April 25, 2016

Clapper in the Fire Department Connection


"There are some buildings connected by one underground fire loop and share a 
fire department connection (FDC) located close to the street for ease of 
access.  The FDCs are not traditional where a welded "Tee" is about 4 ft tall 
by 4 ft horizontal piping where there are four welded outlets that contain a 2 
1/2 in. threaded nipple and a 2 1/2 in. hose adapter.  Is an integral clapper a 
required component for a fire department connection (FDC)?” 


We have reviewed NFPA 13, 2016 edition as the applicable standard.  Our 
informal interpretation is that clappers or check snoots should have been 
installed for the inlets.


The NFPA 13 standard is silent regarding the clappers inside the FDC.  The 
clapper must be present when there are two or more inlets in the FDC per its 
listing by UL and FM Global.  Clappers swing freely and open to incoming water 
at the connections and close the opening to unused inlets by water pressure.  
That way the hose supply does not have to be depressurized to connect 
additional hoses to the FDC.  In addition, the clappers also prevent backflow 
into hose lines of lower pressures.  Hose inlets on fabricated welded pipe or 
manifold as a FDC are not uncommon. The arrangement doesn't use a listed FDC 
device and could be problematic during use without the clappers.  The 
manufacturers of inlet connections also make check snoots for individual inlet 
connections.  The check snoot would've been ideal for use as the inlet 
connections on the FDC for the piping arrangement that you described.  A 
clapper is provided for each individual hose inlet. For a single hose inlet for 
small diameter risers and residential systems, a clapper would not be required 
per a UL representative.  This makes sense for a single inlet as no additional 
hoses would be connected.  One other residual function of the clapper or check 
snoot is that when the hoses are disconnected, there is not a flow back of 
water inside the FDC piping pouring onto the person handling the hose.


The NFPA 25 standard also supports the use of clappers for the FDCs and 
references clappers in two areas.  First, Section 13.7.1 indicates that FDCs 
shall be inspected quarterly to verify the clapper(s) is in place and operating 
properly.  Secondly, Table A.3.3.7 Water-Based Fire Protection System 
Inspection and Testing Findings says that it is considered an impairment when 
the FDC's clapper is not operating properly or missing and provides a reference 
to Section 13.7.1.  With that said, clappers would not apply to single inlet 
FDC connections including the large diameter quick-connect FDC hose connections 
named Storz.  The Storz inlet connections have no clapper provided since that 
is a single hose connection. 


Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President of Engineering and Technical Services Roland Huggins, a PE registered 
in fire protection engineering;  Tom Wellen, a PE registered in fire protection 
engineering. This is provided with the understanding that the AFSA assumes no 
liability for this opinion or actions taken on it and they are not to be 
considered the official position of the NFPA or its technical committees. 

Copyright 2016, American Fire Sprinkler Assocaiton

Ada Dickson
 
Ada Dickson
Administrative Assistant
Technical Services Dept.
 PH: (214) 349-5965 ext. 124   Fax: (214) 343-8898
E-mail: [email protected]




-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklernotes-firesprinkler.org/attachments/20160427/e39d48aa/attachment.htm>

Reply via email to