Control Valve

 

“Per 17.1.2.9.6, the in-rack sprinkler demand shall not be required to be 
hydraulically balanced with the ceiling level sprinkler system. Does the 
in-rack system for this alternate protection scheme require a separate control 
valve or riser and supply piping? If not, can the in-rack system be tied into 
the ceiling level sprinkler system if it is hydraulically proven? Is the 
outside hose demand for this in-rack system 500 gpm?”

 

We have reviewed NFPA 13, 2016 edition as the applicable standard. Our informal 
interpretation is noted below.

 

There is little guidance regarding alternative protection and in-rack sprinkler 
systems. As such, default to 8.16.1.5 for in-rack sprinkler system control 
valves. Separate indicating control valves and drains shall be provided and 
arranged so that ceiling and in-rack sprinklers can be controlled independently 
per Section 8.15.1.5.1. Separate control valves are ideal since in-rack 
sprinklers are susceptible to damage due to their location. The separate 
control valves allow the ceiling system to remain in service while the in-rack 
sprinkler protection is being restored. Conversely, the in-rack system would 
remain operational when the ceiling system is out of service. There are two 
exceptions for this arrangement. Section 8.16.1.5.2 says that installation of 
20 or fewer in-rack sprinklers supplied by any one ceiling sprinkler system 
shall not require a separate indicating control valve. This permits an in-rack 
sprinkler system to be supplied from the overhead system without a separate 
control valve. The other exception is 8.16.1.5.3 where separate indicating 
valves can to be arranged as sectional control valves supplied from the ceiling 
sprinkler system where in-rack sprinklers are required and the racks including 
the adjacent aisles occupy 8,000 sq. ft. or less of the area protected by the 
ceiling sprinklers. This applies where the in-rack system has more than 20 
sprinklers but only occupies a portion of the area protected by the overhead 
system. This allows the in-rack system to be isolated without affecting the 
ceiling sprinkler system. The area is limited since impairment to the overhead 
system will also impair the in-rack system. Lastly, the 500-gpm hose stream 
allowance does not apply to in-rack sprinklers since it’s included with the 
ceiling sprinkler system.

 

=========

Technical Update is prepared by the Technical Services Dept. of the AFSA: 
Roland Huggins, a PE registered in fire protection engineering, Vice President 
of Engineering and Technical Services; and Tom Wellen, a PE registered in fire 
protection engineering and Tom Noble E.T., a Technical Programs Specialist. 
This is provided with the understanding that the AFSA assumes no liability for 
this opinion or actions taken on it and they are not to be considered the 
official position of the NFPA or its technical committees.

 

Copyright 2017, American Fire Sprinkler Association. All Rights Reserved.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklernotes-firesprinkler.org/attachments/20170403/b8a197e6/attachment.htm>

Reply via email to