September 14, 2015
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Apartment Closets vs. NFPA 101 Life Safety Code
"Under Section 8.15.8.2 for closets and pantries, it specifies that sprinklers 
are
not required in closets less than 24 sq. ft. with the least dimensions not 
greater
than 3 ft in hotels and motels, therefore it is assumed that sprinklers are 
required
in closets of new apartment buildings as they are not under current hotel and 
motel
category.  Appendix D in D.1.1.6 for new apartment buildings specifies that 
closets
less than 12 sq. ft. in area in individual dwelling units shall not be required 
to be sprinklered.  How is this addressed?"
We have reviewed NFPA 13, 2013 edition as the applicable standard.  Our informal
 interpretation is that NFPA 13 requires sprinklers in closets of apartments and
 they can be omitted if only if the NFPA 101 Life Safety Code requires 
sprinklers.
First, there is no mistake regarding the extract information in D.1.1.6 of NFPA 
13 that was taken from NFPA 101 Life Safety Code.  The NFPA 101 Life Safety Code
 and NFPA 13 differ on protection for closets.  In this case, NFPA 101 allows 
sprinklers
to be omitted from closets of limited sizes, but NFPA 13 indicates that if the 
closets
are not hotel or motel occupancies, sprinklers must be installed.  In permanent 
residential occupancies, the closets typically have a higher fuel load and are 
always
protected.  The natural exception is when NFPA 13R or 13D is applied.  We 
sometimes
have a conflict with NFPA 101 Life Safety Code that does allow for small closets
 in apartments to omit sprinklers and those closets are limited in size.  The 
NFPA
101 Life Safety Code applicability needs to be reviewed to determine whether it 
has been adopted in your area.  If it is adopted, then one must determine what 
is
the applicable code requiring sprinkler protection.  If both the building code 
and
the NFPA 101 Life Safety Code required sprinkler protection, then one applies 
the
most restrictive requirement from both codes.  When the building code requires 
protection,
the standard NFPA 13 criteria would apply with the more conservative omission of
 sprinklers from only hotel and motels closets.  If only the NFPA 101 Life 
Safety
Code requires sprinkler protection, the exceptions it contains supersede NFPA 
13.
 This is supported by Section 22.1.1.2 that states, "Where the requirements of 
the
reference standard differ from the requirements of this standard, the referenced
 standard shall take precedence."  If sprinkler protection is not required by 
either
code, the building code still requires a system installed per NFPA 13 but the 
door
is wide open for applying the NFPA 101 Life Safety Code exceptions provided the 
