Wood Framing in Concealed Spaces
"We have a noncombustible steel purlin/girder building where a soffit system and
 the hard lid ceilings throughout the building were constructed of combustible 
wood.
 The direction from the consultants is that the soffit can be wood because it's 
"nonstructural".  Can you advise on the term structural and nonstructural wood 
in
reference to ceiling systems and soffits?"
We have reviewed NFPA 13, 2013 edition as the applicable standard as well as the
 2012 edition of the IBC.  Our informal interpretation is that NFPA 13 does not 
allow omission of sprinklers from soffits with wood framing.
The NFPA 13 standard does not define structure or structural in the standard, 
but
the IBC does in Chapter 2.  The building code such as the IBC can be referenced 
when the NFPA 13 standard does not address a specific topic.  Section 202 of the
 IBC defines structure as that which is built or constructed.  The commentary 
for
the definition says that it is intentionally broad so as to include everything 
that
is built as an improvement to real property within the scope of the code.  The 
IBC
also has definitions of light-frame construction as a type of construction whose
 vertical and horizontal structural elements are primarily formed by a system of
 repetitive wood or cold-formed steel framing members.  Specifically for wood is
 a definition of conventional light-frame construction as type of construction 
whose
primary structural elements are formed by a system of repetitive wood-framing 
members.
 As such, there will be repetitive use of wood to a concealed space and it would
 be considered structural.  It does not have to be load bearing to be 
structural.
The base requirement of NFPA 13 in paragraph 8.1.1 parenthesis (1) is that 
sprinklers
are required to be installed throughout the premises and parenthesis (4) 
sprinklers
can be omitted from areas specifically allowed by the standard.  Paragraph 
8.15.1.1
indicates that concealed spaces of exposed combustible construction must be 
protected
by sprinklers except where sprinklers are not required by paragraphs 8.15.1.2.1 
through 8.15.1.2.18 and 8.15.6. Paragraph 8.15.1.2.1 indicates that concealed 
spaces
of noncombustible and limited-combustible construction with minimal combustible 
loading having no access shall not require sprinkler protection.  The annex says
 in A.8.15.1.2.1 that minor quantities of combustible materials such as but not 
limited to cabling, nonmetallic plumbing piping, nonstructural wood, and so 
forth
can be present in concealed spaces constructed of limited or noncombustible 
materials
but should not typically be viewed as requiring sprinklers.  This section is not
 about the framing material since it states the construction must be 
noncombustible
