Remote Area for Composite Wood Joist Channels

  

╥We have had multiple AHJs determine the intent of whether or not this 
concealed combustible space with composite wood joists requires a 3,000 sq. ft. 
calculation area. Section 8.15.1.2.6 references equivalent materials to the web 
construction and Section 11.2.3.1.4(4)(j) does not. The annex 
A.11.2.3.1.4(4)(j) also refers to gypsum or equivalent material used as the 
fire stopping. Is it the intent to apply the 3,000 sq. ft. remote area when 
applying Section 8.15.1.2.6?╙ 

 

We have reviewed NFPA 13, 2013 edition that you indicated as the applicable 
standard. Our informal interpretation is that gypsum should be added to the 
composite wood joist channels to limit the volumes to less than 160 cu. ft. to 
avoid a 3000 sq. ft. remote area.

  

Chapter 8 and Chapter 11 have two separate functions regarding sprinklers.  
Chapter 8 determines when sprinklers can be omitted in concealed combustible 
spaces. Chapter 11 sets the minimum remote area size based on the arrangement 
of concealed combustible spaces. Section 11.2.3.1.4(4)(j) states, ╥Light or 
ordinary hazard occupancies where noncombustible or limited combustible 
ceilings are attached to the bottom of composite wood joists either directly or 
onto metal channels not exceeding 1 in. in depth, provided the adjacent joist 
channels are firestopped into volumes not exceeding 160 cu. ft. using materials 
equivalent to 1/2 in. gypsum board and at least 3 1/2 in. of batt insulation is 
installed at the bottom of the joist channels when the ceiling is attached 
utilizing metal channels.╙ Additional guidance is provided in the annex as 
A.11.2.3.1.4(4)(j) that indicates gypsum board (or equivalent material) used as 
the firestopping will compartmentalize the concealed space and restrict the 
ability for fire to spread beyond 160 cu. ft. zones covering multiple joist 
channels. This is different from Chapter 8 where sprinklers can be omitted from 
the concealed combustible space. Chapter 11 has the requirement for gypsum in 
order to avoid the 3,000 sq. ft. remote area.  The reason for the gypsum to be 
added is that the composite wood joist webs fail so quickly during a fire. The 
gypsum enclosure may be one or multiple composite wood joist channels depending 
on the construction configuration. A 3,000 sq. ft. remote area will be required 
if gypsum or equivalent is not installed to limit the volume to 160 cu. ft. 
With the overall concealed space subdivided by gypsum into 160 cu.ft. portions, 
this now presents a risk similar to the long-standing allowance in 
11.2.3.1.4(4)(d)that divides the overall space into 160 cu. ft. portions using 
solid wood joists.

 

 ------------

Technical Update is prepared by the Technical Services Dept. of the AFSA: 
Roland Huggins, a PE registered in fire protection engineering, Vice President 
of Engineering and Technical Services; and Tom Wellen, a PE registered in fire 
protection engineering. This is provided with the understanding that the AFSA 
assumes no liability for this opinion or actions taken on it and they are not 
to be considered the official position of the NFPA or its technical committees.

 

Copyright 2016, American Fire Sprinkler Association. All Rights Reserved.