August 24, 2015
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Flange Spigot and C-900 (PVC) Pipe
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

"Figure A.10.6.3.1 depicts an underground fire service, spigot piece and system 
riser entering a building.  Is it acceptable for the spigot piece to be C-900 
pipe
in accordance with AWWA C900 in lieu of ductile iron pipe?"  In response to your
 question we have reviewed NFPA 13, 2013 edition as the applicable standard.  
Our
informal interpretation is that Section 6.3.1.1.1 will allow an underground pipe
 to enter under the building, rise up and extend 24 inches above the finished 
floor.
The committee discussed the issue of allowing PVC pipe to be utilized in a 
spigot
piece and extend 24 inches above the finished floor when Section 6.3.1.1.1 was 
added
to NFPA 13.  The chairman was specifically asked if PVC pipe would be allowed in
 this scenario.  As it was discussed around the committee, the consensus was 
that
Section 6.3.1.1.1 did not restrict the material and that PVC pipe could be 
utilized.
 The allowance of Section 6.3.1.1.1 will also appear in the 2016 edition of NFPA
 13 as Section 10.1.4.1.
A Public Comment No. 219 was made on the 2016 edition of NFPA 13.  This comment 
would have added a Section 10.1.4.2 that would've added a requirement to protect
 the plastic pipe from direct rays of the sunlight, incompatible materials, or 
the
weight of the sprinkler riser on the plastic pipe.  The committee rejected 
Public
Comment No. 219.  You will have to be aware, however, that Section 24.1.6.1.2 
will
require that the transition (spigot) piece be protected against possible damage 
from corrosive agents, solvent attacks or mechanical damage.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2015, American Fire Sprinkler Association. All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001h-raFFtboGY5DdkcAcDhVw5MJIRZPidVNeg4UUpxmeMC9VAaVbuq8lCM1_5Ib3_2cxQmMbfUzo06R8GFt-I5by3XQscUgu7nFsI8nyxAxAZo-51ssSrw_41-lgxxKhrrpPwZP7JS7w8UpkcfJEVc2n97pxviM7G96ayFHHlbvNnBkiLgtRyBww==&c=e7lcE_9ojvgSUCZid2wUMGyCl1MBItE7Lo_xQPlzgR8CYr2Lkq_iAw==&ch=X977FcAh2HJFF5esd6RrK6d2We-7X3Xvg3tBsqpK8khnnq0fXeXNMw==]
  Join AFSA 
[http://r20.rs6.net/tn.jsp?f=001h-raFFtboGY5DdkcAcDhVw5MJIRZPidVNeg4UUpxmeMC9VAaVbuq8lCM1_5Ib3_2QAV-Mrlt067TcDd6EK8_RjwXIVjED_rL6NrO968BJv4y1UHUS5zeSyEzJpt8stn_lldCK_ejl7tXz4JLGUtnC95TjgfZNVhIvso5IFNBwKe_VXzBCBP6bWnZXBQKRKRqqUhrABIXI-kiMo85LS3IOHAh25-i7Ykh&c=e7lcE_9ojvgSUCZid2wUMGyCl1MBItE7Lo_xQPlzgR8CYr2Lkq_iAw==&ch=X977FcAh2HJFF5esd6RrK6d2We-7X3Xvg3tBsqpK8khnnq0fXeXNMw==]
  Scholarships 
[http://r20.rs6.net/tn.jsp?f=001h-raFFtboGY5DdkcAcDhVw5MJIRZPidVNeg4UUpxmeMC9VAaVbuq8lCM1_5Ib3_2Bsq-0KbTXIb2HiJH1bTrK1EGXCLTUIfijit0BmEwkDmkjf8RWJ1DqXoCGWrFZOhk8LHCNmTuPgDCRIhC_eNnbyaqECU4q9U8o1tYopCsGCu9JDVgfylLSQ==&c=e7lcE_9ojvgSUCZid2wUMGyCl1MBItE7Lo_xQPlzgR8CYr2Lkq_iAw==&ch=X977FcAh2HJFF5esd6RrK6d2We-7X3Xvg3tBsqpK8khnnq0fXeXNMw==]
Safety Training 
[http://r20.rs6.net/tn.jsp?f=001h-raFFtboGY5DdkcAcDhVw5MJIRZPidVNeg4UUpxmeMC9VAaVbuq8lCM1_5Ib3_2oq0eHGlIqXXlzYxzLOu6eKoLpGfuhfPjt9aqDLORl62xdpMk0GHPiY6YqSWp9ZFMOpQtKDAZWZaRtoYVzLSeOx6BMtbpKB0AaL9pwWu93R-gr0FgE_WFAHHhivFUVlWJb15-HRGtzyaAfak0XUkq3P82Gv0j0BkOsWoQoGSUYd4=&c=e7lcE_9ojvgSUCZid2wUMGyCl1MBItE7Lo_xQPlzgR8CYr2Lkq_iAw==&ch=X977FcAh2HJFF5esd6RrK6d2We-7X3Xvg3tBsqpK8khnnq0fXeXNMw==]
  Technical Services 
[http://r20.rs6.net/tn.jsp?f=001h-raFFtboGY5DdkcAcDhVw5MJIRZPidVNeg4UUpxmeMC9VAaVbuq8lCM1_5Ib3_2NMH08cf15hJyIvTzDvvveVcIB_Rdk0rQvf5mI2LDqk22YnWND9Kx8Bq_WBB1MubVXfTaid34FOZ0ZdjGBsc1Z5n2msgTxwJETJLqqy4BnYO1kTAY5bfwzkq7WOpv6mnrz7s9z9HoVApKoIhbFx6XMA==&c=e7lcE_9ojvgSUCZid2wUMGyCl1MBItE7Lo_xQPlzgR8CYr2Lkq_iAw==&ch=X977FcAh2HJFF5esd6RrK6d2We-7X3Xvg3tBsqpK8khnnq0fXeXNMw==]
Informal Interpretation Request 
[http://r20.rs6.net/tn.jsp?f=001h-raFFtboGY5DdkcAcDhVw5MJIRZPidVNeg4UUpxmeMC9VAaVbuq8lCM1_5Ib3_24pVGN6NkLWHO6wTU4AWbVFqDutxVW9MGgzD4p6xGssZged4OT1kfrSeN8HwL1VVt9YIsSIg2aHWytJYkbcCO5VUHEhVSsJTRzQlEUQcFixOUGKSYCDvOzDjTR1X2XZThEGhAz8ewbD1XUy_MteRn88dfmjdNUGq1ColeX-TmUrANVXXp2ubBTgEosugl4X9pilCN7HMeE311caxkqdhaVlc2p_BzYrKU&c=e7lcE_9ojvgSUCZid2wUMGyCl1MBItE7Lo_xQPlzgR8CYr2Lkq_iAw==&ch=X977FcAh2HJFF5esd6RrK6d2We-7X3Xvg3tBsqpK8khnnq0fXeXNMw==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Link 
[http://r20.rs6.net/tn.jsp?f=001h-raFFtboGY5DdkcAcDhVw5MJIRZPidVNeg4UUpxmeMC9VAaVbuq8lCM1_5Ib3_2nh6di-3cPo0cV1XdQoA0I2kuII9yq9Q1LImCPNLdupTRf0v7gIzkXTo8sXg0KmyOtWEZG4ChQGf-_Oy8D9C5OOLvx8Z1lwoByyigQflgUxj5aU9Suzdrtw-ag25CnGzOwXZ6t40ZXjLOByz6ULmP4Kcf-082EAbBDoINM3_FVhyWXUKdRRbfPw==&c=e7lcE_9ojvgSUCZid2wUMGyCl1MBItE7Lo_xQPlzgR8CYr2Lkq_iAw==&ch=X977FcAh2HJFF5esd6RrK6d2We-7X3Xvg3tBsqpK8khnnq0fXeXNMw==]
Archives 
[https://www.firesprinkler.org/technical-services/subscribe-technical-updates/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