or limited-combustible materials but is about the presence of other combustible 
materials referred to as loading.  The annex expands on this issue by providing 
the examples cabling, piping, and nonstructural wood.  Then it goes on to 
discuss
that this allowances is affected by the amount of combustibles.  This section 
does
not allow a minor amount of wood framing since it is definitely part of the 
structural
components of the building. Pretty much all of the remaining paragraphs in this 
section address omitting sprinklers in concealed spaces with combustible 
structural
members.  Your description does not qualify for any of the remaining exceptions.
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2015, American Fire Sprinkler Association. All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001F-zAQau8nGLSHLCM3czHS__-3XEMTlThikNBJqWnnC_E5G4Q3XT5AYOhos0H9VMGy4-6UajjF9QEBWtmOFeS1eN-B8qazWYtjj_0rDAA6_zs0n_tbEpeMxl-51apaDvBHXoqQIOq2pfQOwfdqmtznsZPnc9YO46UK_a_RicHWDyfORd1lx6ang==&c=WJTeFWy-ekxdx7SnjG47ew63q63s7gXHwOD5svfrAwe6CJAXkIB3Aw==&ch=J3miopkdVaemyV3mDEi9uSg83rQI_vAPWjAzEFqoOv6uLKPdY-sTlA==]
  Join AFSA 
[http://r20.rs6.net/tn.jsp?f=001F-zAQau8nGLSHLCM3czHS__-3XEMTlThikNBJqWnnC_E5G4Q3XT5AYOhos0H9VMGAMjyqdB63zqNBuu-ZY-9dvBlTEUMDOh_dKRrZs5TIaoUMrkldadYZfHWkrEy6zLF3b6AV9TSWlT9SVssWk57OqBsOxr5zMCcphsweH6ZN0OwYYhbwGa6M6hBf8kwI_9fZP55ew4yaAvYN_eKAubvv1uIz_Sq5M_y&c=WJTeFWy-ekxdx7SnjG47ew63q63s7gXHwOD5svfrAwe6CJAXkIB3Aw==&ch=J3miopkdVaemyV3mDEi9uSg83rQI_vAPWjAzEFqoOv6uLKPdY-sTlA==]
  Scholarships 
[http://r20.rs6.net/tn.jsp?f=001F-zAQau8nGLSHLCM3czHS__-3XEMTlThikNBJqWnnC_E5G4Q3XT5AYOhos0H9VMGjStkI1EJD5VH74D7gJdr90hagG1iHr3WSo8pkJIGb_C83KxEMuVgNZHroiXmuxAC4QJTHuKDRmlGVUJqu6AXFYy-0Gsxr0XrPKzbgBE06GStUFSdpdNRsA==&c=WJTeFWy-ekxdx7SnjG47ew63q63s7gXHwOD5svfrAwe6CJAXkIB3Aw==&ch=J3miopkdVaemyV3mDEi9uSg83rQI_vAPWjAzEFqoOv6uLKPdY-sTlA==]
Safety Training 
[http://r20.rs6.net/tn.jsp?f=001F-zAQau8nGLSHLCM3czHS__-3XEMTlThikNBJqWnnC_E5G4Q3XT5AYOhos0H9VMGmMTHoAi52gU7WamoAR8uO5PpIJFv3xPIcs38mJ72Mafwys0B8etX-930BJw8Y052drO1S1R6yoDrnOZa1GgxcNJY6sgECVIpxDj6wISkrcvAnCmbSj_hvKUNAsKUZ792HWt9AgvQR2KCviY7K0Lqo4TisgDC7A2aDbQtYT5pVm4=&c=WJTeFWy-ekxdx7SnjG47ew63q63s7gXHwOD5svfrAwe6CJAXkIB3Aw==&ch=J3miopkdVaemyV3mDEi9uSg83rQI_vAPWjAzEFqoOv6uLKPdY-sTlA==]
  Technical Services 
[http://r20.rs6.net/tn.jsp?f=001F-zAQau8nGLSHLCM3czHS__-3XEMTlThikNBJqWnnC_E5G4Q3XT5AYOhos0H9VMGqlFIfkvlWAjVDxYba_cl3diE6h-6vTrc7IHrXmhFZkwNORWrXRYZlGPoE12X3QZWVkFQjJaEE-ZLWIkqdAXDMpe1wXXygMB5H5fk-Swy3IjG1xmK-Vg_T9oXUn7pFI8qX2UDauReLoooJ3SFjuKvdQ==&c=WJTeFWy-ekxdx7SnjG47ew63q63s7gXHwOD5svfrAwe6CJAXkIB3Aw==&ch=J3miopkdVaemyV3mDEi9uSg83rQI_vAPWjAzEFqoOv6uLKPdY-sTlA==]
Informal Interpretation Request 
