Looped Dry Systems

"A dry pipe system is looped more than once.  The local AHJ is stating that any 
system with more than one loop is defined as a gridded system and cannot be 
designed
in that manner.  Can a dry pipe system have more than one loop?"

We have reviewed NFPA 13, 2013 edition as the applicable standard.  Our informal
 interpretation is that this layout is considered to be a looped system.
Section 3.4.6 defines "gridded sprinkler system" as a sprinkler system in which 
parallel cross mains are connected by multiple branch lines, causing an 
operating
sprinkler to receive water from both ends of its branch line while other branch 
lines help transfer water between cross mains.  Section 3.4.7 defines a "looped 
sprinkler system" as a sprinkler system in which multiple cross mains are tied 
together
so as to provide more than one path for water to flow to an operating sprinkler 
and branch lines are not tied together.  Some confusion may be created since 
your
layout has more than one loop, creating more than two paths for water to get to 
a sprinkler.  However, if setting a two-path limitation for looped systems were 
the intent, this definition would specify it as such.  The key is that the 
branch
lines are not tied together as per the definitions.  Excessive amounts of air 
can
remain trapped in the system piping when the branch lines are tied together and 
that can significantly delay water from reaching the operating sprinklers.  The 
looped dry pipe systems have to meet the system sizes and initial water 
discharges
per Section 7.2.3.  Based on the information provided the layout is considered a
 looped system and they are permitted to be dry.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Thank You Veterans!
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

NFPA 14 - Comments Close on Nov 14th

The first draft 
[http://r20.rs6.net/tn.jsp?f=001CrBVJcQqUq-ku1gKuhf53d3le1TnfkON9uUgOYELfESZWLZ7A9FoMUjYxjUChYCC7jTHW5W_Ghyukxaq9-__xGUL1CtoF-JwrZcqgjLQxu1wUpkZkd3MTLmbSdhpZYOE8XO8NU8ndFYWYKv03o4dSxiI58OoTtKoFD4PA2thjJ8SZhT5F_Ll31Ed-butwfRn7v5r266M-VNIZIxLZfqx3Q2-TPNxDBsKrpjhQhaJWgkwUYhSFkf3iZQnkrFHvnHvpa3mkjW7UM0=&c=5Z0lKnthFGBCGsMNuxmd5ReLrFxTrISeSfcediQUnaXJbRa1fejFCA==&ch=CGjKLwO8RtWxRVy8N_CioFjIEcOoxLfXWh8H50Cu4_LYo6EGs7BIEg==]
for the next edition of NFPA 14 has been published and available for comment.

The Public Comment closing date for Fall 2015 documents is October 10, 2014 for 
paper submissions and November 14, 2014 for online submissions.

SUBMIT YOUR PUBLIC COMMENTS ELECTRONICALLY!  The Fall 2015 documents are active 
and accepting Public Comments electronically through the Electronic Submission 
(e-PC)
System.  The system will automatically pull in the text and will show changes in
 track changes.  It will even save your Comments.

