August 31, 2015
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Plastic Idle Pallets
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

"What is the design criteria for plastic pallets stored 5 ft and under without 
cutoffs
from other storage?"
We have reviewed NFPA 13, 2010 edition that you indicated as the applicable 
standard.
 Our informal interpretation is that there are two options available.
Idle plastic pallets are more challenging than exposed unexpanded plastics in 
Chapter
15.  Thus you must apply the criteria of Chapter 12.  This section for idle 
plastic
pallets is presented in a very poor manner and was corrected for the 2013 
edition.
 For now, you need to apply the criteria as follows.  Section 12.12.2.1 
indicates
seven (7) different manners for the storage of plastic pallets.  You are allowed
 to select any of the seven options as applicable.  The first two options don't 
apply since they are outside the building.  Option 3 sends you to the next 
section
with two additional options but neither applies to your situation.  Section 
12.12.2.2(1)
is using a cut-off room.  Section 12.12.2.2(2) allows very limited amounts of 
plastic
pallets to be stored indoors where the facility has any level of sprinkler 
protection
for a different commodity or occupancy classification.  The 2013 edition 
specifies
a minimum ceiling design of OH2 shall be used.  To apply 12.12.2.2(2), all three
 of the following are required; (a) plastic pallets piled no higher than 4 ft, 
(b)
use high temperature-rated sprinklers, and (c) each pallet pile of no more than 
two stacks shall be separated from other pallet piles by at least 8 ft of clear 
space or 25 ft of stored commodity.  Option 4 sends you to Table 12.12.2.1 for 
ESFR
systems and is the first applicable option.  It's a broad based option and 
starts
at up to 25 ft of storage with no reduced allowance for lower storage heights.  
It's the only option that can be applied to storage in racks as emphasized by 
Section
12.12.2.3.  Option 5 is the only other applicable choice.  It's for indoor 
storage
with spray sprinklers for the following arrangement: (a) maximum storage height 
of 10 ft, (b) maximum ceiling height of 30 ft, (c) sprinkler density 0.6 gpm/sq.
 ft. over 2000 sq. ft., and (d) minimum sprinkler K-factor of 16.8.  There is no
 reduced allowance for lower heights.  The remaining two options do not apply 
since
they are for other protection schemes based on listed pallets and full scale 
testing.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2015, American Fire Sprinkler Association. All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001ry4iJ-I-aaeWdLWxA_RpQew4xKsOFME0I0jpFEFEHYsIXUjX39pbrVMLuvLRSFPs8R6r4cNzPN3k98eS4BOachen3T6GPf1v55AEfk9ZZcum4KdMEo_uB_kiUbZnvvKdaGtE-kaLco8Rxj6tRS7KEw32QHPMhGJxRw09dGv9X-kEXIaPQE9eAQ==&c=5v2toBdo5yKDPCwEDMJycD88E5i_uPIw-jsngVzTuwDcWGVTcb1NBw==&ch=4YHF4Xr48ddBF06ILqifbAIbH-IJTdSu8DYyrRz9zZ_U83v8XiU8_A==]
  Join AFSA 
[http://r20.rs6.net/tn.jsp?f=001ry4iJ-I-aaeWdLWxA_RpQew4xKsOFME0I0jpFEFEHYsIXUjX39pbrVMLuvLRSFPs8ifyMeGgz0Qp6P1Nk__gEt8P3VaSMuJMDXnTZlTlTIDnydWsEFVfGln8R45D3VRVZOG3rpeZz40SafBtrunZW8w9hs1DK3NeRyJ855teIMgJUUtHxI_Ott12xMhDS8NxcY01W8anj6W_0zSn-H1jZ3DGQBbMR1xl&c=5v2toBdo5yKDPCwEDMJycD88E5i_uPIw-jsngVzTuwDcWGVTcb1NBw==&ch=4YHF4Xr48ddBF06ILqifbAIbH-IJTdSu8DYyrRz9zZ_U83v8XiU8_A==]
  Scholarships 
[http://r20.rs6.net/tn.jsp?f=001ry4iJ-I-aaeWdLWxA_RpQew4xKsOFME0I0jpFEFEHYsIXUjX39pbrVMLuvLRSFPsCg2nXr7QAi5U0jiEn19q6H67-zDkKT3cz7Xc982r-s_3q34NJjIQOOoMrTvGuk96Wl04zN8VED7LMY211NIHvl3VOPv7T_d_RbnTor4OYAmieHcX3CDsVA==&c=5v2toBdo5yKDPCwEDMJycD88E5i_uPIw-jsngVzTuwDcWGVTcb1NBw==&ch=4YHF4Xr48ddBF06ILqifbAIbH-IJTdSu8DYyrRz9zZ_U83v8XiU8_A==]
Safety Training 
[http://r20.rs6.net/tn.jsp?f=001ry4iJ-I-aaeWdLWxA_RpQew4xKsOFME0I0jpFEFEHYsIXUjX39pbrVMLuvLRSFPsNwICLpmPZ6DcRQEkhBVxotXZQKzapySvbFpMRtUT7g-iWHfqcxFSOuEmRaFK6hlku8mKCMxFlhsypNlxDM6Aj4Hi10A4O0fLPoDP-ej9BuWM31jcRVqpdLEWhFbRqXX-qH4MUi1K0oQuomp2db9Un8w3Tt3vwDcYFtGllQufu8s=&c=5v2toBdo5yKDPCwEDMJycD88E5i_uPIw-jsngVzTuwDcWGVTcb1NBw==&ch=4YHF4Xr48ddBF06ILqifbAIbH-IJTdSu8DYyrRz9zZ_U83v8XiU8_A==]
  Technical Services 
[http://r20.rs6.net/tn.jsp?f=001ry4iJ-I-aaeWdLWxA_RpQew4xKsOFME0I0jpFEFEHYsIXUjX39pbrVMLuvLRSFPsmCY-0amkAkMgQxjpl74kZtD65U2PxiHvJ-t21D6ethidBq1TxJnmgCGBhWg-ib9-xhV60O7gcFPEzRJuWpbvZm2ugY4SJtbzqiNkb17o3T-hkQ8xR1wGIacmRSQZNT5SMoJRrqurZ00qhn4LL2QzTg==&c=5v2toBdo5yKDPCwEDMJycD88E5i_uPIw-jsngVzTuwDcWGVTcb1NBw==&ch=4YHF4Xr48ddBF06ILqifbAIbH-IJTdSu8DYyrRz9zZ_U83v8XiU8_A==]
Informal Interpretation Request 
[http://r20.rs6.net/tn.jsp?f=001ry4iJ-I-aaeWdLWxA_RpQew4xKsOFME0I0jpFEFEHYsIXUjX39pbrVMLuvLRSFPsYWW39nQqRdw06OaRR_PvGrF64c-LOhXZP71bJDSLoO-q_uICpacKtH4xboN5bfuRw824n9MtQvPRIw5q3JeB-GHhPImtmhSBZKLtx5dYVl-ux0QKciEODS0DxghlF5FnkViCewIPNHIOIFA4Kd071xnJzt9R6DhXhQM4f9mUo8jw2Eue1_hp8RASi4zFcyWY814RFe86gOb5uVxS5S0dGXtNZdRiiXng&c=5v2toBdo5yKDPCwEDMJycD88E5i_uPIw-jsngVzTuwDcWGVTcb1NBw==&ch=4YHF4Xr48ddBF06ILqifbAIbH-IJTdSu8DYyrRz9zZ_U83v8XiU8_A==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Link 
[http://r20.rs6.net/tn.jsp?f=001ry4iJ-I-aaeWdLWxA_RpQew4xKsOFME0I0jpFEFEHYsIXUjX39pbrWYcxHCGtPhvuz8533azb5Tq6bmF_OVXIoWZT1hiyaJqezPHj6NpDcUHVXRJu2vb6GMBU8QqWhAyJttnCt0FjHTcStxCuN1xgP-QRRu923FQJEzVYnfMrGT1nNXF6ejL4gI8EXg-KDKeLmXXULE_IOm_t6iEw2OxKi8N2mPdbt29i1ud9zZhFP7t8meB3Wr7pA==&c=5v2toBdo5yKDPCwEDMJycD88E5i_uPIw-jsngVzTuwDcWGVTcb1NBw==&ch=4YHF4Xr48ddBF06ILqifbAIbH-IJTdSu8DYyrRz9zZ_U83v8XiU8_A==]
Archives 
[https://www.firesprinkler.org/technical-services/subscribe-technical-updates/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