[http://r20.rs6.net/tn.jsp?f=001F-zAQau8nGLSHLCM3czHS__-3XEMTlThikNBJqWnnC_E5G4Q3XT5AYOhos0H9VMGYpQ-sakVyzR12miwdOyYFPdf5Cl1dcJXrMqhubBmLAl4-2vEKUcdENrnnus1Bg_AsfXBHSv9UW1EZ-OgM7NAJgKbUKNIQF4QBvPj5UWgjYAwU36OE1O9JhfyScRYopD89mst5PX8z3EmSinzg8O5jpLqVTeMPkx3PyXqoo2a7G3388YyQKrNVat3NQ_6w8KjXfoTrhcyAur0Wv3uVpZVGRX6H4oCn4QO&c=WJTeFWy-ekxdx7SnjG47ew63q63s7gXHwOD5svfrAwe6CJAXkIB3Aw==&ch=J3miopkdVaemyV3mDEi9uSg83rQI_vAPWjAzEFqoOv6uLKPdY-sTlA==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Call for Trainers
If you, or someone you know, are well versed in any (or all) of the following 
areas:
installation, layout, or inspection/testing/ maintenance of fire sprinkler 
systems,
and want to teach or develop courses, let us hear from you!
Click HERE  
[http://r20.rs6.net/tn.jsp?f=001F-zAQau8nGLSHLCM3czHS__-3XEMTlThikNBJqWnnC_E5G4Q3XT5AS9FKIh8vFtbLgaWFHL7TwqSupihFqstHDNX6eqiy_t3xrXCugZ_mFqAlmLJQouAmY1vqCB7ip8uwxWt_X738dpbKUb4yL5dj42OMxYLrqmz5PI6iueL0RPdo-UizUMvh9DfQSXBJWZo&c=WJTeFWy-ekxdx7SnjG47ew63q63s7gXHwOD5svfrAwe6CJAXkIB3Aw==&ch=J3miopkdVaemyV3mDEi9uSg83rQI_vAPWjAzEFqoOv6uLKPdY-sTlA==]for
more details
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning Fire Sprinkler System
Planning School
November 2-13, 2015
Sold Out!
2016 Schedule
Jan. 11 - 22, 2016
Feb. 8 - 19, 2016
April 4 - 15, 2016
May 16 - 27, 2016
July 18 - 29, 2016
Oct. 3 - 14, 2016
For more info, call:
214-349-5965 ext. 132
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Link 
[http://r20.rs6.net/tn.jsp?f=001F-zAQau8nGLSHLCM3czHS__-3XEMTlThikNBJqWnnC_E5G4Q3XT5AS9FKIh8vFtbCkuJjevFKsiY9xieZ-cGs2aFqAo0CWzTADFuPOslt9tK1taNjb1HDpHgLZfUFh_7WKg_rmm6_c2nuHIP54iHzpCLEzzCxh4GEjtAMlpk2OsJ_TixQjeKaqDXHPJtpng0IUcL6Ciwm_lYyafVudxF6VwoqKqilx7VFXbXg84iG61eJEMImNpdAQ==&c=WJTeFWy-ekxdx7SnjG47ew63q63s7gXHwOD5svfrAwe6CJAXkIB3Aw==&ch=J3miopkdVaemyV3mDEi9uSg83rQI_vAPWjAzEFqoOv6uLKPdY-sTlA==]
Archives 
[https://www.firesprinkler.org/technical-services/subscribe-technical-updates/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]
AFSA Quality Contractor Recognition 
[http://r20.rs6.net/tn.jsp?f=001F-zAQau8nGLSHLCM3czHS__-3XEMTlThikNBJqWnnC_E5G4Q3XT5AYOhos0H9VMGe_BMnnBw3xi2F-dXwqSoGhiPR1LDHiAuOqZQSaOwoErCW0oVudbwHB9ypsNTEXMOn48EgV4yG4mdEF484s18D3TFttPCt8MjjKBXhvZFatFsvTJWJlMhWfdEhv8aZS4OxFM7FIcXuJRNQUzA35Ia-UbDb3e_1xPcQeW6B8AVTC2qPlMdPpmgT38SkCYzW2Zw&c=WJTeFWy-ekxdx7SnjG47ew63q63s7gXHwOD5svfrAwe6CJAXkIB3Aw==&ch=J3miopkdVaemyV3mDEi9uSg83rQI_vAPWjAzEFqoOv6uLKPdY-sTlA==]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1122383671472

This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=e54c22a1-c83d-4959-b0aa-dfbf8aed3840


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=e54c22a1-c83d-4959-b0aa-dfbf8aed3840


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp

Online Marketing by
Constant Contact(R)
www.constantcontact.com



American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to