A weekly newsletter dealing with codes and other technical issues

April 6, 2015
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

NFPA 13D Design Discharge

"The newly revised Section 10.2 in the 2013 edition of NFPA 13D removed the 
previously
required 13 gpm minimum for two sprinklers not listed with specific discharge 
criteria,
as well as 18 gpm for a single sprinkler calculation.  The handbook explains the
 new requirements are now based exclusively on deferring to the criteria in the 
listed sprinklers and allows for the design in Section 10.2 to include up to a 
maximum
of two sprinklers.  Can a single sprinkler be used as the basis for the design, 
assuming the largest room can be protected by a single sprinkler?  It is also 
assumed
that the room has beams and slopes meeting the criteria in Section 10.2 of the 
2013
edition.  Previously, a minimum 18 gpm would be required to take this approach, 
but no guidance is apparent in the new standard for a single sprinkler 
approach."

We have reviewed NFPA 13D, 2013 edition as the applicable standard as well as 
the
2010 edition.  Our informal interpretation is that a single sprinkler design is 
permitted for compartments requiring only one sprinkler at the pressure and flow
 indicated by the listing.

The reference for sprinkler discharge of 13 gpm per sprinkler for all design 
sprinklers
and 18 gpm for a single flowing sprinkler were deleted.  The criteria were for 
sprinklers
that were not listed with specific discharge criteria.  The flows were based on 
early fire testing before listed sprinklers with specified flows and pressures 
were
widely available.  All residential sprinklers currently have the flows and 
pressures
specified in their listings.  The reference to the old discharge criteria in 
8.1.1.1.1
and 8.1.1.1.2 of the 2010 edition were no longer necessary and deleted from the 
2013 edition.  Section 10.2.1 of the 2013 edition was expanded for beamed and 
sloped
ceilings.  This section indicates that for each of the five following 
situations,
the number of sprinklers in the design area shall be all of the sprinklers 
within
a compartment, up to a maximum of two sprinklers that require the greatest 
hydraulic
demand.  A single sprinkler design is appropriate if the compartment size is 
small
enough to be protected by a single sprinkler.  If the applications exceed that 
of
Section 10.2.1, Sections 10.2.2, 10.2.3, and 10.2.4 are other options available.
  If written guidance is not available per the listing for that particular 
application,
then determination of the design area is to be discussed with the AHJ.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

NFPA 25 Open for Public Comments

The first draft report for the next edition of NFPA 25, Standard for the 
Inspection,
Testing, and Maintenance of Water-Based Fire Protection Systems, is open for 
public
comments.

Public Comment Closing Date for Online Submission: 5/15/2015

Public Comment Closing Date for Paper Submittal: 4/10/2015

http://www.nfpa.org/25 [http://www.nfpa.org/25]

2017 edition:

