Obstructions Against the Wall 

“I am trying to apply figure A.8.6.5.1.2 to a bulkhead with a demising wall 
above it stepped back about 8 in. from the front edge of the bulkhead. Below 
the bulkhead is a floor to bulkhead wall that is stepped back 2 ft-8 in. from 
the front edge of the bulkhead. Two foot of the depth below the bulkhead is 
filled with a full height built-in cabinet. The AHJ is not comfortable allowing 
this code to be applied in my situation because the wall is not in the same 
vertical plane above and below the bulkhead. I do not see any dimensions in 
Figure A.8.6.5.1.2 that give a depth of the setback for the wall. The figure 
only gives a maximum depth of 4 ft. I am well under this total width and my 
sprinkler head is 20 in. above the top of the bulkhead. Can I apply this code 
to avoid installing a sprinkler in the 8-in. wide bulkhead in front of the 
cabinet?”  

We have reviewed NFPA 13, 2010 edition that you indicated as the applicable 
standard. Our informal interpretation is that a sprinkler is not required in 
the 8-in. bulkhead. 

A cabinet fills the void where an 8-in. shelf against the wall is present. The 
standard does reference in 8.5.3.2.3 that the distance from the wall to the 
sprinkler shall be measured to the wall behind furniture, such as wardrobes, 
cabinets, and trophy cases. That is to address the correct placement of the 
sprinkler. What the standard does not say is to omit this cabinet when 
considering obstructions. As such, the cabinet becomes the face of the wall 
when applying the obstruction rules. This should not be considered as a 2 ft-8 
in. niche. This application is an 8-in. shelf against the wall. Section 
8.6.5.1.1 indicates that sprinklers shall be located so as to minimize 
obstructions to discharge as defined in 8.6.5.2 and 8.6.5.3, or additional 
sprinklers shall be provided to ensure adequate coverage of the hazard. Since 
the obstruction is located 20 in. below the deflector, 8.6.5.3.1 would apply. 
More specifically, sprinklers shall be installed under fixed obstructions over 
4-ft wide, such as ducts, decks, open grate flooring, cutting tables, and 
overhead doors per 8.6.5.3.3. Hence, Figure A.8.6.5.1.2 specifically shows your 
application. The vertical plane above and below the obstruction doesn’t appear 
to be of a concern for this application as both surfaces will be wetted. If, 
for instance, the distance from the deflector to the shelf was less than or 
equal to 18 in. 8.6.5.2.1.2 would refer back to 8.6.5.1.2. Applying 
8.6.5.1.2(3), nicknamed the soffit rule, this would place the sprinkler a 
minimum of 20 in. away from the obstruction to the centerline of the sprinkler. 
The sprinkler is located at 24 in. thus you met the intent of the standard.

=========

Technical Update is prepared by the Technical Services Dept. of the AFSA: 
Roland Huggins, a PE registered in fire protection engineering, Vice President 
of Engineering and Technical Services; and Tom Wellen, a PE registered in fire 
protection engineering and Tom Noble E.T., a Technical Programs Specialist. 
This is provided with the understanding that the AFSA assumes no liability for 
this opinion or actions taken on it and they are not to be considered the 
official position of the NFPA or its technical committees.

Copyright 2017, American Fire Sprinkler Association. All Rights Reserved.

 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklernotes-firesprinkler.org/attachments/20170417/1d392eed/attachment.htm>

Reply via email to