e-PC System and Instructions.  Submit Public Comments by selecting your document
 from the list at  http://www.nfpa.org/aboutthecodes 
[http://www.nfpa.org/codes-and-standards/document-information-pages],
then Click on the "Next Edition" tab (see screenshot below).  You can submit 
comments
or just start and save your work in progress.  If you would like to review 
instructions
on this process, please go to http://www.nfpa.org/submitcomment 
[http://www.nfpa.org/submitcomment].
 For your information, a list of the Fall 2015 Revision Cycle documents can be 
found
at: 
http://www.nfpa.org/codes-and-standards/document-information-pages?cycle=Fall%202015
[http://r20.rs6.net/tn.jsp?f=001CrBVJcQqUq-ku1gKuhf53d3le1TnfkON9uUgOYELfESZWLZ7A9FoMUjYxjUChYCC89-gABMJpcp8TisfzfamJrRtoVtkMxhWKIltWZivy1pe3_SdADAzVRi2b76m-QkQ8UcshqZ-gQUGBTTD8Bhd9Bk3P0S16MyTMScU-OUH85JNea3eXnY-nYy6IyVv2974yCSWGlCrwr2XQlbRYGtlzethpg53qFenfddbk-448uJKRYJqW6fs7iWhnGjq8QoO7Sbq8QhJ3cM=&c=5Z0lKnthFGBCGsMNuxmd5ReLrFxTrISeSfcediQUnaXJbRa1fejFCA==&ch=CGjKLwO8RtWxRVy8N_CioFjIEcOoxLfXWh8H50Cu4_LYo6EGs7BIEg==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001CrBVJcQqUq-ku1gKuhf53d3le1TnfkON9uUgOYELfESZWLZ7A9FoMfUlMnb444QVowkZ0dUTnkWm0KcJ0sCHP5NpsP-ZKJLUQM6pRNqqF2r2-21N9ga8NVVrft6KP5x0XkCA6JR4VHALq1tWRvHVSzoNfCZNP2uwe2hEHmR0RH8SnPMRABIyMA==&c=5Z0lKnthFGBCGsMNuxmd5ReLrFxTrISeSfcediQUnaXJbRa1fejFCA==&ch=CGjKLwO8RtWxRVy8N_CioFjIEcOoxLfXWh8H50Cu4_LYo6EGs7BIEg==]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2014, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?f=001CrBVJcQqUq-ku1gKuhf53d3le1TnfkON9uUgOYELfESZWLZ7A9FoMXxmn5SmP-lwbYQqlkQka_FSyfo4SjTh_1c131pDyGXRYWwt8tVL8VaCdtrCfnhoyg6ebe7EXmH1u04wYZPMAPWp5_m-FHv81kMHsgi8i9yOIbrDrd6HRckGSa3MIolnm0jjsJ9tIHxOpjr_cTgbFD88JLyg3OU613LG9DY8bCBuosftJ7zZt6XP-BGXwv5pARldrraLJ_M0NUt_P39S1-Y=&c=5Z0lKnthFGBCGsMNuxmd5ReLrFxTrISeSfcediQUnaXJbRa1fejFCA==&ch=CGjKLwO8RtWxRVy8N_CioFjIEcOoxLfXWh8H50Cu4_LYo6EGs7BIEg==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

AFSA Webinar
Advanced Technologies in Clean Agent Systems
November 19
11:00 am - 12:30 pm CDT
1.5 CPD and 0.15 CEU for a $15.00 fee
Register Button 
[http://r20.rs6.net/tn.jsp?f=001CrBVJcQqUq-ku1gKuhf53d3le1TnfkON9uUgOYELfESZWLZ7A9FoMVBEVlDMikGtSrSASJS30zSQ0MammHmhfEfW5Lf4Q1LcmECZtm1anqzhz6Ww2trp25MlyYSd_wRzlWAasyt5I80NTltF8PK8qSc1j9wGTUrgVUp7375Zs418s-1uOXyMuImoqB3P9jWhEQV-cp-rNINfKK34tb80Uc5DhRnOIM7Q&c=5Z0lKnthFGBCGsMNuxmd5ReLrFxTrISeSfcediQUnaXJbRa1fejFCA==&ch=CGjKLwO8RtWxRVy8N_CioFjIEcOoxLfXWh8H50Cu4_LYo6EGs7BIEg==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
More Information [http://www.firesprinkler.org/education-center/schools/]
January 19 - 30, 2015
March 16 - 27, 2015

