October 19, 2015
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Use of Dated Sprinklers
"A sprinkler activated on a dry pipe sprinkler system that was installed in 2012
for a senior center. Upon investigation, it was found that the upright
sprinklers
utilized were manufactured in 2003 and found as discontinued. Would the use of
these sprinklers constitute a violation of the NFPA 13 standard in any way?"
We have reviewed NFPA 13, 2013 edition as the applicable standard. Our informal
interpretation is that the use of the sprinkler would be in compliance with
NFPA
13, Section 6.2.
Even though the sprinkler was manufactured in 2003 and installed in 2012, it is
still considered a new sprinkler as long as it has never been installed. The
sprinklers
have a UL listing as a quick response 5.6 K-factor sprinklers. As with any
sprinkler
it must be installed per its listing. Another issue that should be looked at
with
this sprinkler is how it was stored. As required by Section 6.2.9.3, sprinklers
that are placed in a spare head cabinet must be kept in the location where they
are not exposed to temperatures in excess of 100 deg. F. This would also apply
to any sprinkler being stored over any period of time.
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
in fire protection engineering. This is provided with the understanding that
the
AFSA assumes no liability for this opinion or actions taken on it and they are
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2015, American Fire Sprinkler Association. All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Quick Links
firesprinkler.org
[http://r20.rs6.net/tn.jsp?f=001-7ftmVDN3a3rT4UciZscZtHhAWABnPvQvDt-MVgvKtSEfxGvG48BInXKRjc68Vvis4STxsK2u3T8ZS_SbjCoA4Jz0wDIkWYfwbS3j5SNmfogYDAeR5y8imG0KXKJYS1GIGBTNaoutGTdLiZvk5kNeAMUW63n0QjfP1Sr8jar2yiBooHmdoXvSA==&c=u4hacbGI657n2UbmehlvA9o1cGgMqvB1SzteleTxE-VzieoRdbT5XQ==&ch=C_o5IccU9NjEXOYWbZHVBIir2m00iTzBpxvj1b_9krLiEipFpsWq6A==]
Join AFSA
[http://r20.rs6.net/tn.jsp?f=001-7ftmVDN3a3rT4UciZscZtHhAWABnPvQvDt-MVgvKtSEfxGvG48BInXKRjc68Vvi1xSW1oSTzP4LV3HRY6VPzv3t-Dj-j_OrqV20E-KijiNmjaPM59w_Gw9WP8LlqfRmmEmbTwpj-hz0_E4bQ-BibupqEF3R_0LUmer6zt5Sj7LghGuYIy7-pKEyWrTHn2uw2W1Bvna4JHUkAgsf1B6JUekaNzsCGs-Q&c=u4hacbGI657n2UbmehlvA9o1cGgMqvB1SzteleTxE-VzieoRdbT5XQ==&ch=C_o5IccU9NjEXOYWbZHVBIir2m00iTzBpxvj1b_9krLiEipFpsWq6A==]
Scholarships
[http://r20.rs6.net/tn.jsp?f=001-7ftmVDN3a3rT4UciZscZtHhAWABnPvQvDt-MVgvKtSEfxGvG48BInXKRjc68Vvi0PCySHF8jpx_NRQb986wUvrwcpZ5Wkybzy7YwyufoOJQF8jIowAk3hjchcqokwZmA1-ZrviZWXoM9LHpJo00qGCGrlNZwnT51j8KsWNkzc2UDyfccu2hPA==&c=u4hacbGI657n2UbmehlvA9o1cGgMqvB1SzteleTxE-VzieoRdbT5XQ==&ch=C_o5IccU9NjEXOYWbZHVBIir2m00iTzBpxvj1b_9krLiEipFpsWq6A==]
Safety Training
[http://r20.rs6.net/tn.jsp?f=001-7ftmVDN3a3rT4UciZscZtHhAWABnPvQvDt-MVgvKtSEfxGvG48BInXKRjc68Vvip0Do3vJQFCbrsxku2Wi6HMB9nJK9LJKf5SvL8H43SwqS5Ryv9BPdtyhpWBzvuQYCK8aqPzpuzv_0q8Ui5yoxdD5vHkQC9wQh2AuRq426vi0YXApc2RJ1gGxJOWzhP2_VGbjx0XB8EQhUkZxc0nQZx2mnqTmNpw83bk0CIfIcMjo=&c=u4hacbGI657n2UbmehlvA9o1cGgMqvB1SzteleTxE-VzieoRdbT5XQ==&ch=C_o5IccU9NjEXOYWbZHVBIir2m00iTzBpxvj1b_9krLiEipFpsWq6A==]
Technical Services
[http://r20.rs6.net/tn.jsp?f=001-7ftmVDN3a3rT4UciZscZtHhAWABnPvQvDt-MVgvKtSEfxGvG48BInXKRjc68VvinKfGQwxHuTDXw8J-tICn8ZJNnBzyzxSr0D9K6JmKfv4SaxehqwUAPnGRHd8nZuz7f7YOGsD8-0aDbneM2bngFOdMK3Ig-hdR4DCVbkZEIOSzubMFGl-BabZT9ti0anS9p4Kwx5sSFk3KWpXVAR_FuA==&c=u4hacbGI657n2UbmehlvA9o1cGgMqvB1SzteleTxE-VzieoRdbT5XQ==&ch=C_o5IccU9NjEXOYWbZHVBIir2m00iTzBpxvj1b_9krLiEipFpsWq6A==]
