ESFR Sprinklers and Aisle Widths
"I have an existing ESFR system protecting Group A plastics in racks greater
than
25 ft. The racks are being moved and reducing the aisles from 10 ft to 6 ft
apart.
Control mode sprinkler criteria shows a greater discharge for Class I-IV
commodities
in racks up to 25 ft at different aisle widths and NFPA 13 identifies a minimum
aisle within the general sections. I cannot find similar guidance for ESFR
sprinklers
in Section 17.3.3. Is there a difference in the design basis for shorter
aisles?"
We have reviewed NFPA 13, 2013 edition as the applicable standard. Our informal
interpretation is that aisles must be at least 3.5 ft.
Lets first look at aisles when using spray sprinklers and single- or double-row
racks. As you indicated for Class I-IV commodities in racks up to 25 ft, there
are separate criteria for 4 ft and 8 ft aisles. You can interpolate the density
between these two points. For racks greater than 25 ft, Section 16.3.1
indicates
that an aisle of at least 4 ft is required. Moving into Group A plastics,
aisles
are required by Section 17.1.2.2 to have a minimum width of 3.5 ft. This is in
the general section so it applies to both up to and greater than 25 ft. As
already
alluded to, the actual minimum width is indeed 3.5 ft. This is stated in the
definitions
for both single-row and double-row racks. Fortunately, this is explicitly
stated
in Section 16.2.1.3.2.1(C). While addressing interpolation, it also tells us to
use the same density as a 4 ft aisle in narrower aisles down to 3.5 ft.
Unfortunately,
this is only stated in Section 16.2. So technically, this applies only to Class
I-IV commodities in racks no greater than 25 ft. There is no interpolation in
17.3.1 but the fact that the criteria on a narrower aisle certainly is i
ntended to apply to racks for Class I-IV greater than 25 ft. Otherwise, we
would
have a major deficiency with no protection criteria for acceptable single- or
double-row
racks with aisles between 3.5 ft and 4 ft.
As for ESFR and CMSA, the criteria refer to single- and double-row racks. Thus
you simply go to the definitions in Chapter 3 and apply the 3.5 ft as part of
the
defining variables for these racks.
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
in fire protection engineering. This is provided with the understanding that
the
AFSA assumes no liability for this opinion or actions taken on it and they are
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2015, American Fire Sprinkler Association. All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Quick Links
firesprinkler.org
[http://r20.rs6.net/tn.jsp?f=001CiXm1teq3WzGN0gJsJiKX97FQBdpsYO19rt8BkGhLCOB6hMWKozlUFV6YEOLhiCzbHaUsMRvjwaZtWuohlCoNw7Nl0gShvMwqTc9Ky_cTTRxy5n6XpIVuLYwJ15Giie0GIP9gKZGTnVuSXVFEffAQU8OkD5BKOQCRJviBx-qZ2JSk7BiNfI_xg==&c=PClS0Jk4Y_-0H470E65_pcN9DantFXFw6mZmHJLSnJP7F2RQaS0ROA==&ch=aEt1vcwYX1u3zOSf4k1GE4sSXStfS4DPgfGpVrCOqy-jGLczKSheUw==]
Join AFSA
[http://r20.rs6.net/tn.jsp?f=001CiXm1teq3WzGN0gJsJiKX97FQBdpsYO19rt8BkGhLCOB6hMWKozlUFV6YEOLhiCznBYxEmNHurqRg_0MTR9QsrDRIWwuuCWCA7A8Pe7TnXBiezDPVzTEhkpmaatjycBpfJfMpAQy97BruB5rseiTfBxHJiNRKk9s7AqrCGMTggxcQWrso46jY2LQ6K0_O55Y3EmLMQX3UFZVUPyj_9pp_TzC3Ww5edmn&c=PClS0Jk4Y_-0H470E65_pcN9DantFXFw6mZmHJLSnJP7F2RQaS0ROA==&ch=aEt1vcwYX1u3zOSf4k1GE4sSXStfS4DPgfGpVrCOqy-jGLczKSheUw==]
Scholarships
[http://r20.rs6.net/tn.jsp?f=001CiXm1teq3WzGN0gJsJiKX97FQBdpsYO19rt8BkGhLCOB6hMWKozlUFV6YEOLhiCzTtMsibgofMnOBCnk4-sgAgNZ-gV3uweOmCn3TOMyLH3XOdROlrkSOqT8IYuDi493-BygwJ2oLRpp22AHNT5MTTdT8vAmnF1mohFuIrmYgEYblApcrDG3sQ==&c=PClS0Jk4Y_-0H470E65_pcN9DantFXFw6mZmHJLSnJP7F2RQaS0ROA==&ch=aEt1vcwYX1u3zOSf4k1GE4sSXStfS4DPgfGpVrCOqy-jGLczKSheUw==]
Safety Training
