November 16, 2015
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Deflector Placement for Beams with Different Depths
"I have a building with panel construction with beams 9 ft apart and 28 ft long.
  It's a long building with a central 21-inch deep beam running the long length 
of the building, but offset from the centerline of the room by 2 ft 6 inches.  
On
the longer side of the central beam, the structural members are 16-inch deep 
beams.
 On the other side, they are 14-inch deep beams.  Because the central beam is 
offset,
my middle line of my proposed grid is close, but not directly under the central 
beam.  I plan to sprig the heads up for future tenant finish-outs so elevation 
isn't
an issue.  I'm wondering where I should elevate my deflectors from which set of 
beams.  Is it acceptable for the center line of the grid to protect both sides 
of
the 21-inch beam, but be 2-inches too low for the 14-inch side?"
We have reviewed NFPA 13, 2013 edition as the applicable standard.  Our informal
 interpretation is that a branch line with sprinklers can protect under both 
sides
of the 21-inch beam.
NFPA establishes two types of construction, Obstructed and Unobstructed.  The 
type
of construction you described is obstructed construction.  NFPA uses the term 
"panel
construction" in A.3.7.1 (4) as panels formed by beams spaced more than 7-1/2 ft
 apart and framed into girders with a maximum of 300 sq. ft. in area.  Section 
8.6.4.1.2
establishes that under obstructed construction, the sprinkler deflector shall be
 located 1 to 6 inches below the structural members and a maximum distance of 22
 inches below the ceiling/roof deck.  In your application, a 21-inch deep beam 
separates
the 14-inch and 16-inch beams to where the sprinkler deflectors are located 
within
1 to 6 inches under the 16-inch beam.  Although the 14-inch beam is adjacent to 
the 21-inch beam and it's within the area of coverage of the sprinklers under 
the
16-inch beams, the sprinklers do not have to be placed within 1 to 6 inches of 
the
14-inch deep beam.  The deflector distance throughout the area of coverage of 
the
sprinkler is not as critical as that required for unobstructed construction in 
Section
8.6.4.1.1.1.  As explained in the Sprinkler Systems Handbook, panel construction
 can be considered a version of beam and girder construction.  Beam and girder 
construction
causes heat from a fire to accumulate within the bays or panels formed by the 
supporting
members.  As a fire continues to generate heat, the heat flows down the length 
of
the members, activating only sprinklers within that bay or panel.  Once the 
capacity
of the bays or panels is reached, fire gases spill over into the adjacent bays 
or
panels and allow sprinklers in other bays and panels to activate.  Because of 
