Sample Size for Testing Sprinklers

  

“I have six apartment buildings that were constructed in 2002 that have dry 
sidewall sprinklers protecting the breezeways.  The dry sprinklers require 
testing since they are over 10 years old. NFPA requires a minimum of 1 percent 
of the total sprinklers but not less than four sprinklers to be tested. To meet 
this requirement would this be for each building individually or could it be 
based on the entire six buildings since they were all constructed in the same 
year with the same make, model and temperature of sprinklers?”

 

We have reviewed NFPA 25, 2014 edition that you indicated as the applicable 
standard. Our informal interpretation is testing all six breezeways as one 
sample is appropriate.

 

Installation standards are easy because they are generally written to address 
single systems, but even then there are exceptions such as water supplies and 
FDC connections. NFPA 25 is not written in a per system format (although our 
inspection forms typically are per system to better communicate what has been 
performed). You’re right that we generally look at individual buildings, but in 
the case where it’s an open breezeway between buildings, treating it as one 
area would be no different than treating a warehouse with three systems as a 
single area. Let’s now look at the actual text on this issue. The scope 
(Section 1.1) indicates it applies to fire protection systems (plural). This 
could be interpreted either way. More importantly, Section 5.3 on Testing tells 
us that a representative sample from one or more areas shall be tested. The 
representative sample is intended to cover the all the sprinklers within a 
given environment (since the potential for corrosion, loading, painting, etc. 
varies based on the function and exposure of where the sprinklers are placed. 
The sample can come from different areas within a system or different floors 
(that are typically different systems). This is clarified in the NFPA 25 
Handbook where the commentary on Section 5.3.1.2 states:

 

“The sample should be somewhat random and should be representative of the 
sprinklers installed in the system. For example, sprinklers should be selected 
from different floors or areas of the building and not selected simply because 
they are more accessible than other sprinklers. In addition, the selection 
should take into consideration the age and types of sprinklers as well as the 
environmental conditions to which they are subjected.”

 

The sample is also not required to be every type installed as long as one of 
the types from the same manufacturer is tested as dictated by A.5.3.1.2.

Considering all the breezeways are the same environment with the same 
manufacturer, pulling a single sample of four sprinklers or 1 percent of the 
total sprinklers from the combined areas meets the intent of the standard. 
There is a downside when defining a larger area as the representative sample. 
That is, if there is a failure from any one of the different areas, you have to 
replace the sprinklers in all of the areas.

 

------------

Technical Update is prepared by the Technical Services Dept. of the AFSA: 
Roland Huggins, a PE registered in fire protection engineering, Vice President 
of Engineering and Technical Services; and Tom Wellen, a PE registered in fire 
protection engineering. This is provided with the understanding that the AFSA 
assumes no liability for this opinion or actions taken on it and they are not 
to be considered the official position of the NFPA or its technical committees.

 

Copyright 2016, American Fire Sprinkler Association. All Rights Reserved.