A weekly newsletter dealing with codes and other technical issues

January 5, 2015
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Concrete Tee Construction With ESFR Sprinklers

"A building owner wants to put an ESFR system in a warehouse that has concrete 
tee
concrete construction with stems at 5 ft on center and 20 inches deep.  NFPA 13 
allows ESFR sprinklers to be installed in obstructed noncombustible construction
 and installed in every channel.  This puts my sprinklers 5 ft apart, under the 
8 ft minimum.  FM standards seem to imply I can do it per FM but it is not 
clear.
 Is it allowed to install ESFR sprinklers in this type of construction?"

We have reviewed NFPA 13, 2013 edition as the applicable standard.  Our informal
 interpretation is that ESFR sprinklers may not be used for this application per
 NFPA 13 but may be allowed per FM Data Sheet 2-0.

Section 8.4.6.3.1 says that where depths of the solid structural members (beams,
 stem, and so forth) exceed 12 in., ESFR sprinklers shall be installed in each 
channel
formed by the solid structural members.  Section 8.12.4.1.6 also indicates that 
with obstructed construction, the branch lines shall be permitted to be 
installed
across the beams, but sprinklers shall be located in the bays and not under the 
beams.  This section gives guidance to locate the sprinklers within bays and not
 under the stems of the concrete tee construction.  Some manufacturers of ESFR 
sprinklers
address construction types and others do not.  For example, data sheets for 
Tyco's
ESFR sprinklers references roof construction as unobstructed or obstructed 
construction
and gives examples as smooth ceiling, bar joists, beam and girder, and so forth.
  Where the depths of the solid structural members (e.g., beams and stem) exceed
 12 inches, install ESFR sprinklers in each channel formed by the structural 
members.
 Since your channels are 20 in. deep, sprinklers are required in each channel.  
When the installation of ESFR's are located in each channel, Section 8.4.6.3.2 
reminds
us that we still must comply with the spacing and area of coverage defined by 
8.12.2
and 8.12.3.  Section 8.12.3.4 explicitly states that the minimum spacing between
 sprinklers must be 8 ft.  There is no allowance for a baffle between closely 
spaced
ESFR sprinklers as allowed for spray sprinklers.