the
phenomenon, the deflector positioning rules in Chapter 8 provide a degree of 
flexibility
in positioning the deflector in relation to the ceiling and the supporting 
members.
 As such, if a fire is located on the 14-inch beam side, sprinklers will 
activate
under those bays or panels.  If the fire is not controlled, the heat will 
continue
to build up and eventually spill over and activate the sprinklers on the other 
side
of the 21-inch deep beam that are under the 16-inch deep beams.  For panel 
construction,
it's the lower structural member that matters.  The main objective of the 
sprinkler
system is to keep the upper layer cool, preventing flashover, thus controlling 
the
fire.
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2015, American Fire Sprinkler Association. All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001idrUHw9_YR74VbW-_Xp8jkSsgr0MUbJcbVjihxsBWQvdf3yg_btmpAtW7UUiq-jvAfYod5uRcFabjyNdDf-roK0rJhtoG0-AU9lvpvp3zuJEve5CPSYg0vNrfdNsoTE3X60VMca5M5MkctFNqQv8kojj0lHC73Gujy4BlTOq_FiE9mHob5TZgw==&c=aJlsu29wMowPS48vR_j4p-mMQlax7FjISoRV3TlL6sFAssG_yQe2XA==&ch=JlLJRE26PefhPdl_rOl7o_e3Ovb1jewwcBHsfAH_MaWc_6RMXM_h4Q==]
  Join AFSA 
[http://r20.rs6.net/tn.jsp?f=001idrUHw9_YR74VbW-_Xp8jkSsgr0MUbJcbVjihxsBWQvdf3yg_btmpAtW7UUiq-jv6kTjYwp149ITBfoQ9jSu3zl0_0uli_lHBIBhDW27jW0teDo0gQowAWfDXtQRJmudfTyitqxvdDIYrDHhRTm4VjMq2TuS5rvXchmxpVcfeveOA80ZtvNbgmgsm93qn2vFYxJFU_IC2fkOQzx9hl5a2fsmI7l4Wdog&c=aJlsu29wMowPS48vR_j4p-mMQlax7FjISoRV3TlL6sFAssG_yQe2XA==&ch=JlLJRE26PefhPdl_rOl7o_e3Ovb1jewwcBHsfAH_MaWc_6RMXM_h4Q==]
  Scholarships 
[http://r20.rs6.net/tn.jsp?f=001idrUHw9_YR74VbW-_Xp8jkSsgr0MUbJcbVjihxsBWQvdf3yg_btmpAtW7UUiq-jviobYCH92V0IR9QH9-ImbI6lydl31StwQDsJcSLqKlMAHC8voxbaK21aY0DC4JbmdKVBMbRHQ9MMNTgkslW-60mLAS1KItUIwVmJ6Rq1-o6TJCLDcfvRR1g==&c=aJlsu29wMowPS48vR_j4p-mMQlax7FjISoRV3TlL6sFAssG_yQe2XA==&ch=JlLJRE26PefhPdl_rOl7o_e3Ovb1jewwcBHsfAH_MaWc_6RMXM_h4Q==]
Safety Training 
[http://r20.rs6.net/tn.jsp?f=001idrUHw9_YR74VbW-_Xp8jkSsgr0MUbJcbVjihxsBWQvdf3yg_btmpAtW7UUiq-jv_Ltf9bWE1H6BStEYqzh-z8xe6_oteqm2LPvzbFgwg7IKMVbRQ8KbpBwFEay_062YypKutlErcRzdumc6QfeMuMiTdneWMbft949W2MQWB5HzeAepBHK5i3IASlz77g0mF3gO0N_uRidI-YYJ5q3vO9Uo1r9t6sQkFdAkSK8J8zM=&c=aJlsu29wMowPS48vR_j4p-mMQlax7FjISoRV3TlL6sFAssG_yQe2XA==&ch=JlLJRE26PefhPdl_rOl7o_e3Ovb1jewwcBHsfAH_MaWc_6RMXM_h4Q==]
  Technical Services 
[http://r20.rs6.net/tn.jsp?f=001idrUHw9_YR74VbW-_Xp8jkSsgr0MUbJcbVjihxsBWQvdf3yg_btmpAtW7UUiq-jv9vLP63EQmxXEIL2G0VDYyjQLwYPIHI7zld_IK-99OTNjzw47OO53w8JsReUgQSO-Hbo3qxWwWOnYble3J9X_Vf6x90agpqcrzpV1dH2uGB4GtCAXf-xihWmKFMOl8_frefwy62MknNqWkaK2uCpeOA==&c=aJlsu29wMowPS48vR_j4p-mMQlax7FjISoRV3TlL6sFAssG_yQe2XA==&ch=JlLJRE26PefhPdl_rOl7o_e3Ovb1jewwcBHsfAH_MaWc_6RMXM_h4Q==]
Informal Interpretation Request 
