"I'm reviewing plans that shows a pantry that is 4 ft x 4 ft when including a 
wing
or niche that is 12 in. by 18 in.  The total square footage is less than 24 sq. 
ft. and the smallest dimension is technically less than 3 feet.  Does this meet 
the intent of Section 8.3.3?"
We have reviewed NFPA 13D, 2013 edition as the applicable standard.  Our 
informal
interpretation is that sprinklers may not be required.
Section 8.3.3 does indicate in parenthesis (2) that the shortest dimension does 
not exceed 3 ft.  Technically, a fire sprinkler is required in the pantry by the
 standard.  With that said, this wing or niche that increases the dimension 
beyond
3 ft does not significantly increase the hazard in the pantry to require a 
sprinkler
since the area does not exceed 24 sq. ft.  This is supported by recent changes 
to
clothes closets, linen closets, and pantries in NFPA 13, 13R and 13D standards. 
 The 2016 edition of NFPA 13D removed the wording "the shortest dimension does 
not
exceed 3 ft".  The clothes closets, linen closets, and pantries cannot exceed 24
 sq. ft. and the walls and ceilings have to be surfaced with noncombustible or 
limited-combustible
materials as defined in NFPA 220.  This also occurred for clothes closets, linen
 closets, and pantries in dwelling units in the 2016 edition of NFPA 13R in 
Section
6.6.3 and NFPA 13 in Section 8.15.8.2 for clothes closets, linen closets, and 
pantries
within dwelling units in hotels and motels.  The committee statement used was 
that
the 3-foot dimension is not necessary since it does not change the size of the 
closet
where sprinklers can be omitted.  The fire doesn't know whether the closet is 2 
ft by 12 ft or 4 ft by 6 ft.  Section 1.5 of the 2013 edition allows alternate 
methods
if they provide an equivalent level of protection.  What better assurance of 
equivalency
can be provided than the latest edition of NFPA 13?  Nonetheless, this will be 
your
decision as the AHJ not to require a sprinkler inside the pantry.
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2015, American Fire Sprinkler Association. All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001MwcCnDLlJfQQcXrTp5wt5kXCz_bi9WEDdliLmQ2w8ToaAvkRxDm2ESKjMEWAYcxeTisgsBmJkhPTSjQ1pe7LylaupCmQ8MF03k4E27RludEQdzprpDoW0AXShx7Crgklm2pCtCxOKCzs6svFv08XMhynvi_JOmPuI27gfoGWUtYdWMSKE-g_Qw==&c=BaAZaSyHFhpemuNAYXvcivC97TYe3tz4tGl0dtgRJAjy_FW8tVp_Ew==&ch=KUznRITx2VittH83f8r9y988vqDsDsj7u4EGdfCOS6UatRZ_Sef_Zg==]
  Join AFSA 
[http://r20.rs6.net/tn.jsp?f=001MwcCnDLlJfQQcXrTp5wt5kXCz_bi9WEDdliLmQ2w8ToaAvkRxDm2ESKjMEWAYcxeZWXzgCVG6701DcU5o0L1kvqyzWQPY8FT_qpF-py55HVUgM4GZJRxbp5rqTW5TVuOhoDkGGCjt6k9T9M0IzkXjwmbrLDHVveaUo4u3d4H9qThsmJD-zF41PvWp5C0cK3jMJs0_UKlGeu-Ae-86CpO7ftJBslJ03Lg&c=BaAZaSyHFhpemuNAYXvcivC97TYe3tz4tGl0dtgRJAjy_FW8tVp_Ew==&ch=KUznRITx2VittH83f8r9y988vqDsDsj7u4EGdfCOS6UatRZ_Sef_Zg==]
  Scholarships 
[http://r20.rs6.net/tn.jsp?f=001MwcCnDLlJfQQcXrTp5wt5kXCz_bi9WEDdliLmQ2w8ToaAvkRxDm2ESKjMEWAYcxee8xrbVJqniffwS1C3iWKJ0PzIlD5P80zCbSv0JbwuKbx3nbYF8GU27Dv4NS-13oRdg5jSp5rEUXi1Gm6oUyKF8xaUUI3M6bHboGywc8XL_t6DAIgcdEzuQ==&c=BaAZaSyHFhpemuNAYXvcivC97TYe3tz4tGl0dtgRJAjy_FW8tVp_Ew==&ch=KUznRITx2VittH83f8r9y988vqDsDsj7u4EGdfCOS6UatRZ_Sef_Zg==]
Safety Training 
[http://r20.rs6.net/tn.jsp?f=001MwcCnDLlJfQQcXrTp5wt5kXCz_bi9WEDdliLmQ2w8ToaAvkRxDm2ESKjMEWAYcxeF62nAgT5xJG4YkselwjetFVWpxBWCVLdfMCtMf4zaFXilrUx30p_hrgfPfngmOULDT3Iv_6hAaipJyKStaTyi3_ohicQkIvhN09Cl3wN_SqEmiOJ3uOGzODpQevtbImr0ijbU0BLvew6TrK20g2nAW6MsnYhwjB5cyK3I6HzvGg=&c=BaAZaSyHFhpemuNAYXvcivC97TYe3tz4tGl0dtgRJAjy_FW8tVp_Ew==&ch=KUznRITx2VittH83f8r9y988vqDsDsj7u4EGdfCOS6UatRZ_Sef_Zg==]