Regarding FM Data Sheet 2-0 dated April 2011, Section 2.2.3.2 gives an exception
 to the sprinkler spacing of Table 17.  The exception states, "When sprinklers 
are
provided in every channel bay formed by obstructed construction, the minimum 
linear
and area spacing recommendations listed in Table 17 do not apply to the 
sprinklers
located in adjacent channel bays. See Figure 26 for a diagram of this 
arrangement."
 Figure 26 shows the spacing of sprinklers when installed in every bay channel 
formed
by solid structural members.  The sprinkler spacing in the bays should not 
exceed
the distances in Table 17.  When an alternative standard to NFPA 13 is used, the
 situation should be discussed with the local AHJ.  Other alternatives to meet 
NFPA
13 is to install insulation in each channel such that the distance from the 
insulation
to the bottom of the concrete tees is less than 12 inches or a suspended ceiling
 to eliminate the obstructed construction. Otherwise, you must use another 
sprinkler
type that will permit the use of concrete tee construction with stems greater 
than
12 inches.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001KhF0S-E2_z_e2_jW10IAlbkc87RyBg0QlkLsZE4EtYMwASIEp5m5CTWk4UvHmZr_4VSzJpTWP1LdeGoMM6WdOE8CCiIsbrSSsncUJ5kzchRTwSlMyWI0-0Eh4MCIISXnffyl4SF9VCKNjRsASNXebkB6iEszHWDrI4porLfQp8w1_4fdblA8Nw==&c=sRwidlkiM2Kt-z33w5pB6pWgT3YqaS9HW65ODzWW2HLDUX0lRCsW_g==&ch=48LgBPT-d_YYi3FQ3HC7oHXXOO6rxLDAaCPh0u38YAk1T2_4ssIV7w==]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2015, American Fire Sprinkler Association. All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org [http://www.firesprinkler.org]    Join AFSA 
[http://www.firesprinkler.org/membership/purchase-membership/]
   National 
[http://r20.rs6.net/tn.jsp?f=001KhF0S-E2_z_e2_jW10IAlbkc87RyBg0QlkLsZE4EtYMwASIEp5m5CdLUnd5CNMPtc86rPBOOYv9a5f4xYYJtLcAMTJRF_z6HaTk50ViGwxx5NHXWWBfPafScS9DrrakRyXqaZ3FZPZdJUadhL1Cux8jfnYjlUozPWDcB9Lhbq0URkJen_cdqrw==&c=sRwidlkiM2Kt-z33w5pB6pWgT3YqaS9HW65ODzWW2HLDUX0lRCsW_g==&ch=48LgBPT-d_YYi3FQ3HC7oHXXOO6rxLDAaCPh0u38YAk1T2_4ssIV7w==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?f=001KhF0S-E2_z_e2_jW10IAlbkc87RyBg0QlkLsZE4EtYMwASIEp5m5CdLUnd5CNMPtc86rPBOOYv9a5f4xYYJtLcAMTJRF_z6HaTk50ViGwxx5NHXWWBfPafScS9DrrakRyXqaZ3FZPZdJUadhL1Cux8jfnYjlUozPWDcB9Lhbq0URkJen_cdqrw==&c=sRwidlkiM2Kt-z33w5pB6pWgT3YqaS9HW65ODzWW2HLDUX0lRCsW_g==&ch=48LgBPT-d_YYi3FQ3HC7oHXXOO6rxLDAaCPh0u38YAk1T2_4ssIV7w==]
Safety Training 
[http://r20.rs6.net/tn.jsp?f=001KhF0S-E2_z_e2_jW10IAlbkc87RyBg0QlkLsZE4EtYMwASIEp5m5CRMXyCj7lFDyaN8uqFrUef_EFUUMXerRQ2NI3CKoHuIIaKhWj-SqXKkvX52jgsjJz8KATTkCaDgwSWJ7IIc1hredDnb4Eo0ncRxk05VPq-K94DWXfHSzPRd_bQ1N_4NK1C2BV61Fucq0xPapaVLyDHmUycvojBvQcDejpaZgk4h-4Upx8oPHXfQ=&c=sRwidlkiM2Kt-z33w5pB6pWgT3YqaS9HW65ODzWW2HLDUX0lRCsW_g==&ch=48LgBPT-d_YYi3FQ3HC7oHXXOO6rxLDAaCPh0u38YAk1T2_4ssIV7w==]
    Technical Services 
[http://r20.rs6.net/tn.jsp?f=001KhF0S-E2_z_e2_jW10IAlbkc87RyBg0QlkLsZE4EtYMwASIEp5m5CYG2A1fmhG35FdNg5XXwTun3A5-9hoHSKdkfUrIgm6Qqa5YLQ5hFryaV45s2FphHQvn_bc6uWbTRh5EZ5UGv7sTWj4Br1aqXKehcFOVPWbZYKCzEOX_rZF7HEJJVYP4gqB7Wi7YERZZLFjBR1qy29SJEtpJ-z00z7g==&c=sRwidlkiM2Kt-z33w5pB6pWgT3YqaS9HW65ODzWW2HLDUX0lRCsW_g==&ch=48LgBPT-d_YYi3FQ3HC7oHXXOO6rxLDAaCPh0u38YAk1T2_4ssIV7w==]
    Informal Interpretation Request 
[http://r20.rs6.net/tn.jsp?f=001KhF0S-E2_z_e2_jW10IAlbkc87RyBg0QlkLsZE4EtYMwASIEp5m5CYG2A1fmhG35BXN5bg-2N4QWeRVLeSXko64LsI3qCrH93Sb3y6QS-9MMS-b6johD2wHeu4NqITKGP9FBKalo5xOEkvUziaSPbHFQBmSn2427FaJThd4ASue73TJWvubmEr1S2oTWs-UhqUomJCpTDbeSgQoPjlq0dVFP2TegbLjS5xoc6CcquExLTPo5rfDKdg==&c=sRwidlkiM2Kt-z33w5pB6pWgT3YqaS9HW65ODzWW2HLDUX0lRCsW_g==&ch=48LgBPT-d_YYi3FQ3HC7oHXXOO6rxLDAaCPh0u38YAk1T2_4ssIV7w==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?f=001KhF0S-E2_z_e2_jW10IAlbkc87RyBg0QlkLsZE4EtYMwASIEp5m5CRoxo6s-XjTsUCpPylaxy9O_Z-3D2q4jvT-PpXTbgVD1KVytAsZhVYR0rCMe2yHVtaJjKQA9VLS4rwK_BPQ5Ftm-_o3HLOStMM2qjWigoNOUCAaAptOobp5Q-d8HeLaxPE2rhMNbNwo_U5d4jPq4D26UH-irFIi1oAr0FcPuUZ3Y62U2IhzOKaaYXd83cvV_MquAIMRCCyrXXVTRAAejGZU=&c=sRwidlkiM2Kt-z33w5pB6pWgT3YqaS9HW65ODzWW2HLDUX0lRCsW_g==&ch=48LgBPT-d_YYi3FQ3HC7oHXXOO6rxLDAaCPh0u38YAk1T2_4ssIV7w==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
More Information [http://www.firesprinkler.org/education-center/schools/]
January 19 - 30, 2015
(Sold Out!)
March 16 - 27, 2015