[http://r20.rs6.net/tn.jsp?f=001idrUHw9_YR74VbW-_Xp8jkSsgr0MUbJcbVjihxsBWQvdf3yg_btmpAtW7UUiq-jvBEwpMNN8_qXuDPDGWWLDAvTPhrh5yoy9XZxsdqXdsQXeMc7qTDLHhCEvOy_ETwYQ4p4feWWDMQfZ8MSXWrKyvB6yPLI9R7Dc4q-Rl_umRzbtybeLN7ZF9C77srXE0kjNK8Or3j7xWlbRpC4QERF7Qt0kq3Iwz3-K0YkuTrueQRvw4EAhniSO39444lBXV-u3gnYIMPU-wDi7r2CqfFLQvhNYkurABhuP&c=aJlsu29wMowPS48vR_j4p-mMQlax7FjISoRV3TlL6sFAssG_yQe2XA==&ch=JlLJRE26PefhPdl_rOl7o_e3Ovb1jewwcBHsfAH_MaWc_6RMXM_h4Q==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning Fire Sprinkler System
Planning School
2016 Schedule
Jan. 11 - 22, 2016
Feb. 8 - 19, 2016
April 4 - 15, 2016
May 16 - 27, 2016
July 18 - 29, 2016
Oct. 3 - 14, 2016
For more info, call:
214-349-5965 ext. 132
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Call for Trainers
If you, or someone you know, are well versed in any (or all) of the following 
areas:
installation, layout, or inspection/testing/ maintenance of fire sprinkler 
systems,
and want to teach or develop courses, let us hear from you!
Click HERE  
[http://r20.rs6.net/tn.jsp?f=001idrUHw9_YR74VbW-_Xp8jkSsgr0MUbJcbVjihxsBWQvdf3yg_btmpMwvJw2oZJZTDfPDaxlOPTiELaHaXE0z6_bbM9pLptrpZFRFvQorJsO-bMjzNzq8Gy0zLMOa9ZVF6SHypIL3UXhit65z25-xWBceaBT8SWvhkBXBjK0kf_h7FvQixA3MI9Y2EMdtW2p0&c=aJlsu29wMowPS48vR_j4p-mMQlax7FjISoRV3TlL6sFAssG_yQe2XA==&ch=JlLJRE26PefhPdl_rOl7o_e3Ovb1jewwcBHsfAH_MaWc_6RMXM_h4Q==]for
more details
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Link 
[http://r20.rs6.net/tn.jsp?f=001idrUHw9_YR74VbW-_Xp8jkSsgr0MUbJcbVjihxsBWQvdf3yg_btmpEK83igv7SyRj9_aN1mvf3a9mjr4ZgYHqPCKk-4rsfRNd99879vBrrBe77cVKI-mvzAJat7-ExaHMpECJtMjcLjIjiISQhmbPGkIAkybVfC11QkfahHnikbXjEHWl-gnt8S-n4n0IMdzHYnNAYzA-_h72W5VKEeRqTwurDeisjKcQ2bCMYgKHp57bnVtYbXDEg==&c=aJlsu29wMowPS48vR_j4p-mMQlax7FjISoRV3TlL6sFAssG_yQe2XA==&ch=JlLJRE26PefhPdl_rOl7o_e3Ovb1jewwcBHsfAH_MaWc_6RMXM_h4Q==]
Archives 
[https://www.firesprinkler.org/technical-services/subscribe-technical-updates/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]
AFSA Quality Contractor Recognition 
[http://r20.rs6.net/tn.jsp?f=001idrUHw9_YR74VbW-_Xp8jkSsgr0MUbJcbVjihxsBWQvdf3yg_btmpAtW7UUiq-jvWMYBqODNyIDg79iQpj22Aa7-V2kgcJaHZjUQ7qXwlE20gb_FsEZrC8dN-IlCtgKu7sRroc58_wcNPkcvdeZVKKpc8BEnxW_X5FJDyueiBWdA-3vTpnc7WcE59q8hWikdtKKehxgZVh674hJBrWNdQTOGHfiAfL1FWtfs8cNOwRFjendhoQwuZc-MCdVGIY5-&c=aJlsu29wMowPS48vR_j4p-mMQlax7FjISoRV3TlL6sFAssG_yQe2XA==&ch=JlLJRE26PefhPdl_rOl7o_e3Ovb1jewwcBHsfAH_MaWc_6RMXM_h4Q==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1122858416399

This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=c1161dc3-b63b-4f9b-a165-dda97aeb21d9


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=c1161dc3-b63b-4f9b-a165-dda97aeb21d9


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp

Online Marketing by
Constant Contact(R)
www.constantcontact.com



American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to