AHJ allows it.  It should be noted that the 2010 edition of NFPA 13 moved this 
information
to Annex D in an attempt to avoid the misperception that it is an allowance by 
NFPA
13.  The bottom line is that the protection of apartment closets is typically 
required
but it depends on what code is driving the sprinkler requirement.
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2015, American Fire Sprinkler Association. All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001r45dLdB_WsHbMxGhHZ2n7RIqq0g0Ze8YmKRyU_cBT1laXf8CYAQ71NuLjIduN9e3BVRI1bQ2jc9zt6AIsOAtPrF-ZvO9aJOUwswgHXGXRSBPOS5NQbHrURh2KRTTrMcjxWUsu_pgkSCbBEhHJVzLRo29G9l-YHamlAximWPAx_3aQstbipsfcw==&c=apy46VnsB7782I1J8iEF7cggIoHADaFlD1AAhxqWWVo5ySEzHQws6Q==&ch=2uLe8ct9zqh210me5KfD09_nlEp8ebVOoSqwo1mPxULMiCEOrkwaew==]
  Join AFSA 
[http://r20.rs6.net/tn.jsp?f=001r45dLdB_WsHbMxGhHZ2n7RIqq0g0Ze8YmKRyU_cBT1laXf8CYAQ71NuLjIduN9e3Z2LK0oqM7BRP337fuTfeqR-HURM7g6z-YI-Noqx6_xia1H4TxMNTwbuFEKMROAtUugSpzeg37bvKyFeuViZV8tCF_3FQGPsEcqNEi2AL7TVv-J1wYztAfB4QEfhItbOPu1UCA7gWqaFvLSThkBufqyxN5FBYu7SA&c=apy46VnsB7782I1J8iEF7cggIoHADaFlD1AAhxqWWVo5ySEzHQws6Q==&ch=2uLe8ct9zqh210me5KfD09_nlEp8ebVOoSqwo1mPxULMiCEOrkwaew==]
  Scholarships 
[http://r20.rs6.net/tn.jsp?f=001r45dLdB_WsHbMxGhHZ2n7RIqq0g0Ze8YmKRyU_cBT1laXf8CYAQ71NuLjIduN9e3WzYsNAZc5He4y3nKdzykgDpKOQQSegIb4XycVNH7hxXeVQfNJVNW7f1yFjYDrEk_TbaZm2nAzFlxhs1bmC1L0lynTKMacGeQ2J1nsJnNaVr5X1FqHsIOTQ==&c=apy46VnsB7782I1J8iEF7cggIoHADaFlD1AAhxqWWVo5ySEzHQws6Q==&ch=2uLe8ct9zqh210me5KfD09_nlEp8ebVOoSqwo1mPxULMiCEOrkwaew==]
Safety Training 
[http://r20.rs6.net/tn.jsp?f=001r45dLdB_WsHbMxGhHZ2n7RIqq0g0Ze8YmKRyU_cBT1laXf8CYAQ71NuLjIduN9e3qaTlMuMlxSyl0oQbMwwPBGcz8CSgwQ3NFatVzv8Cu0rRN1V8EOpeVv_Je7zYLtlZKAidpwUwICKahiOPEL1sO9wBpRoTrdT388VSB4nn4Rt8btxjg6VFBYbM3qSBHa2nFqP2TFED3f5oTPZbtVpLPvT0w9UXPYKnO7Wzo5U5OI4=&c=apy46VnsB7782I1J8iEF7cggIoHADaFlD1AAhxqWWVo5ySEzHQws6Q==&ch=2uLe8ct9zqh210me5KfD09_nlEp8ebVOoSqwo1mPxULMiCEOrkwaew==]
  Technical Services 
[http://r20.rs6.net/tn.jsp?f=001r45dLdB_WsHbMxGhHZ2n7RIqq0g0Ze8YmKRyU_cBT1laXf8CYAQ71NuLjIduN9e3KK95ebtn_2qdTLz-1S7SXNa5hGlr_f-APhmTIjHwFM1ysmQkBYpqDC0uJjZZCkAiMV_8A05PONYJF9Htt6ARCzSy6H2uOhApR991BSqsV-nElWS3Jh12WIV5-wz6ZgeKjNtNPvThveVlgvsFuSXGpw==&c=apy46VnsB7782I1J8iEF7cggIoHADaFlD1AAhxqWWVo5ySEzHQws6Q==&ch=2uLe8ct9zqh210me5KfD09_nlEp8ebVOoSqwo1mPxULMiCEOrkwaew==]
Informal Interpretation Request 
[http://r20.rs6.net/tn.jsp?f=001r45dLdB_WsHbMxGhHZ2n7RIqq0g0Ze8YmKRyU_cBT1laXf8CYAQ71NuLjIduN9e3IgiwoU4hy8vo5m1qM5cBuh90dvW7GLQE0EJ7mOnPXjmgFcT7SFVESNexJwnTMv5TpSo5gyE0YvRdVJWt2hBQTBl87kQ6l1CvN7c5EJC1k-j504eBFOEN666ONcnu9DQd7y1N4W-pbWAZhQUNZbpdZoPdB9vhHh1gaFdabutKvxMpDUaDNyLQNEOl08wCn7nQ31WlVPgM1DwwKcrXFH3Q-OZKfIu-3il8&c=apy46VnsB7782I1J8iEF7cggIoHADaFlD1AAhxqWWVo5ySEzHQws6Q==&ch=2uLe8ct9zqh210me5KfD09_nlEp8ebVOoSqwo1mPxULMiCEOrkwaew==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