Posted under Next Edition tab:
First Draft Report - open for public comment 
[http://r20.rs6.net/tn.jsp?f=001iXL8cArRSRP39E2O5isVeCWIWPlZmcLeKBLsTgaGL-l53SnUp_OmgQwM2bYjJbev1UJSbO3ibCYTTMqk6vcVpro6zvSH-rRe85MONVGhPpkanbvgVjAl7KYwICNZ8tIluk2xY_kjGUl9tOk1RLN1b_Z41qsWKIun2hp13vWJsypJ4zg4kpJWiiqK8EwC8G2_Xqm-aKfR-MWJr9d8XmbJkE2L7LDEmJPa3nQiYDR1wURP9N8UpPGBsla4lPUMpLDXmn9pwVzTsxa7zRFFW7b3XekLOvLPCVQO&c=BigfAEOYmCmlQMphL6TKhDn6AybJ7bQv3NbaV-ocFEMj-_Lu58PVRg==&ch=x_T1waooU6t_n90kByU-g7tyaNUT55oVKZjySVElQJzRN4qjDcBJtg==]
First Draft Ballot Final 
[http://r20.rs6.net/tn.jsp?f=001iXL8cArRSRP39E2O5isVeCWIWPlZmcLeKBLsTgaGL-l53SnUp_OmgdSSIxtxGTu-SLeCWv59wYChRTfDZcLIf16HjAwdxJ5kOGhlqGi0th-ZR0J6RWxI0lnWHpDqENipEXecRx41J-1YEPEvJaf4jbsPa95KqK5DntsZ2yAhfbDhSKIFNgqicpdKsB_8fCaen7-2A8cD49y4oCX3quOFiceMFv6xoYJqz_y3PDavKAcLvG3EOXJeaoSsU5oosWGv7mtmaIFvb2I=&c=BigfAEOYmCmlQMphL6TKhDn6AybJ7bQv3NbaV-ocFEMj-_Lu58PVRg==&ch=x_T1waooU6t_n90kByU-g7tyaNUT55oVKZjySVElQJzRN4qjDcBJtg==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001iXL8cArRSRP39E2O5isVeCWIWPlZmcLeKBLsTgaGL-l53SnUp_OmgWrsvzs7qgRtSLewEiHPIvt-r8Eydw3LwEMc27oIZyUnrvnUU_euKzGbsUSHO-Fz-HvWzAJWhpzrWC4wQTxJdUI6fGEi7RQXv7OgALJEHrDNjcLlko2UQOZ9BidAiZiItw==&c=BigfAEOYmCmlQMphL6TKhDn6AybJ7bQv3NbaV-ocFEMj-_Lu58PVRg==&ch=x_T1waooU6t_n90kByU-g7tyaNUT55oVKZjySVElQJzRN4qjDcBJtg==]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2015, American Fire Sprinkler Association. All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org [http://www.firesprinkler.org]    Join AFSA 
[http://www.firesprinkler.org/membership/purchase-membership/]
   National 
[http://r20.rs6.net/tn.jsp?f=001iXL8cArRSRP39E2O5isVeCWIWPlZmcLeKBLsTgaGL-l53SnUp_OmgeMOHrky-ucPZpj-5P-mY6VFyuTy6IK4JbtXIGO0Fjoe98zRevcpB_c6TrhWhXTnYG5EKuUZfVGXFYIi-ACHs71rD1m5gqWfhQiohPgOO4a7uPswF0Un7wLEdM4eL1ViiQ==&c=BigfAEOYmCmlQMphL6TKhDn6AybJ7bQv3NbaV-ocFEMj-_Lu58PVRg==&ch=x_T1waooU6t_n90kByU-g7tyaNUT55oVKZjySVElQJzRN4qjDcBJtg==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?f=001iXL8cArRSRP39E2O5isVeCWIWPlZmcLeKBLsTgaGL-l53SnUp_OmgeMOHrky-ucPZpj-5P-mY6VFyuTy6IK4JbtXIGO0Fjoe98zRevcpB_c6TrhWhXTnYG5EKuUZfVGXFYIi-ACHs71rD1m5gqWfhQiohPgOO4a7uPswF0Un7wLEdM4eL1ViiQ==&c=BigfAEOYmCmlQMphL6TKhDn6AybJ7bQv3NbaV-ocFEMj-_Lu58PVRg==&ch=x_T1waooU6t_n90kByU-g7tyaNUT55oVKZjySVElQJzRN4qjDcBJtg==]
Safety Training 
[http://r20.rs6.net/tn.jsp?f=001iXL8cArRSRP39E2O5isVeCWIWPlZmcLeKBLsTgaGL-l53SnUp_OmgXMuUyJpXbx3ShvmiO_oulUT9ns3rYpMhURjeqEG2his4WQa_Kjy1X1xkPEC6yRORDDtrNoJEyQEqt1Ent4JmKkpYb7qnbul9tl-hUvg5IC4qWhcuH1jX9sr0iS2OFLnHgpG5XP6QQVVGUCs9ZySqCps0Z38LT7uYtq_b2gNnEKOfjvO2mUxlPQ=&c=BigfAEOYmCmlQMphL6TKhDn6AybJ7bQv3NbaV-ocFEMj-_Lu58PVRg==&ch=x_T1waooU6t_n90kByU-g7tyaNUT55oVKZjySVElQJzRN4qjDcBJtg==]
    Technical Services 
[http://r20.rs6.net/tn.jsp?f=001iXL8cArRSRP39E2O5isVeCWIWPlZmcLeKBLsTgaGL-l53SnUp_OmgeOWXENeIkOMVOcwtj6T8jft6J83kQic3iJB7XF6yimLVv21jO_XwHyi98nAKn6L-6XecGpKdtGkFblLAK6ZyrKAZI53JNdacsbelyg3Bo4C2c0LlTpq7RUezAJOSk5n1oMmJYypDe-IfAqinLCdPMhOZq_lIpPACw==&c=BigfAEOYmCmlQMphL6TKhDn6AybJ7bQv3NbaV-ocFEMj-_Lu58PVRg==&ch=x_T1waooU6t_n90kByU-g7tyaNUT55oVKZjySVElQJzRN4qjDcBJtg==]