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://www.firesprinkler.org/events/].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?f=001KhF0S-E2_z_e2_jW10IAlbkc87RyBg0QlkLsZE4EtYMwASIEp5m5CfMcZ1VifuDIL7kEMI4Qii1PVT07g_MM-ps39igibgF7cvnncEwBFNsaEK3Vwb2L9Eu7eVFuWrQJhIqayWS_v-CP2-45UtBRLnwSKTW34BNmmaTJrs0z2M5VBdJLzLJujA==&c=sRwidlkiM2Kt-z33w5pB6pWgT3YqaS9HW65ODzWW2HLDUX0lRCsW_g==&ch=48LgBPT-d_YYi3FQ3HC7oHXXOO6rxLDAaCPh0u38YAk1T2_4ssIV7w==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Webinar
Sprinkler Pipe Corrosion: Mitigating It With a Nitrogen System

January 28

11:00a - 12:30p (CST)
This webinar offers 1.5 CPD and 0.15 CEU for a $15.00 fee.
AFSA MEMBER BENEFIT
This webinar is free to all AFSA member companies and their employees!

Register Button 
[http://r20.rs6.net/tn.jsp?f=001KhF0S-E2_z_e2_jW10IAlbkc87RyBg0QlkLsZE4EtYMwASIEp5m5CY655fkIhuWL129tkYkzDfM_ehV8eGjpCJ6EJVJW7QFANUPmnrjC-2VHanSaJi2e89RNws4HIlsB4WXYU2biUVePUQTgFyfH3AGM_AYQSvQoFKweUtq3IlGiq3ERZ9f3FkGdKsq-bIlIumzkFvgq6KxwB8LEae7ayA==&c=sRwidlkiM2Kt-z33w5pB6pWgT3YqaS9HW65ODzWW2HLDUX0lRCsW_g==&ch=48LgBPT-d_YYi3FQ3HC7oHXXOO6rxLDAaCPh0u38YAk1T2_4ssIV7w==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://www.firesprinkler.org/sprinklerage/subscribe/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1119650508485

This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=09efce53-29b2-4320-816f-5b7c1e03d187


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=09efce53-29b2-4320-816f-5b7c1e03d187


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp

Online Marketing by
Constant Contact(R)
www.constantcontact.com



American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to