Informal Interpretation Request
[http://r20.rs6.net/tn.jsp?f=001-7ftmVDN3a3rT4UciZscZtHhAWABnPvQvDt-MVgvKtSEfxGvG48BInXKRjc68VvifI3_i2Lrb_wbbVtzrXfmiVF8BFQTgBqnMmz2CtWU1Fe6eb3IfnI-F1g5xU6_FBwH2M4aeapgB6sOHgS0NrDCVEP7XewVXoqh8q3qeJkwUapoAc3J-wTFFUe6vZkbx--Eq8lQBdot7UsLrrtBu__tyk3dppYN2aoS-UxWemR5Keasaw_mHs6WQicfVIOUwACQ1ARm3HSCRWhqrRNXorfrjqqRyzeFyORF&c=u4hacbGI657n2UbmehlvA9o1cGgMqvB1SzteleTxE-VzieoRdbT5XQ==&ch=C_o5IccU9NjEXOYWbZHVBIir2m00iTzBpxvj1b_9krLiEipFpsWq6A==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Call for Trainers
If you, or someone you know, are well versed in any (or all) of the following
areas:
installation, layout, or inspection/testing/ maintenance of fire sprinkler
systems,
and want to teach or develop courses, let us hear from you!
Click HERE
[http://r20.rs6.net/tn.jsp?f=001-7ftmVDN3a3rT4UciZscZtHhAWABnPvQvDt-MVgvKtSEfxGvG48BIiBuHfPxj_qToSl4r3wxDanqLHhM4OrlsbdvBvnzHc4uSYBevqPPk__pfndsK_AlOEBPNt_493Lm105Ar9CdliMUuKjWkDMPVZ2we-nvVDFoKWpRnPh8d-zzaVI7GVVS2gwkEquODtpB&c=u4hacbGI657n2UbmehlvA9o1cGgMqvB1SzteleTxE-VzieoRdbT5XQ==&ch=C_o5IccU9NjEXOYWbZHVBIir2m00iTzBpxvj1b_9krLiEipFpsWq6A==]for
more details
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Training Calendar
AFSA Beginning Fire Sprinkler System
Planning School
November 2-13, 2015
Sold Out!
2016 Schedule
Jan. 11 - 22, 2016
Feb. 8 - 19, 2016
April 4 - 15, 2016
May 16 - 27, 2016
July 18 - 29, 2016
Oct. 3 - 14, 2016
For more info, call:
214-349-5965 ext. 132
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
PDF Link
[http://r20.rs6.net/tn.jsp?f=001-7ftmVDN3a3rT4UciZscZtHhAWABnPvQvDt-MVgvKtSEfxGvG48BInpcs3n3BbM6eaFlgd9GtN-lC82lkMf2QAZPsGX42AT0IOvt0QD0Bk--lHrkiAHhBc1wId4NTs59nvhmKfiWumGTMkC6qyhNKdzZ3I6rl6ROPZuNi36pKT7MSu4esMhTSdcnGq2ChB8ik70goFyqOXD4gTxmO7p8OJfu5Ux24lkC9tTsKBjEjIR_MB-fyQZrTA==&c=u4hacbGI657n2UbmehlvA9o1cGgMqvB1SzteleTxE-VzieoRdbT5XQ==&ch=C_o5IccU9NjEXOYWbZHVBIir2m00iTzBpxvj1b_9krLiEipFpsWq6A==]
Archives
[https://www.firesprinkler.org/technical-services/subscribe-technical-updates/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Quality Contractor
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]
AFSA Quality Contractor Recognition
[http://r20.rs6.net/tn.jsp?f=001-7ftmVDN3a3rT4UciZscZtHhAWABnPvQvDt-MVgvKtSEfxGvG48BInXKRjc68VviHkL4ZsxVYVIUg4OrDRdgtfDsKaJvm2uPPbv5dXL2rrU7RJXjtOi8aj7OrYpi0lZtUFCg8FctBgfizeyCbEgYoaw0YVuToMNmEzxqZX-9KeyVMkLeT3kmTHBwLBWGdOP2PDOXszrPBjj7xwb4IEUuD7QtT8WtSOCY4KHHnpPvNAEdaE-HLNNNFbyLfF9Q2xgM&c=u4hacbGI657n2UbmehlvA9o1cGgMqvB1SzteleTxE-VzieoRdbT5XQ==&ch=C_o5IccU9NjEXOYWbZHVBIir2m00iTzBpxvj1b_9krLiEipFpsWq6A==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1122549964798
This email was sent to [email protected] by
[email protected].
Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=70b2ae18-db8e-4a09-9cc4-a054718bed9c
Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=70b2ae18-db8e-4a09-9cc4-a054718bed9c
Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp
Online Marketing by
Constant Contact(R)
www.constantcontact.com
American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas |
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org