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://www.firesprinkler.org/events/].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?f=001CrBVJcQqUq-ku1gKuhf53d3le1TnfkON9uUgOYELfESZWLZ7A9FoMVXfvpRo1wb9KQ9IHsk-k76ZjNvuJcbv7coTZfKo7iRklMyLNfSuXENn4h954GD9-dyYC8Rqw7Ip6GWE3Log7b5PFsLmWU2iK_b70uhM6eqMH_IaPcrVyCP3o16jWmq74w==&c=5Z0lKnthFGBCGsMNuxmd5ReLrFxTrISeSfcediQUnaXJbRa1fejFCA==&ch=CGjKLwO8RtWxRVy8N_CioFjIEcOoxLfXWh8H50Cu4_LYo6EGs7BIEg==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://www.firesprinkler.org/sprinklerage/subscribe/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org [http://www.firesprinkler.org]
Join AFSA [http://www.firesprinkler.org/membership/purchase-membership/]
National  
[http://r20.rs6.net/tn.jsp?f=001CrBVJcQqUq-ku1gKuhf53d3le1TnfkON9uUgOYELfESZWLZ7A9FoMSZvn6fMGBbWyXibp-RHzZQ3sYVTQdqFcRaBLq4b5qea5NWmjfv0yJWFmoxWBb-a0vKLx6HK_X5A8s_NHSblddpiesCU-7b9rEZY34B7oIbv_RFjgY8G5brBoArxkVv1ng==&c=5Z0lKnthFGBCGsMNuxmd5ReLrFxTrISeSfcediQUnaXJbRa1fejFCA==&ch=CGjKLwO8RtWxRVy8N_CioFjIEcOoxLfXWh8H50Cu4_LYo6EGs7BIEg==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?f=001CrBVJcQqUq-ku1gKuhf53d3le1TnfkON9uUgOYELfESZWLZ7A9FoMSZvn6fMGBbWyXibp-RHzZQ3sYVTQdqFcRaBLq4b5qea5NWmjfv0yJWFmoxWBb-a0vKLx6HK_X5A8s_NHSblddpiesCU-7b9rEZY34B7oIbv_RFjgY8G5brBoArxkVv1ng==&c=5Z0lKnthFGBCGsMNuxmd5ReLrFxTrISeSfcediQUnaXJbRa1fejFCA==&ch=CGjKLwO8RtWxRVy8N_CioFjIEcOoxLfXWh8H50Cu4_LYo6EGs7BIEg==]
Safety Training 
[http://r20.rs6.net/tn.jsp?f=001CrBVJcQqUq-ku1gKuhf53d3le1TnfkON9uUgOYELfESZWLZ7A9FoMVBEVlDMikGt151PaYPgamnXbcumWUVJwWFPquh3KoDTaMn06kDmiqq8c9Cx6j5LdiMBgixw1sIdOzxOsc-1fBEsHcYkQCoENMZ0Hd_DXmAKNISI19Ri4RgGXMOdidoEK_-8W89rWQvl9y7yYcJ-b6a-QW48bIUiL_UwnfQS6V9cWZRvWGN72HQ=&c=5Z0lKnthFGBCGsMNuxmd5ReLrFxTrISeSfcediQUnaXJbRa1fejFCA==&ch=CGjKLwO8RtWxRVy8N_CioFjIEcOoxLfXWh8H50Cu4_LYo6EGs7BIEg==]
Technical Services 
[http://r20.rs6.net/tn.jsp?f=001CrBVJcQqUq-ku1gKuhf53d3le1TnfkON9uUgOYELfESZWLZ7A9FoMYJpkTu1irC4pjS1GRY_2RUlZeuk9R_7kpMfGUJvclSGSpTNGOrffOUuUwN7r2oh5QX9qVyhFFchKxD9qQXHeYJVgnV42CUqLhDRadS3ZYyGnLO43prD5Et_XWd2tJqOTI8psYgL4fJ3l3XZmI9ZfaWJHcjuceFgPA==&c=5Z0lKnthFGBCGsMNuxmd5ReLrFxTrISeSfcediQUnaXJbRa1fejFCA==&ch=CGjKLwO8RtWxRVy8N_CioFjIEcOoxLfXWh8H50Cu4_LYo6EGs7BIEg==]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?f=001CrBVJcQqUq-ku1gKuhf53d3le1TnfkON9uUgOYELfESZWLZ7A9FoMYJpkTu1irC4VDiBekIxubcNqGMCT5GV5vCCc5vE2tuPVQx4Kf7Km7fLA9gOtl_u_mnFhmhloHdAoivfOfltftHFUrr3WhWSG2VwJtA3tcDFHs-0uSzk4Vm6r4S1MczGkahnViYPGv3y8ayS-VaOZEBbUtQTo4eyoUQOqEe-FcZyzy5pcly5295Jd0sKfwUhng==&c=5Z0lKnthFGBCGsMNuxmd5ReLrFxTrISeSfcediQUnaXJbRa1fejFCA==&ch=CGjKLwO8RtWxRVy8N_CioFjIEcOoxLfXWh8H50Cu4_LYo6EGs7BIEg==]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1119107174234

This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=ef47e668-375e-44f6-b57a-7a12c49c7157


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=ef47e668-375e-44f6-b57a-7a12c49c7157


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp

Online Marketing by
Constant Contact(R)
www.constantcontact.com



American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to