDdZYURdZkPw2oKQ==]
Buyer's Guide
[http://r20.rs6.net/tn.jsp?f=001C7-wd6haA8AT4sEdCaZDayYwoiwftdwSRVdfB7mNfJejHfQG_NtxkZ3IrIimvM27n8mQRjL5I2P97zxhmA10pAjW71cHAf-lqniRY4w5g8osjSOD19RBy_fPk4fcihhiuyioRNhoXbRYsFyB7ea-YF7JGNo5A0hYYDCapwiVtp-VZ2UyvfYahawlyyf6S5tmfNjTkDLm33kK47sIvDtpUA==&c=_lgxLvnM08SS1gcTF88vtKQ668DKswXsoe76AnafTYjQJ_OJYOawfg==&ch=DcGtWDCojG_4KMRZ-71zjMUz2M_oz4qMabRr8kDDdZYURdZkPw2oKQ==]
Join AFSA Video
[http://r20.rs6.net/tn.jsp?f=001C7-wd6haA8AT4sEdCaZDayYwoiwftdwSRVdfB7mNfJejHfQG_NtxkZ3IrIimvM279IUsFqJLnFxBrlkzpjJvV7_gxO6TnnDOYcQetDAaW0ApESZ0tzpz6GcrKrTzSNBR0L2l0NIvNqQOPrNFW4ngdr9LUccA8eHE4o-kXYBr7ZYP1PR6s7jWaCXgjfMn4bGtP0_glX5GNQZ_vDtOLl1PzQ==&c=_lgxLvnM08SS1gcTF88vtKQ668DKswXsoe76AnafTYjQJ_OJYOawfg==&ch=DcGtWDCojG_4KMRZ-71zjMUz2M_oz4qMabRr8kDDdZYURdZkPw2oKQ==]
National
[http://r20.rs6.net/tn.jsp?f=001C7-wd6haA8AT4sEdCaZDayYwoiwftdwSRVdfB7mNfJejHfQG_NtxkeLR1eUKbzJ68-MZ6C-Aq-bMVKldVWG2RyYDMkXoAWOFyX19-WJi2L6Yv_BD-GqecSe6RmY5OPCu4osGhXwalDPUs8yKQtlWdJ8zg6N8EET-Yw58O1ZDnoOuxHpI1K1tzQ==&c=_lgxLvnM08SS1gcTF88vtKQ668DKswXsoe76AnafTYjQJ_OJYOawfg==&ch=DcGtWDCojG_4KMRZ-71zjMUz2M_oz4qMabRr8kDDdZYURdZkPw2oKQ==]
Scholarship Contest
[http://r20.rs6.net/tn.jsp?f=001C7-wd6haA8AT4sEdCaZDayYwoiwftdwSRVdfB7mNfJejHfQG_NtxkeLR1eUKbzJ68-MZ6C-Aq-bMVKldVWG2RyYDMkXoAWOFyX19-WJi2L6Yv_BD-GqecSe6RmY5OPCu4osGhXwalDPUs8yKQtlWdJ8zg6N8EET-Yw58O1ZDnoOuxHpI1K1tzQ==&c=_lgxLvnM08SS1gcTF88vtKQ668DKswXsoe76AnafTYjQJ_OJYOawfg==&ch=DcGtWDCojG_4KMRZ-71zjMUz2M_oz4qMabRr8kDDdZYURdZkPw2oKQ==]
OSHA Alliance
[http://r20.rs6.net/tn.jsp?f=001C7-wd6haA8AT4sEdCaZDayYwoiwftdwSRVdfB7mNfJejHfQG_NtxkZ3IrIimvM27cRQ8EvH5UXkedePnYAqhBiesyp0L6gFUDncfQoIsly6je5HleoXielAWlfFj7YZrV9f0u_QIwHY-zFJnc-swDtvS0Q1ZlTuVDwEk3sEn2dmbtCVycP7pefjZ9hG1lDEYTXkZTscx2f4Arp5WiLYbVg==&c=_lgxLvnM08SS1gcTF88vtKQ668DKswXsoe76AnafTYjQJ_OJYOawfg==&ch=DcGtWDCojG_4KMRZ-71zjMUz2M_oz4qMabRr8kDDdZYURdZkPw2oKQ==]
Technical Services
[http://r20.rs6.net/tn.jsp?f=001C7-wd6haA8AT4sEdCaZDayYwoiwftdwSRVdfB7mNfJejHfQG_NtxkVNHdqU_B0RSURMuCwdkzS4D-CLbZ4iYUd61mJykIhfeFm5YRo95V8RW72GYhLw27KbF9IIUruJMc-6B43jGLJxw1CclXD6Lruy1pa0zt6_H_SFUHEEZfsyonPL_WQAU8c8jeRUa2tHW&c=_lgxLvnM08SS1gcTF88vtKQ668DKswXsoe76AnafTYjQJ_OJYOawfg==&ch=DcGtWDCojG_4KMRZ-71zjMUz2M_oz4qMabRr8kDDdZYURdZkPw2oKQ==]
Informal Interpretation Request Form
[http://r20.rs6.net/tn.jsp?f=001C7-wd6haA8AT4sEdCaZDayYwoiwftdwSRVdfB7mNfJejHfQG_NtxkfLvCxfM_uu8grAXGY9Wz1JwQRpMuVsi1vcrZBThj6ywK5wdgmqiPAunJ-g07JWNuAA27FcA05HjKRSQHAAaeF7f7Th4sycI2i80rN4yDbplKNhF7IFhP7Qx-h1iv3TcQl1pSmB_CU5zkew55zw6PPY4-_3zgBC7905nl4gMKDRP&c=_lgxLvnM08SS1gcTF88vtKQ668DKswXsoe76AnafTYjQJ_OJYOawfg==&ch=DcGtWDCojG_4KMRZ-71zjMUz2M_oz4qMabRr8kDDdZYURdZkPw2oKQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Join Our Mailing List
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1118163792144
This email was sent to [email protected] by
[email protected].
Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=f9fff22b-50b3-4b5f-acf2-03dda1c7743d
Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=f9fff22b-50b3-4b5f-acf2-03dda1c7743d
Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp
Online Marketing by
Constant Contact(R)
www.constantcontact.com
American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas |
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org