Loads from Branch Lines

 

“For apartment building projects, we typically run a main in a corridor and 
then have branch lines that tie into the heads of the units. When calculating 
the lateral brace loads, it is obvious that we must include the loads of the 
branch lines that run perpendicular to the main. Do we also need to include the 
load of the pipes that run off the branch line that are parallel to the main?”

 

We have reviewed NFPA 13, 2016 edition as the applicable standard. Our informal 
interpretation is the weight of all pipe connected to the branch line within 
the zone of influence need to be included.

 

The zone of influence includes the weights of branch lines, armovers, drops, 
return bends, and sprigs. The direction of the pipe, whether parallel or 
perpendicular to the main, does not matter. Section 9.3.5.9.6 states, “The zone 
of influence for lateral braces shall include all branch lines and mains 
tributary to the brace, except branch lines that are provided with longitudinal 
bracing or as prohibited by 9.3.5.9.6.1.” The annex for this indicates that the 
zones of influence do not have to be symmetrically based on brace spacing. It 
is the intent of NFPA 13 that the chosen zone of influence be the worst-case 
load scenario. In addition, the annex material at the end of A.9.3.5.9 
indicates that the factor of 1.15 is intended to approximate the additional 
weight of all valves, fittings, and other devices attached to the system. There 
is no mention of drops, armovers and sprigs so consider the definition of a 
branch line. The definition of a branch line is the pipes supplying sprinklers, 
either directly or through sprigs, drops, return bends, or armovers. Thus, the 
weight of the water-filled pipe for determining horizontal loads within the 
zone of influence should include armovers, drops, return bends, and sprigs. 
This may be clarified in the 2019 edition of NFPA 13 but this has yet to be 
processed through the standards-making process.

  

=========

Technical Update is prepared by the Technical Services Dept. of the AFSA: 
Roland Huggins, a PE registered in fire protection engineering, Vice President 
of Engineering and Technical Services; and Tom Wellen, a PE registered in fire 
protection engineering and Tom Noble E.T., a Technical Programs Specialist. 
This is provided with the understanding that the AFSA assumes no liability for 
this opinion or actions taken on it and they are not to be considered the 
official position of the NFPA or its technical committees.

 