External Ice Effects on Fire Systems
"After a thorough 5-year inspection was conducted, checking for proper grade and
 all low point drains serviced, a sprinkler head still froze and burst without 
damage
to the pipe or fitting.  One side of the building actually hangs over a river.  
Maintenance personnel have reported ice build up on the pipe and roof trusses.  
Are there any studies on the effects of external icing on sprinklers?"
We have reviewed NFPA 25, 2011 edition that you indicated as the applicable 
standard.
 Our informal interpretation is external ice on sprinkler components may cause 
damage.
Ice build-up on sprinklers is not specifically mentioned in NFPA 25 and would be
 considered a form of loading on sprinklers but catching it would depend on the 
time of year if relying solely on a hired inspection and service provider.  The 
majority of the information focuses on removing water inside the pipe prior to 
freezing
to prevent sprinkler activations or pipe ruptures.  Sprinkler components can be 
damaged as ice forms and expands. Kerry M. Bell, Principal Engineer for 
UL LLC wrote an article for the Asia Pacific Fire Magazine dated April 2015 that
 touches on this issue.  The article states, "In regard to dry sprinklers 
installed
in freezers, it was determined that ice build-up external and internal to the 
sprinkler
had the potential to apply excessive stresses to the operating parts."  This 
article
also references a report titled, A Technical Analysis: The Use and Maintenance 
of
Dry Type Sprinklers by James Golinveaux, of Tyco Fire & Building Products.  The 
two documents acknowledge ice can build-up on sprinklers and may cause stresses 
where inadvertent sprinkler activation may occur.  The two documents were sent 
to
you by separate correspondence. Other than dry-pendent sprinklers in freezers, 
the
external build-up of ice on sprinklers has not been previously identified as an 
issue.  NFPA 25 addresses external ice build-up on components that are exposed 
to
the elements (hydrants, tanks, and exterior valves) but so conducting the 
typical
inspection would not identify this issue.  Owners are responsible for their 
systems
and should have flagged it for a separate review.
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2015, American Fire Sprinkler Association. All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001Akg9osKW1XXf2rl1jeevg-dytTkABE9M_8l_SEHzK4kPtY2t_SzphhhoXVmNp30ORMc99Zqe9GEaCyRk87bKqwRFhszO2XhQt4Xea-0nhjR4g_DrLSFPxuPsdj76Oc8neml5HdSmRS8UAElrOiTmreOhXSk9M-FbFbLqJH0aQiSgyzOOBBKmIg==&c=nHLE8PPYbIuDGyx3pugkporM0ClZl2lldDw5ShFsDvOvQfuJDA63_w==&ch=x-M6jnW6YD61ootqgTu5Zb5NhtRzrPHeN61cLOgp2OPO6oq3_g4uaw==]
  Join AFSA 
[http://r20.rs6.net/tn.jsp?f=001Akg9osKW1XXf2rl1jeevg-dytTkABE9M_8l_SEHzK4kPtY2t_SzphhhoXVmNp30Ob_y-3M4wmESmJ06ScbIoxyA_4jBMk21lYm36WlDa3-28wP_aahxsTB8POjLKHFFhi_gXD3v_PjUDA2vz3RxgFFWPbGxCHTe3UWqbyfOmWCJZ1fWRwEPgxG_MLjRsN0lCIi79OVoad9ReMAEfBmuzQhdesMqctDpm&c=nHLE8PPYbIuDGyx3pugkporM0ClZl2lldDw5ShFsDvOvQfuJDA63_w==&ch=x-M6jnW6YD61ootqgTu5Zb5NhtRzrPHeN61cLOgp2OPO6oq3_g4uaw==]
  Scholarships 
[http://r20.rs6.net/tn.jsp?f=001Akg9osKW1XXf2rl1jeevg-dytTkABE9M_8l_SEHzK4kPtY2t_SzphhhoXVmNp30Ovt6R4ytykWZ_qx_zbkmLiq61fUTWQRWS3lOSu2GI3wV_RaH3q0Tl2eO8qHnge3hDEe0I4eC1MbxTgeAy2sVatGkOn5YsfxL7dndj_ycQHSUVLVw7DDacWQ==&c=nHLE8PPYbIuDGyx3pugkporM0ClZl2lldDw5ShFsDvOvQfuJDA63_w==&ch=x-M6jnW6YD61ootqgTu5Zb5NhtRzrPHeN61cLOgp2OPO6oq3_g4uaw==]