    Informal Interpretation Request 
[http://r20.rs6.net/tn.jsp?f=001iXL8cArRSRP39E2O5isVeCWIWPlZmcLeKBLsTgaGL-l53SnUp_OmgeOWXENeIkOM1RSgqRFLdS1skv2u66HdsrbCllj7XuoKUYKmoxJzVMXykp2sC6jyh3UJZupaTfPFDUoP97uaO4Fn6IaPhf_h9YSdgEv_GBF_IQ_86HY5zgKRGWSghD9oglGmxJZf0zEE69QWSq5YHKrL_PCOHUVgPTcNJezgkbd61cN5pRS0L-icpjqc_9WZaQ==&c=BigfAEOYmCmlQMphL6TKhDn6AybJ7bQv3NbaV-ocFEMj-_Lu58PVRg==&ch=x_T1waooU6t_n90kByU-g7tyaNUT55oVKZjySVElQJzRN4qjDcBJtg==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?f=001iXL8cArRSRP39E2O5isVeCWIWPlZmcLeKBLsTgaGL-l53SnUp_OmgSeJWfpX5bMLFlKmCDh39vxxFcPL4uheyvIrEGQ94YwBHdiv_8IZMKd3bicsG4sWm1qp68cTztLIG1U6yXczo2s7toIMng00KPN43lZXXVOCxz_UvUVh8TJPDiKexncXnhlQ7bNOlzrZ6klnWMQtBfoZXOuI4L5rVyY2H0aw2p5d85-ZWPto4sbYQxYj_EiYdw==&c=BigfAEOYmCmlQMphL6TKhDn6AybJ7bQv3NbaV-ocFEMj-_Lu58PVRg==&ch=x_T1waooU6t_n90kByU-g7tyaNUT55oVKZjySVElQJzRN4qjDcBJtg==]
Archives 
[http://r20.rs6.net/tn.jsp?f=001iXL8cArRSRP39E2O5isVeCWIWPlZmcLeKBLsTgaGL-l53SnUp_OmgfvK2Jp2MpKoy05aqUiQGsjaMMcjMZ-tLI0RTVe7t0BGvxpjAlGTg7-oSyj9GJVA5rfj29w1PILOEdR5zyS_pBoDgHI8FN7_8_siGleZvtEqkfFe8PnBreS9pbPzunmyJ9tO81A-LiK_9bwB0I6Ot-RwOxYQb7l98bfW_eJB_IdUV3pUyDf9DCNawALRXytDVA==&c=BigfAEOYmCmlQMphL6TKhDn6AybJ7bQv3NbaV-ocFEMj-_Lu58PVRg==&ch=x_T1waooU6t_n90kByU-g7tyaNUT55oVKZjySVElQJzRN4qjDcBJtg==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
More Information 
[http://r20.rs6.net/tn.jsp?f=001iXL8cArRSRP39E2O5isVeCWIWPlZmcLeKBLsTgaGL-l53SnUp_OmgfvK2Jp2MpKoVsucLxXEEPhJ7Q0wmRpyhOeBjDhoD5Vcxc_nkEa-74grFIlOHORPPLMM6UB8oLRg-gloP2CgGaUrF05QVXbrLtmffyIjGYyMjlMgR1bKxSs5GO9imbSu0ECrkQYrm2Io&c=BigfAEOYmCmlQMphL6TKhDn6AybJ7bQv3NbaV-ocFEMj-_Lu58PVRg==&ch=x_T1waooU6t_n90kByU-g7tyaNUT55oVKZjySVElQJzRN4qjDcBJtg==]
July 20 - 31, 2015
September 14 - 25
May 11 - 22, 2015
Sold Out!

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://www.firesprinkler.org/events/].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?f=001iXL8cArRSRP39E2O5isVeCWIWPlZmcLeKBLsTgaGL-l53SnUp_OmgfVPwEBb9qBzXHQmtIC-QuNu9zpOQtB6RHreNVmoZInnz23T5JIeuEo9PgY_VCYEBbdonAB-oW7q2yOwtrMFFvljL_R9iUAHzgGRcYHVR99AO5luT8uEI72D9cdEzl5uOA==&c=BigfAEOYmCmlQMphL6TKhDn6AybJ7bQv3NbaV-ocFEMj-_Lu58PVRg==&ch=x_T1waooU6t_n90kByU-g7tyaNUT55oVKZjySVElQJzRN4qjDcBJtg==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://www.firesprinkler.org/sprinklerage/subscribe/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1120613864463

This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=f9275f82-dbe7-40a0-bf19-2a7225b49935


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=f9275f82-dbe7-40a0-bf19-2a7225b49935


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp

Online Marketing by
Constant Contact(R)
www.constantcontact.com



American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to