SA Cover for TU 
[http://r20.rs6.net/tn.jsp?f=001h-raFFtboGY5DdkcAcDhVw5MJIRZPidVNeg4UUpxmeMC9VAaVbuq8nsJfafQD53lANDDaxxZDPFuddyKT1A0ofO-TqQzOYjMhiRAoGw3O5xoTDcC4-rnHJvVEQah0CEzhIrFXndAuVl3n6iv84kHTSjA1oKK6efeyVNlvCrlD2NlVqbiWwt4JzkJ5SSzj7EWl76LJ7waJcLgyBB4O0obwg==&c=e7lcE_9ojvgSUCZid2wUMGyCl1MBItE7Lo_xQPlzgR8CYr2Lkq_iAw==&ch=X977FcAh2HJFF5esd6RrK6d2We-7X3Xvg3tBsqpK8khnnq0fXeXNMw==]
Free Subscription
to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?f=001h-raFFtboGY5DdkcAcDhVw5MJIRZPidVNeg4UUpxmeMC9VAaVbuq8lCM1_5Ib3_2LsQ_Flmv06PI7Gw6igS-VsvweeEI5NY_XT_hK0jsEdtnjCjrj8jx_wFeS8ddYTkkAHegPwHBEsVRuGds5CqSaVHrr2YKofJF1nxDWXd9ukr_inbEd8xBVUbktKwrSY5ky5uypQzr1sXzWB0YjpflHQ==&c=e7lcE_9ojvgSUCZid2wUMGyCl1MBItE7Lo_xQPlzgR8CYr2Lkq_iAw==&ch=X977FcAh2HJFF5esd6RrK6d2We-7X3Xvg3tBsqpK8khnnq0fXeXNMw==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]
AFSA Quality Contractor Recognition 
[http://r20.rs6.net/tn.jsp?f=001h-raFFtboGY5DdkcAcDhVw5MJIRZPidVNeg4UUpxmeMC9VAaVbuq8lCM1_5Ib3_24ABCmrbXfZTglSS4-CLjihOFkpAAFLABdWyPl77XyOKcg_mSLVs5rJrc5c-umzSO1r3jhKb6vtwgRqsE4OESf3D_iOqoqUJ8ZAX1kJJgg42-mzb023BvcZQaufHdMYJuDA1znajYtWfbbnOMicc8YZ4SkJk1LBg1Xb4qMICLnaL4eDDEh3vkqWeQpokuq7xS&c=e7lcE_9ojvgSUCZid2wUMGyCl1MBItE7Lo_xQPlzgR8CYr2Lkq_iAw==&ch=X977FcAh2HJFF5esd6RrK6d2We-7X3Xvg3tBsqpK8khnnq0fXeXNMw==]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1121963382582

This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=e1a6357c-e047-4d9b-9b7a-7ab0ad9b0d0e


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=e1a6357c-e047-4d9b-9b7a-7ab0ad9b0d0e


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp

Online Marketing by
Constant Contact(R)
www.constantcontact.com



American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to