Safety Training 
[http://r20.rs6.net/tn.jsp?f=001Akg9osKW1XXf2rl1jeevg-dytTkABE9M_8l_SEHzK4kPtY2t_SzphhhoXVmNp30OWdbUOd3Zu0MzEZ3TF4OdIsLF1Bk7opHaplCehvVnysK-eT_m40g48NAJ6KzYhXN38i2gUG1zQg0pYnrP-igZrNYsB7DysUSOfac5xuApzyX59jgN8p4sNOTAkr3bJPbjGeHON-AX3f9UgadhnYTO0COwB5vLpmW_TB0kf-uAh4M=&c=nHLE8PPYbIuDGyx3pugkporM0ClZl2lldDw5ShFsDvOvQfuJDA63_w==&ch=x-M6jnW6YD61ootqgTu5Zb5NhtRzrPHeN61cLOgp2OPO6oq3_g4uaw==]
  Technical Services 
[http://r20.rs6.net/tn.jsp?f=001Akg9osKW1XXf2rl1jeevg-dytTkABE9M_8l_SEHzK4kPtY2t_SzphhhoXVmNp30OddK4Mmj5ZF6saUdJRBJMzblupnl-QgWogMfnSjqIigBUjB9jWLlVtRnOSuIE_Cx1v-YDRk9LeJ0Ol3dEbsbQ-eiP7ng_AAG0TcOfa8IoZ_vnuZOV5e-jrJWoG3wOZxZPRDG-d4sU33LlSo9xzb9J3Q==&c=nHLE8PPYbIuDGyx3pugkporM0ClZl2lldDw5ShFsDvOvQfuJDA63_w==&ch=x-M6jnW6YD61ootqgTu5Zb5NhtRzrPHeN61cLOgp2OPO6oq3_g4uaw==]
Informal Interpretation Request 
[http://r20.rs6.net/tn.jsp?f=001Akg9osKW1XXf2rl1jeevg-dytTkABE9M_8l_SEHzK4kPtY2t_SzphhhoXVmNp30OBtGFVPIurA9S4g60nWD8BCz58btDpFSedFMCOmwu9pTLhI6t0ZmX3wX_dgcNyQ2AuTsQ4BZzWOvzq4G-FnRQXivv_9mqaaPfu8fPOwVcwMzChJO9_6auNoL7CRIoT4VmpHT26ga4qZ5x4Qbmu-Yoiu_6ytewmBZO9gxOQgbBoGYnNoE9dUxlw0rWRUi4fAeBu2_DtvRjDOUzTqUJgln3MYvRs1S5C-dd&c=nHLE8PPYbIuDGyx3pugkporM0ClZl2lldDw5ShFsDvOvQfuJDA63_w==&ch=x-M6jnW6YD61ootqgTu5Zb5NhtRzrPHeN61cLOgp2OPO6oq3_g4uaw==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
November 2-13, 2015
Sold Out!
2016 SCHEDULE
Jan. 11 - 22, 2016
Feb. 8 - 19, 2016
April 4 - 15, 2016
May 16 - 27, 2016
July 18 - 29, 2016
Oct. 3 - 14, 2016
For more info, call:
214-349-5965 
[http://r20.rs6.net/tn.jsp?f=001Akg9osKW1XXf2rl1jeevg-dytTkABE9M_8l_SEHzK4kPtY2t_Szphnt9y6Ncob-gGYo4oMxvwNbqYf-r1PqNmIYNrX_6PrVrD_WuCzqOrz3yUyzkEWcLJSI0IS7nhWrhoRB918ju0GZ77EVGmuePiol7BIFeuBjHAdkrATTUKqOmO1EMBwW9NZKKBrHit9rxgXipYZVmNptWwARrOU1J10-bV46BAvLRV11m3bwnX4s=&c=nHLE8PPYbIuDGyx3pugkporM0ClZl2lldDw5ShFsDvOvQfuJDA63_w==&ch=x-M6jnW6YD61ootqgTu5Zb5NhtRzrPHeN61cLOgp2OPO6oq3_g4uaw==],
ext. 132
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Link 
[http://r20.rs6.net/tn.jsp?f=001Akg9osKW1XXf2rl1jeevg-dytTkABE9M_8l_SEHzK4kPtY2t_SzphtuUdPk-JWNMNxAlKSsfTb0ekudEx0TQgs4_Th2ajDm-6KDt2XflTUTff2Rs800mnXKKUII-TlQewuhgv7L7bFxPmT5Bvh5Swg463czb6UGOBEWyw2XQ2RBM3HdjuOkxXKhXctXdNYT_ombqqgqf9-kW0img6nLPkzX-iup4U1YK2xCfHa7ToOjCxLH8ck9ZZQ==&c=nHLE8PPYbIuDGyx3pugkporM0ClZl2lldDw5ShFsDvOvQfuJDA63_w==&ch=x-M6jnW6YD61ootqgTu5Zb5NhtRzrPHeN61cLOgp2OPO6oq3_g4uaw==]
Archives 
[https://www.firesprinkler.org/technical-services/subscribe-technical-updates/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]
AFSA Quality Contractor Recognition 
[http://r20.rs6.net/tn.jsp?f=001Akg9osKW1XXf2rl1jeevg-dytTkABE9M_8l_SEHzK4kPtY2t_SzphhhoXVmNp30O4F4F_90soar6KbDXwaKQVBXEfc1DqkkJII4AqxTeqmYm40YWEzop-rMWhEKjMgVveWWz962mrG1RzJBJN7PiwCUPK90pYDue-Yljc9IdVIfOyDrY_ELcZoHu1AvtZ1yGm6nIetNGrUWoADVZHxwp0LxRJOldvaTiOxZY0l31uAko6ib9cdU1kLy-W_jLKR-X&c=nHLE8PPYbIuDGyx3pugkporM0ClZl2lldDw5ShFsDvOvQfuJDA63_w==&ch=x-M6jnW6YD61ootqgTu5Zb5NhtRzrPHeN61cLOgp2OPO6oq3_g4uaw==]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1122250342138

This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=80173e42-9407-4d59-95cd-bbe53366b9b5


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=80173e42-9407-4d59-95cd-bbe53366b9b5


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp

Online Marketing by
Constant Contact(R)
www.constantcontact.com



American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to