[http://r20.rs6.net/tn.jsp?f=001CiXm1teq3WzGN0gJsJiKX97FQBdpsYO19rt8BkGhLCOB6hMWKozlUFV6YEOLhiCz-sT9Um0PoKWGiZuzog1zUnWeGhKnuQv-qKYX3ohIqwJrI8MBmy73afkIGhUiyH8P8EguKEITGuJENGy-4dqg4wVqqb3Q4jNjYULnMOfp4feLVqXlPl44iono0R1Gyeb7JjwBy9a5dOioWCWyHgyLzhxa1hE5UB_kFM7yso9EmDA=&c=PClS0Jk4Y_-0H470E65_pcN9DantFXFw6mZmHJLSnJP7F2RQaS0ROA==&ch=aEt1vcwYX1u3zOSf4k1GE4sSXStfS4DPgfGpVrCOqy-jGLczKSheUw==]
Technical Services
[http://r20.rs6.net/tn.jsp?f=001CiXm1teq3WzGN0gJsJiKX97FQBdpsYO19rt8BkGhLCOB6hMWKozlUFV6YEOLhiCz927CjHyawS4GqoOq2mZ4eOXqqq3Z0LoTTRzJ1IgbDzcsdC-QsC-DTisglDpDuomDNqYRGjI-YWrCpPJQuoPqJyvSIP2-Ig1LHEq3YQSgmxJRa21Goj_Kf1YJe35mJIDABIzIOcac8cKuy7J5h3_l2g==&c=PClS0Jk4Y_-0H470E65_pcN9DantFXFw6mZmHJLSnJP7F2RQaS0ROA==&ch=aEt1vcwYX1u3zOSf4k1GE4sSXStfS4DPgfGpVrCOqy-jGLczKSheUw==]
Informal Interpretation Request
[http://r20.rs6.net/tn.jsp?f=001CiXm1teq3WzGN0gJsJiKX97FQBdpsYO19rt8BkGhLCOB6hMWKozlUFV6YEOLhiCzV7J4F_6u--5YctFdjvxDgYebnatxZpg3LAXnivFqiE9_OpxF_3UTvA-LxPGDJEqvAmgZGlNyCq3aEKYCNqiOeKkDAOKYDvFA1egaHD5noBdZSmMy9-O4Whf4iU4LsWATEq-RAegr4TCTosF8_L3-3u30kxFrjLKndYTEr7Enk7kcByD8InoDN1dHU0Lue7SBcCkAzk9kZDu9TbcjCyUXD4IQLatQpKPK&c=PClS0Jk4Y_-0H470E65_pcN9DantFXFw6mZmHJLSnJP7F2RQaS0ROA==&ch=aEt1vcwYX1u3zOSf4k1GE4sSXStfS4DPgfGpVrCOqy-jGLczKSheUw==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Training Calendar
AFSA Beginning Fire Sprinkler System
Planning School
2016 Schedule
Jan. 11 - 22, 2016
Feb. 8 - 19, 2016
April 4 - 15, 2016
May 16 - 27, 2016
July 18 - 29, 2016
Oct. 3 - 14, 2016
For more info, call:
214-349-5965 ext. 132
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Call for Trainers
If you, or someone you know, are well versed in any (or all) of the following
areas:
installation, layout, or inspection/testing/ maintenance of fire sprinkler
systems,
and want to teach or develop courses, let us hear from you!
Click HERE
[http://r20.rs6.net/tn.jsp?f=001CiXm1teq3WzGN0gJsJiKX97FQBdpsYO19rt8BkGhLCOB6hMWKozlUOWewwo8AzlUWxFqRyBGvHWfTERVDzwxIVLJsn-eUIvJx16guX5Gv_Y_geVGjZ4VqsBxZ9KIyokrB7K_Lief-Tl74JuFgnAS2U6-_qgocijOHuCXRam_D6ATVWt8SjXSbE2M9_TWu2VD&c=PClS0Jk4Y_-0H470E65_pcN9DantFXFw6mZmHJLSnJP7F2RQaS0ROA==&ch=aEt1vcwYX1u3zOSf4k1GE4sSXStfS4DPgfGpVrCOqy-jGLczKSheUw==]for
more details
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
PDF Link
[http://r20.rs6.net/tn.jsp?f=001CiXm1teq3WzGN0gJsJiKX97FQBdpsYO19rt8BkGhLCOB6hMWKozlUDUBpGLaA10tAcei8_dJzTgo2F55-rrS-Mol00FQZTCqgmB2axCZgSiJ_Sls76Mvmd9aSboPQ3u3sop4EUo5qD3TOaoaywdUF2RxLNvEH2fD3dpdWR10ZghbJX_w8C_8BjrmjUj30fsEMcy7fxcbxID590XR8ZWaDLzNqAsTwkSUQhYpQ0H3_wKvmh2TT8CD8g==&c=PClS0Jk4Y_-0H470E65_pcN9DantFXFw6mZmHJLSnJP7F2RQaS0ROA==&ch=aEt1vcwYX1u3zOSf4k1GE4sSXStfS4DPgfGpVrCOqy-jGLczKSheUw==]
Archives
[https://www.firesprinkler.org/technical-services/subscribe-technical-updates/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Quality Contractor
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]
AFSA Quality Contractor Recognition
[http://r20.rs6.net/tn.jsp?f=001CiXm1teq3WzGN0gJsJiKX97FQBdpsYO19rt8BkGhLCOB6hMWKozlUFV6YEOLhiCz-I9NRv2to4TXiniSTiy7qaUJElVNgcCzOkmbnYt2VeI-s3VNEHe2d5cQ7phnRvRLW-BxXc2tQw_Fs-7hcFXzy-JF3oKCAV3Bx5r59KUi6tESCjWELNHkk4XVUrIzVHHB8J5euNPm2J5SBv93ZSaHGjL7YxFVEPp6bZb3DFYh0TfM9Dbx6gj79xJjqYeo6zoU&c=PClS0Jk4Y_-0H470E65_pcN9DantFXFw6mZmHJLSnJP7F2RQaS0ROA==&ch=aEt1vcwYX1u3zOSf4k1GE4sSXStfS4DPgfGpVrCOqy-jGLczKSheUw==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1122973740773
This email was sent to [email protected] by
[email protected].
Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=d7f6e197-3c07-433a-99ad-6d213f29f3f3
Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=d7f6e197-3c07-433a-99ad-6d213f29f3f3
Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp
Online Marketing by
Constant Contact(R)
www.constantcontact.com
American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas |
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org