SA Cover for TU 
[http://r20.rs6.net/tn.jsp?f=001ry4iJ-I-aaeWdLWxA_RpQew4xKsOFME0I0jpFEFEHYsIXUjX39pbrT33F3rfYD1KF68kXiKRxi-O6GpveQaa8egTUmjvwdA_lZhVvTLRWDeWVpM90yKRxAAjZCBkT-QOaEK1N2uAPjl3K68B_pJ_iobXp8_jI26YLKv4VdRcrmaLvcq6pkwa_o7J4S3DzTz3yQNLlGP42PcPrOx3lRcBAQ==&c=5v2toBdo5yKDPCwEDMJycD88E5i_uPIw-jsngVzTuwDcWGVTcb1NBw==&ch=4YHF4Xr48ddBF06ILqifbAIbH-IJTdSu8DYyrRz9zZ_U83v8XiU8_A==]
Free Subscription
to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?f=001ry4iJ-I-aaeWdLWxA_RpQew4xKsOFME0I0jpFEFEHYsIXUjX39pbrVMLuvLRSFPs9E8m3u-SzryEuTWHWwfY6okYq8DUnz89prDvca21sIITFvNpW0YwlpbGJvPsfcUsByNBzWLuLrxKPucQ7c6x2atYNmB2jmB-ZduOM8hodApOhtZgRjrj249GRz62Iwv1uzs8Bg5pvtxIWN_HmcLjpw==&c=5v2toBdo5yKDPCwEDMJycD88E5i_uPIw-jsngVzTuwDcWGVTcb1NBw==&ch=4YHF4Xr48ddBF06ILqifbAIbH-IJTdSu8DYyrRz9zZ_U83v8XiU8_A==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]
AFSA Quality Contractor Recognition 
[http://r20.rs6.net/tn.jsp?f=001ry4iJ-I-aaeWdLWxA_RpQew4xKsOFME0I0jpFEFEHYsIXUjX39pbrVMLuvLRSFPsJQpWKgWkihnhXt4euI8jktaxEft_qL7fw2Vwok5LoqgDhcXNuMVxdz9QnZGi_cwf2XKVdH83Et6xMv_m95yfT0zirVoZKtypxQBUnLeyQtSiAF_s9Vb20HgYjjtXIWcKrFJru3jsPd6rLdPugSw48hUwYnYmpkbwTrX154EkZ2Pz_wf4aTsRFeW8dz9tO4wD&c=5v2toBdo5yKDPCwEDMJycD88E5i_uPIw-jsngVzTuwDcWGVTcb1NBw==&ch=4YHF4Xr48ddBF06ILqifbAIbH-IJTdSu8DYyrRz9zZ_U83v8XiU8_A==]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1122031693904

This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=dc5272ea-240a-4655-867a-75d4c539a3db


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=dc5272ea-240a-4655-867a-75d4c539a3db


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp

Online Marketing by
Constant Contact(R)
www.constantcontact.com



American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to