Webinar
NFPA 13, 2016 Ed. Update
by James Golinveaux
Tyco Fire Protection Products
September 17
11:00 AM - 12:30 PM (CST)
Click here 
[http://r20.rs6.net/tn.jsp?f=001r45dLdB_WsHbMxGhHZ2n7RIqq0g0Ze8YmKRyU_cBT1laXf8CYAQ71D0ySiO0-Et-6T5Z4l9BWFL__EuMpKPDLU1evDpvOZzXB8zKLMf1fGhlBKswo8MoUqY6xi30VPvKJAFXaqmh85J2DH3WQgEPaC72CKQrqfg8vx_XxXELVoWPJgWJrg2D1UmsGY2GChbg1BLq_8H3z9ckSwUvp3YDO2UvcC7f1I-v&c=apy46VnsB7782I1J8iEF7cggIoHADaFlD1AAhxqWWVo5ySEzHQws6Q==&ch=2uLe8ct9zqh210me5KfD09_nlEp8ebVOoSqwo1mPxULMiCEOrkwaew==]
to register.
AFSA Beginning
Fire Sprinkler System
Planning School
November 2-13, 2015
Sold Out!
2016 SCHEDULE
Jan. 11 - 22, 2016
Feb. 8 - 19, 2016
April 4 - 15, 2016
May 16 - 27, 2016
July 18 - 29, 2016
Oct. 3 - 14, 2016
For more info, call:
214-349-5965 
[http://r20.rs6.net/tn.jsp?f=001r45dLdB_WsHbMxGhHZ2n7RIqq0g0Ze8YmKRyU_cBT1laXf8CYAQ71CykrtjEaOtoG_IPKDgr5eDvN-cRnMuyYqr4mD8JasS5-xVn7eh2y758BrgoMcHPioT5TcN-bAqijaVPD2lXWFtxt6a-blY4bMIjlNlr-lOuHQFgjiShuDTuNMnqGDTnF8uHnc-ZKiQ44vkJ25PWEUe8raEWnpHG2AQV_nVrKLmw1u1sMQdWEnI=&c=apy46VnsB7782I1J8iEF7cggIoHADaFlD1AAhxqWWVo5ySEzHQws6Q==&ch=2uLe8ct9zqh210me5KfD09_nlEp8ebVOoSqwo1mPxULMiCEOrkwaew==],
ext. 132
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Link 
[http://r20.rs6.net/tn.jsp?f=001r45dLdB_WsHbMxGhHZ2n7RIqq0g0Ze8YmKRyU_cBT1laXf8CYAQ71FhGoCLSdx5xH8b5gNjlnFUgbVccEH3u6CYKDEPYe3wtApNb-zP7GfWjvAHVPXY1MJm987-__8bdHJ-KWsYKdjAmy8O1lCbX1ci2n7k3ns1WsWsbE7TiRTdfL7gKGBSS-SQt2kLLI0ACjYwgcuXdOkRIAL_7aBhxbiaDmrIhVmrBwHU0DdyqIAvqk5ewko2Azg==&c=apy46VnsB7782I1J8iEF7cggIoHADaFlD1AAhxqWWVo5ySEzHQws6Q==&ch=2uLe8ct9zqh210me5KfD09_nlEp8ebVOoSqwo1mPxULMiCEOrkwaew==]
Archives 
[https://www.firesprinkler.org/technical-services/subscribe-technical-updates/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]
AFSA Quality Contractor Recognition 
[http://r20.rs6.net/tn.jsp?f=001r45dLdB_WsHbMxGhHZ2n7RIqq0g0Ze8YmKRyU_cBT1laXf8CYAQ71NuLjIduN9e3TDg1qGAoILiAQq5nR-0yLIOae7x3uNVmxnDbB_dPcsBWQxJZzZSpHrKuNt9-iX1oJ42UmndsCGIN_sIjzffxuk-OqfPzR489ryJELZomGzQXwb2EARZTFP2NUbhvUNbhJ6uKD6fMm2xyaQ6rRsNpZJ7Z02o40pIdOj4B5e9Cs8v7TcD2KyAGlXDPVZVyvG5b&c=apy46VnsB7782I1J8iEF7cggIoHADaFlD1AAhxqWWVo5ySEzHQws6Q==&ch=2uLe8ct9zqh210me5KfD09_nlEp8ebVOoSqwo1mPxULMiCEOrkwaew==]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1122096778435

This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=44db84de-7f7d-453b-b28c-7668aeb04ceb


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=44db84de-7f7d-453b-b28c-7668aeb04ceb


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp

Online Marketing by
Constant Contact(R)
www.constantcontact.com



American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to