  Technical Services 
[http://r20.rs6.net/tn.jsp?f=001MwcCnDLlJfQQcXrTp5wt5kXCz_bi9WEDdliLmQ2w8ToaAvkRxDm2ESKjMEWAYcxe57foTUqUJIGrRsdcI9PvF5J1umkDTg3ZqMADwWU9EZEgd-q6EIfNN9SW-f1Nu5QxHtosx9ZTCgEo3POKn8vQkmKW8DBYVdPZEeMG_RQmxFXdvJpAmXT6H5ikb2OGMr02VBfdR4j9jVTjlSebmVwwEg==&c=BaAZaSyHFhpemuNAYXvcivC97TYe3tz4tGl0dtgRJAjy_FW8tVp_Ew==&ch=KUznRITx2VittH83f8r9y988vqDsDsj7u4EGdfCOS6UatRZ_Sef_Zg==]
Informal Interpretation Request 
[http://r20.rs6.net/tn.jsp?f=001MwcCnDLlJfQQcXrTp5wt5kXCz_bi9WEDdliLmQ2w8ToaAvkRxDm2ESKjMEWAYcxeoCaOdUOmqEEIufGlDi2zv6SjF-vAa3ADHGsFX4HZAr0-kJuZMw4x9HzRYRbyeF-67lZLxKfSc0xnpT4Bjqtud419i5gi7ZIaYoBIxr4IXCJDqLnkG4dMnHTt1YNeUzVb4IdN3ou4xOclyGFTJASIKg2C_Ii2qEvsnjEYn5L-iPwNe2mdzkCyRQoN7BDhVoBxvUpUCkJFS8KXz8V_8-N6a7xrTowVF8x_&c=BaAZaSyHFhpemuNAYXvcivC97TYe3tz4tGl0dtgRJAjy_FW8tVp_Ew==&ch=KUznRITx2VittH83f8r9y988vqDsDsj7u4EGdfCOS6UatRZ_Sef_Zg==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning Fire Sprinkler System
Planning School
2016 Schedule
Jan. 11 - 22, 2016
Feb. 8 - 19, 2016
April 4 - 15, 2016
May 16 - 27, 2016
July 18 - 29, 2016
Oct. 3 - 14, 2016
For more info, call:
214-349-5965 ext. 132
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Call for Trainers
If you, or someone you know, are well versed in any (or all) of the following 
areas:
installation, layout, or inspection/testing/ maintenance of fire sprinkler 
systems,
and want to teach or develop courses, let us hear from you!
Click HERE  
[http://r20.rs6.net/tn.jsp?f=001MwcCnDLlJfQQcXrTp5wt5kXCz_bi9WEDdliLmQ2w8ToaAvkRxDm2EVMBZnjKN8VrBHpFUvIoESEoudL29z9QctUXI3OYvmaJfivf7t9mQqXZv2zZIxwBevkiob6bHR_4q_Ie1r0BnSV2UM93GbeRJLs9vjWW2DG3fCPrwhNXb2Ci5LYFvqewKCjVBMdyIo22&c=BaAZaSyHFhpemuNAYXvcivC97TYe3tz4tGl0dtgRJAjy_FW8tVp_Ew==&ch=KUznRITx2VittH83f8r9y988vqDsDsj7u4EGdfCOS6UatRZ_Sef_Zg==]for
more details
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Link 
[http://r20.rs6.net/tn.jsp?f=001MwcCnDLlJfQQcXrTp5wt5kXCz_bi9WEDdliLmQ2w8ToaAvkRxDm2EYWC8aKqYRYm3B0XVWZqoJlcIKWgJQLymKhBNjeAmX-sy2zSjuyOrXGqqc1EIaGsHQYoI39VDgQbl8i9Fz2E6dMIMIpABcWxIMjJHzyjSyilY6GsNxdpBAladjbE-UFNiSGfu2ljT4UlPNlr4cOm6rnuQPVxXr_P2QIiqLp1wIlhWPd2ndxzEvMSe8tyPLH6Ng==&c=BaAZaSyHFhpemuNAYXvcivC97TYe3tz4tGl0dtgRJAjy_FW8tVp_Ew==&ch=KUznRITx2VittH83f8r9y988vqDsDsj7u4EGdfCOS6UatRZ_Sef_Zg==]
Archives 
[https://www.firesprinkler.org/technical-services/subscribe-technical-updates/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]
AFSA Quality Contractor Recognition 
[http://r20.rs6.net/tn.jsp?f=001MwcCnDLlJfQQcXrTp5wt5kXCz_bi9WEDdliLmQ2w8ToaAvkRxDm2ESKjMEWAYcxe_AyONIDwz_fybBOdJmREQ_DJdZ6otlgwOR6d1uQRbf-OKKM8cY5IdH4rsoap7S0MCzWozlois4oTPc7yLeCLLv4KMJKKFG6R8piVtFxpX-R6n457FrAWRti1-BPwDWINqEUBNQgpE8JIVX5RvVNx_omInP2ZEvRteq0n2Ys3cE0iUY5DNJ43dpXegpe5DsVb&c=BaAZaSyHFhpemuNAYXvcivC97TYe3tz4tGl0dtgRJAjy_FW8tVp_Ew==&ch=KUznRITx2VittH83f8r9y988vqDsDsj7u4EGdfCOS6UatRZ_Sef_Zg==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1122767271493

This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=10301c05-176d-4ce9-8852-cdc7852b84e1


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=10301c05-176d-4ce9-8852-cdc7852b84e1


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp

Online Marketing by
Constant Contact(R)
www.constantcontact.com



American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to